The L-shaped probe grew legs, so this was improvised with a straight metal tube. There seems to be a persistent notion that angling the probe toward the appliance (into the exhaust stream) is the correct technique, but wouldn't this result in interference from ram air pressure of the rising flue gases?

Tags: CAS, CAZ, analysis, combustion, draft, pitot, safety, spillage, tube

Views: 542

Reply to This

Replies to This Discussion

I'm guessing that is the short metal tube that comes with the DG.  If that is the case, go with perpendicular to the pipe.  Might want to trim some of the pipe insulation off as well before the job is completed.  The insulation looks a little close to the vent, based just on the pictures above (clearance to combustables).

Thanks Dan. Yes, it's the straight tube from the DG bag. Interestingly, Minneapolis sells what they call a "Static Pressure Probe" and distinguish it from a "Pitot Tube", which they don't sell. Both are right-angled metal probes, the difference being that pitot tubes measure ram air (or velocity) pressure through an opening in the tip that static pressure probes don't have.

The principle is familiar to the aviation geek in me (aircraft use a pitot tube to measure airspeed and a static pressure port with an aneroid barometer to measure altitude). After further discussion in our office and examination of one the aforementioned static pressure probes, angling the tip toward the appliance would, in fact, align the holes in the probe perpendicular to the exhaust stream for a true static pressure reading. In that context, the technique I hear people cite about pointing the probe into the stream makes sense, as does your recommendation to hold the straight metal tube perpendicular to the flue.

I think the tight clearance is a result of the photo angle here.

A pitot tube on an airplane is pointed forward because you want to measure air speed and if it points into the wind it measures, well, the speed of the air.

Draft in a heater is different - we aren't looking for MPH but Delta P.  These are 2 different things.  Both the pitot tube and the bent static probe have holes perpendicular to the air stream so are measuring the same thing.  The straight pitot tube in a heater flue should point straight in to measure the same thing that the bent static probe measures when either pointed toward or away from the air stream.  

Interesting that, in your pictures, the probe pointed into the airstream measures zero.

Yep - and the static pressure port is usually on the side of the fuselage, perpendicular to the airstream.

The reading pointed toward the airstream fluctuated between -0.2 and 0.2 or so. If we interpolate the "true" static pressure as about -2.0 (halfway between zero and -4.1), then the interference of the velocity air pressure directly entering the tube, which the manometer would interpret as positive, explains the zero reading.

Isn't there a measurement missing here?...

Yeah, it should have been taken perpendicular to the flue, as Dan pointed out.

Too cryptic, sorry.  

Shouldn't there be another tube and another pressure being measured?...

Hmm. I've understood the intent to be measuring the delta P of flue gases and the ambient air, but it's been quite a few moons since I've done combustion testing on a regular basis. What am I missing here?

Ted

Still too cryptic

Where is the 2nd hose measuring caz depressurization?

I see what you mean - but the title of the thread is:

Which is the valid draft test, noir which is the valid CAZ test

Is it a valid draft test without both numbers?

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Luis Imery added a discussion to the group Job Board
Thumbnail

Hiring: Construction Manager with High Performance Custom Home Experience

POSITION DESCRIPTIONJob Title: Construction ManagerDepartment: Construction –…See More
17 hours ago
Profile IconLuis Imery and Quinn Korzeniecki joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
17 hours ago
Colin Genge posted an event

Retrotec is attending the NEBB Testing and Balancing (Tab) Certified Professional Review Seminar in Chicago, IL at Hilton Chicago O’Hare Airport

June 6, 2016 at 8am to June 8, 2016 at 5pm
Building owners and tenants are concerned that the environmental performance of buildings must be…See More
21 hours ago
Colin Genge updated an event
Thumbnail

Retrotec is exhibiting at the NFPA Conference & Expo-Booth 1355 at Mandalay Bay Convention Center

June 13, 2016 at 8am to June 16, 2016 at 5pm
NFPA's Conference & Expo is widely regarded as the most comprehensive industry event for…See More
21 hours ago
Tom White posted a video

Hayward Healthy Home Principles and Products

Bill Hayward discusses the principles that were used to build the first Hayward Healthy Home and how the products were evaluated for toxicity before they wer...
22 hours ago
Tom White's video was featured

Building Science Insights -- To Vent or Not to Vent

Building Science Presentation with Dr. Joseph Lstiburek.
23 hours ago
Quinn Korzeniecki added a discussion to the group Job Board
23 hours ago
Profile IconIan Smith, Brett Slezak, Autumn Secrest and 6 more joined Home Energy Pros
23 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service