The L-shaped probe grew legs, so this was improvised with a straight metal tube. There seems to be a persistent notion that angling the probe toward the appliance (into the exhaust stream) is the correct technique, but wouldn't this result in interference from ram air pressure of the rising flue gases?

Tags: CAS, CAZ, analysis, combustion, draft, pitot, safety, spillage, tube

Views: 369

Reply to This

Replies to This Discussion

I'm guessing that is the short metal tube that comes with the DG.  If that is the case, go with perpendicular to the pipe.  Might want to trim some of the pipe insulation off as well before the job is completed.  The insulation looks a little close to the vent, based just on the pictures above (clearance to combustables).

Thanks Dan. Yes, it's the straight tube from the DG bag. Interestingly, Minneapolis sells what they call a "Static Pressure Probe" and distinguish it from a "Pitot Tube", which they don't sell. Both are right-angled metal probes, the difference being that pitot tubes measure ram air (or velocity) pressure through an opening in the tip that static pressure probes don't have.

The principle is familiar to the aviation geek in me (aircraft use a pitot tube to measure airspeed and a static pressure port with an aneroid barometer to measure altitude). After further discussion in our office and examination of one the aforementioned static pressure probes, angling the tip toward the appliance would, in fact, align the holes in the probe perpendicular to the exhaust stream for a true static pressure reading. In that context, the technique I hear people cite about pointing the probe into the stream makes sense, as does your recommendation to hold the straight metal tube perpendicular to the flue.

I think the tight clearance is a result of the photo angle here.

A pitot tube on an airplane is pointed forward because you want to measure air speed and if it points into the wind it measures, well, the speed of the air.

Draft in a heater is different - we aren't looking for MPH but Delta P.  These are 2 different things.  Both the pitot tube and the bent static probe have holes perpendicular to the air stream so are measuring the same thing.  The straight pitot tube in a heater flue should point straight in to measure the same thing that the bent static probe measures when either pointed toward or away from the air stream.  

Interesting that, in your pictures, the probe pointed into the airstream measures zero.

Yep - and the static pressure port is usually on the side of the fuselage, perpendicular to the airstream.

The reading pointed toward the airstream fluctuated between -0.2 and 0.2 or so. If we interpolate the "true" static pressure as about -2.0 (halfway between zero and -4.1), then the interference of the velocity air pressure directly entering the tube, which the manometer would interpret as positive, explains the zero reading.

Isn't there a measurement missing here?...

Yeah, it should have been taken perpendicular to the flue, as Dan pointed out.

Too cryptic, sorry.  

Shouldn't there be another tube and another pressure being measured?...

Hmm. I've understood the intent to be measuring the delta P of flue gases and the ambient air, but it's been quite a few moons since I've done combustion testing on a regular basis. What am I missing here?

Ted

Still too cryptic

Where is the 2nd hose measuring caz depressurization?

I see what you mean - but the title of the thread is:

Which is the valid draft test, noir which is the valid CAZ test

Is it a valid draft test without both numbers?

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconSteve Mohler, Victor Couto, Melvin Calahan and 2 more joined Home Energy Pros
46 minutes ago
Aaren Stewart posted a discussion

HVAC - Cooling and Heating Load Reduction

Common load reduction strategies include:      Tightening your building covering and adding…See More
3 hours ago
Kevin Jordan posted a photo
8 hours ago
Mike Burton joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
10 hours ago
Hal Skinner replied to Trip Smith's discussion Starting a Home Weatherization Business. Considering it...
"Hi Tri,p Your 'Yard sign' comment caught my eye.  I work with a Radiant Barrier…"
10 hours ago
Profile IconEric Kjelshus and Trip Smith joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
13 hours ago
Bob Blanchette replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"When it costs the same price as 2 separate systems there is no juice regardless of how hard you…"
14 hours ago
j. west shared Christopher Morin's blog post on Facebook
19 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service