The L-shaped probe grew legs, so this was improvised with a straight metal tube. There seems to be a persistent notion that angling the probe toward the appliance (into the exhaust stream) is the correct technique, but wouldn't this result in interference from ram air pressure of the rising flue gases?

Tags: CAS, CAZ, analysis, combustion, draft, pitot, safety, spillage, tube

Views: 440

Reply to This

Replies to This Discussion

I'm guessing that is the short metal tube that comes with the DG.  If that is the case, go with perpendicular to the pipe.  Might want to trim some of the pipe insulation off as well before the job is completed.  The insulation looks a little close to the vent, based just on the pictures above (clearance to combustables).

Thanks Dan. Yes, it's the straight tube from the DG bag. Interestingly, Minneapolis sells what they call a "Static Pressure Probe" and distinguish it from a "Pitot Tube", which they don't sell. Both are right-angled metal probes, the difference being that pitot tubes measure ram air (or velocity) pressure through an opening in the tip that static pressure probes don't have.

The principle is familiar to the aviation geek in me (aircraft use a pitot tube to measure airspeed and a static pressure port with an aneroid barometer to measure altitude). After further discussion in our office and examination of one the aforementioned static pressure probes, angling the tip toward the appliance would, in fact, align the holes in the probe perpendicular to the exhaust stream for a true static pressure reading. In that context, the technique I hear people cite about pointing the probe into the stream makes sense, as does your recommendation to hold the straight metal tube perpendicular to the flue.

I think the tight clearance is a result of the photo angle here.

A pitot tube on an airplane is pointed forward because you want to measure air speed and if it points into the wind it measures, well, the speed of the air.

Draft in a heater is different - we aren't looking for MPH but Delta P.  These are 2 different things.  Both the pitot tube and the bent static probe have holes perpendicular to the air stream so are measuring the same thing.  The straight pitot tube in a heater flue should point straight in to measure the same thing that the bent static probe measures when either pointed toward or away from the air stream.  

Interesting that, in your pictures, the probe pointed into the airstream measures zero.

Yep - and the static pressure port is usually on the side of the fuselage, perpendicular to the airstream.

The reading pointed toward the airstream fluctuated between -0.2 and 0.2 or so. If we interpolate the "true" static pressure as about -2.0 (halfway between zero and -4.1), then the interference of the velocity air pressure directly entering the tube, which the manometer would interpret as positive, explains the zero reading.

Isn't there a measurement missing here?...

Yeah, it should have been taken perpendicular to the flue, as Dan pointed out.

Too cryptic, sorry.  

Shouldn't there be another tube and another pressure being measured?...

Hmm. I've understood the intent to be measuring the delta P of flue gases and the ambient air, but it's been quite a few moons since I've done combustion testing on a regular basis. What am I missing here?

Ted

Still too cryptic

Where is the 2nd hose measuring caz depressurization?

I see what you mean - but the title of the thread is:

Which is the valid draft test, noir which is the valid CAZ test

Is it a valid draft test without both numbers?

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Rod Fox replied to Kevin Eigel's discussion What is the best energy auditing software?
"I've been trying to answer this question for many years and have not yet found an answer.…"
6 minutes ago
Jerry Lawrence posted events
13 minutes ago
Jan Green commented on Theresa L Gilbride's blog post Find out who's building some of the best-performing homes in the country today with DOE’s Tour of Zero
"Thank you for sharing! "
1 hour ago
Jan Green commented on Theresa L Gilbride's blog post Find out who's building some of the best-performing homes in the country today with DOE’s Tour of Zero
"We have one builder in Arizona on the DOE list.  Good information for a blog!"
1 hour ago
Beverly Lerch posted a photo

FIREPLACE FASHION COVER

A Fireplace Fashion Cover will insulate and isolate your fireplace against drafts and heat loss…
1 hour ago
Home Energy Magazine's blog post was featured

Twenty-First-Century Energy Efficiency—with Carbon on Our Minds

After the first oil embargo, in 1973, our nation recognized the need to save…See More
2 hours ago
SmithWatson shared their blog post on Facebook
3 hours ago
Home Energy Magazine posted a discussion

Home Energy's Sept/Oct issue is live!

The September/October issue is now live on …See More
18 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service