Where to install the vapor barrier for a finished basement?

I have an audit customer that is in the process of finishing his basement. The basement foundation walls are poured concrete. He has installed a polyethylene vapor barrier over the concrete wall per his brother's instructions who is a builder. He plans to install unfaced insulation in the 2 by 4 stud walls that are 2 inches away from the concrete wall. He will be also installing drywall and heating the space with his existing HVAC unit. This is an all-electric two story home located in Ohio.

 

I'm already recommending he seal the entire rim joist with foam since they are leaking a lot of air. The rim joists are currently fitted with faced fiberglass batts. My thoughts are to advise him to also foam the entire basement wall but I'm not sure this is the correct or the best solution. If he decides to install fiberglass batt insulation in the 2 by 4 walls, where should the vapor barrier be installed? The poured cement basement walls are dry with good drainage outside so I'm thinking the vapor barrier should be installed between the drywall and insulation since the basement will be a conditioned space.

Views: 51076

Reply to This

Replies to This Discussion

I'm referencing Joe Lstiburk's "Cold Climates" You should not install poly on the walls in the assembly. It will cause the wall to retain moisture. The key is to let the walls dry to the inside or the outside. I would also not use fiberglass in the basement because it is hydrophilic. A water resistant insulation would be a better material to use. I recommend you get a copy of "Cold Climates" it covers all the different areas in a house and the best methods for building and insulating.
Thanks Chris for your feedback. I will get Joe Lstiburk's book so I can add it to my reference library. 
You're very welcome.

Also, review the work of the Pat Huelman and the folks of the Cold Climate Housing Center. Pat and his people have done a lot of work in this area. And he and Dick Stone do a lot of training -- Affordable Comfort, the Duluth EDC conference, etc.

 

I don't believe any of their work contradicts the info in the "Builder's Guide: Cold Climates" book. But they may well have info on the most recent "miracle" materials out there intended to "allow" building assemblies that will just never work. (Like this goofy idea that you can successfully put a functioning vapor barrier on the warm side of a below-grade concrete wall!) 

Thanks Don for making me aware of Pat Huelman group. I'll definetly review their findings.

Jim,

Your question and the subsequent responses got me thinking. 

I tell myself I should know the answer to this question but I found myself wavering a bit.

I have “Cold Climates” but it has been awhile since I have reviewed it and looked at this wall profile.

 

Out of curiosity I searched the web and here is what I found at an EPA site.

http://www.epa.gov/indoorairplus/technical/moisture/1_12.html

 

“An appropriate assembly for the inside of a basement wall consists of 1 in. of plastic foam board or closed-cell polyurethane spray foam followed by a stud wall with fiberglass insulation filling the cavities. This assembly is covered with moisture- and mold-resistant gypsum board covered by two coats of latex paint. The foam board serves two purposes: providing a capillary break between the foundation wall and the stud wall and keeping warm, humid basement air away from the earth-chilled foundation. It is good practice to put 1 in. of foam board beneath the sole plate of the stud wall and the basement floor and to leave a ½-in. gap between the basement floor and the bottom of the gypsum board. Doing so provides protection from minor floods and damp concrete floors.”

 

Clicking the link provides additional explanation and context for this strategy.

I wonder if this is consistent with the other resources mentioned. If not i would like to hear others thoughts.

You can find an excellent publication on this question at http://www.buildingscience.com/documents/reports/rr-1003-building-a....  The publication presents many solutions and rates them on several criteria.  They also conducted detailed thermal and moisture modeling.

I put 2" XPS on my basement walls as a temporary way to add some insulation before I got to the task of finishing the basement walls. I did not seal the joints between the sheets or the gaps at the top and bottom of the sheets.  I had lots of ice on the top of the foundation wall and ice at every joint and gap down to the soil line.  A well sealed vapor barrier at the foundation wall is absolutely critical to preventing moisture problems.

After seeing the moisture/ice problems first hand, I think I will insulate the stud walls with closed cell foam to assure that I have no air leaks.  This will cost more but the peace of mind is worth it.  I live in a very cold climate near Yellowstone National Park.  We have had many consecutive days of -20 to -30 F this winter.  I am sure this contributed the ice formation behind the XPS and on top of the foundation wall.

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Earth Advantage posted an event
Thumbnail

CakeSystems™ Software Course at Webinar

March 4, 2016 from 9am to 11am
CakeSystems Software training is offered as a self-paced online course of 3-4 hours followed by a…See More
2 hours ago
Anthony Adams posted a blog post

Bonus room attic walls heat load

Hi Everyone...First of all I am 59yr old retired Federal employee. I took HVAC in a trade school 30…See More
5 hours ago
Tom White's video was featured

Multifamily Building Energy Innovation- TrueFlow Capture Box

Video explaining the new tool to help reduce the energy costs of effective ventilation in multifamily buildings.
9 hours ago
Alfie Davis posted a blog post

Utility of a Hardwood Staircase

Everything needs a makeover after a certain time. Your home is one of them.  Sometimes, you…See More
13 hours ago
miguel pace shared a profile on Facebook
18 hours ago
miguel pace liked miguel pace's blog post It is very important to select a fin fan
18 hours ago
Charles Ryan Weitzel posted a discussion

Oil Fired Boiler Being Used as the Heating Source in Two Air Handlers of a Historic Home

I'm not sure this makes any difference, but I've only run into a system like this here, where I…See More
23 hours ago
Ronald Wallis replied to Jonny Fisher's discussion Minneapolis Blower Doors and Duct Blaster for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"interested in your equipment. Do you have pics? Is equipment compliant with new regulations?"
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service