Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 


This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 


They listed it like this:


Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28


Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.


I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 


Views: 2636


Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

WIndows and Daylighting Group
Lawrence Berkeley National Laboratory

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.

Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!



Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Colin Genge posted an event

Home Efficiency Forum at Courtyard Portland City Center

October 21, 2015 at 8am to October 23, 2015 at 5pm
Home Efficiency Forum (formerly known as Boot Camp) brings Northwest Raters, Verifiers, builders…See More
7 hours ago
MCX posted a blog post

Good HVAC in Arlington, Texas

Arlington is a city in the U.S. state of Texas, within the Dallas–Fort Worth–Arlington metropolitan…See More
8 hours ago
Profile IconRichard L. Sanderson and Diane Jackson joined Diane Chojnowski's group

Home Energy Pros on Twitter

We've created a twitter list of members of Home Energy Pros who tweet!See More
9 hours ago
Diane Jackson commented on Diane Chojnowski's group Home Energy Pros on Twitter
"@addisonhomes "
10 hours ago
Diane Jackson posted a blog post
10 hours ago
John Gillis replied to John Gillis's discussion Energy Savings of Whole House Fans vs. Air Conditioners in SoCal Featured on New 'Ask This Old House' Season in the group News & Announcements
"Hi Eric. Thanks for the response. If you wouldn't mind calling/e-mailing Nelson Warner or…"
15 hours ago
Profile IconShandi Whited, Noah Sanders, Edward G Fahrenkrug Jr and 2 more joined Home Energy Pros
17 hours ago
Alan Gindt replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Bob, sorry but it has been sold"
18 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service