Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 

 

This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 

 

They listed it like this:

 

Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28

 

Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.

 

I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 

 

Views: 3015

Attachments:

Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

Christian
WIndows and Daylighting Group
Lawrence Berkeley National Laboratory
Adam:

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.
http://www.windowsvolumepurchase.org/

Christian
Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!

Adam

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Profile IconBob Eldredge, Thomas Joseph and الصفوة joined Home Energy Pros
5 minutes ago
الصفوة liked الصفوة's blog post شركة مكافحة حشرات بالرياض
20 minutes ago
الصفوة posted a blog post
20 minutes ago
Colin Genge updated an event
Thumbnail

Measuring HVAC Performance webinar at Online

February 23, 2016 from 11am to 12pm
If you install, service or test HVAC systems you will want be there for this special webinar.…See More
49 minutes ago
Colin Genge updated an event
Thumbnail

Testing for IECC Code Compliance for duct and house leakage webinar at Online

February 16, 2016 from 11am to 12pm
The International Energy Conservation Code (IECC) is in use or adopted in 47 states, the District…See More
50 minutes ago
Jan Green posted a status
"I'm honored to be selected to speak at the 2016 RESNET Conference right here in sunny Scottsdale 2/29-3/2/16 with SRP & others!"
2 hours ago
Joe Konopacki posted an event

Duct & Envelope Tightness (DET) Verifier at Temperature Equipment Corporation

February 26, 2016 from 8:30am to 4:30pm
The Duct & Envelope Tightness Certification (DET) was designed by the Midwest Home Performance…See More
2 hours ago
Diane Jackson liked Don Hynek's discussion Superinsulation retrofit is Complete!
4 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service