Where to install the vapor barrier for a finished basement?

I have an audit customer that is in the process of finishing his basement. The basement foundation walls are poured concrete. He has installed a polyethylene vapor barrier over the concrete wall per his brother's instructions who is a builder. He plans to install unfaced insulation in the 2 by 4 stud walls that are 2 inches away from the concrete wall. He will be also installing drywall and heating the space with his existing HVAC unit. This is an all-electric two story home located in Ohio.

 

I'm already recommending he seal the entire rim joist with foam since they are leaking a lot of air. The rim joists are currently fitted with faced fiberglass batts. My thoughts are to advise him to also foam the entire basement wall but I'm not sure this is the correct or the best solution. If he decides to install fiberglass batt insulation in the 2 by 4 walls, where should the vapor barrier be installed? The poured cement basement walls are dry with good drainage outside so I'm thinking the vapor barrier should be installed between the drywall and insulation since the basement will be a conditioned space.

Views: 13748

Reply to This

Replies to This Discussion

I'm referencing Joe Lstiburk's "Cold Climates" You should not install poly on the walls in the assembly. It will cause the wall to retain moisture. The key is to let the walls dry to the inside or the outside. I would also not use fiberglass in the basement because it is hydrophilic. A water resistant insulation would be a better material to use. I recommend you get a copy of "Cold Climates" it covers all the different areas in a house and the best methods for building and insulating.
Thanks Chris for your feedback. I will get Joe Lstiburk's book so I can add it to my reference library. 
You're very welcome.

Also, review the work of the Pat Huelman and the folks of the Cold Climate Housing Center. Pat and his people have done a lot of work in this area. And he and Dick Stone do a lot of training -- Affordable Comfort, the Duluth EDC conference, etc.

 

I don't believe any of their work contradicts the info in the "Builder's Guide: Cold Climates" book. But they may well have info on the most recent "miracle" materials out there intended to "allow" building assemblies that will just never work. (Like this goofy idea that you can successfully put a functioning vapor barrier on the warm side of a below-grade concrete wall!) 

Thanks Don for making me aware of Pat Huelman group. I'll definetly review their findings.

Jim,

Your question and the subsequent responses got me thinking. 

I tell myself I should know the answer to this question but I found myself wavering a bit.

I have “Cold Climates” but it has been awhile since I have reviewed it and looked at this wall profile.

 

Out of curiosity I searched the web and here is what I found at an EPA site.

http://www.epa.gov/indoorairplus/technical/moisture/1_12.html

 

“An appropriate assembly for the inside of a basement wall consists of 1 in. of plastic foam board or closed-cell polyurethane spray foam followed by a stud wall with fiberglass insulation filling the cavities. This assembly is covered with moisture- and mold-resistant gypsum board covered by two coats of latex paint. The foam board serves two purposes: providing a capillary break between the foundation wall and the stud wall and keeping warm, humid basement air away from the earth-chilled foundation. It is good practice to put 1 in. of foam board beneath the sole plate of the stud wall and the basement floor and to leave a ½-in. gap between the basement floor and the bottom of the gypsum board. Doing so provides protection from minor floods and damp concrete floors.”

 

Clicking the link provides additional explanation and context for this strategy.

I wonder if this is consistent with the other resources mentioned. If not i would like to hear others thoughts.

You can find an excellent publication on this question at http://www.buildingscience.com/documents/reports/rr-1003-building-a....  The publication presents many solutions and rates them on several criteria.  They also conducted detailed thermal and moisture modeling.

I put 2" XPS on my basement walls as a temporary way to add some insulation before I got to the task of finishing the basement walls. I did not seal the joints between the sheets or the gaps at the top and bottom of the sheets.  I had lots of ice on the top of the foundation wall and ice at every joint and gap down to the soil line.  A well sealed vapor barrier at the foundation wall is absolutely critical to preventing moisture problems.

After seeing the moisture/ice problems first hand, I think I will insulate the stud walls with closed cell foam to assure that I have no air leaks.  This will cost more but the peace of mind is worth it.  I live in a very cold climate near Yellowstone National Park.  We have had many consecutive days of -20 to -30 F this winter.  I am sure this contributed the ice formation behind the XPS and on top of the foundation wall.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
4 hours ago
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
7 hours ago
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
8 hours ago
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
8 hours ago
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
8 hours ago
Tom Delconte's blog post was featured
8 hours ago
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
8 hours ago
Edward Foskey's blog post was featured
8 hours ago
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
9 hours ago
Mike Rogers posted a blog post

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
12 hours ago
David Eggleton replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"That varies, as policies are different from state to state."
12 hours ago
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a Fluke TIR 32.  Used aproximately 10 times 1.5 yrs old.  This is the first…"
12 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service