Where to install the vapor barrier for a finished basement?

I have an audit customer that is in the process of finishing his basement. The basement foundation walls are poured concrete. He has installed a polyethylene vapor barrier over the concrete wall per his brother's instructions who is a builder. He plans to install unfaced insulation in the 2 by 4 stud walls that are 2 inches away from the concrete wall. He will be also installing drywall and heating the space with his existing HVAC unit. This is an all-electric two story home located in Ohio.

 

I'm already recommending he seal the entire rim joist with foam since they are leaking a lot of air. The rim joists are currently fitted with faced fiberglass batts. My thoughts are to advise him to also foam the entire basement wall but I'm not sure this is the correct or the best solution. If he decides to install fiberglass batt insulation in the 2 by 4 walls, where should the vapor barrier be installed? The poured cement basement walls are dry with good drainage outside so I'm thinking the vapor barrier should be installed between the drywall and insulation since the basement will be a conditioned space.

Views: 14596

Reply to This

Replies to This Discussion

I'm referencing Joe Lstiburk's "Cold Climates" You should not install poly on the walls in the assembly. It will cause the wall to retain moisture. The key is to let the walls dry to the inside or the outside. I would also not use fiberglass in the basement because it is hydrophilic. A water resistant insulation would be a better material to use. I recommend you get a copy of "Cold Climates" it covers all the different areas in a house and the best methods for building and insulating.
Thanks Chris for your feedback. I will get Joe Lstiburk's book so I can add it to my reference library. 
You're very welcome.

Also, review the work of the Pat Huelman and the folks of the Cold Climate Housing Center. Pat and his people have done a lot of work in this area. And he and Dick Stone do a lot of training -- Affordable Comfort, the Duluth EDC conference, etc.

 

I don't believe any of their work contradicts the info in the "Builder's Guide: Cold Climates" book. But they may well have info on the most recent "miracle" materials out there intended to "allow" building assemblies that will just never work. (Like this goofy idea that you can successfully put a functioning vapor barrier on the warm side of a below-grade concrete wall!) 

Thanks Don for making me aware of Pat Huelman group. I'll definetly review their findings.

Jim,

Your question and the subsequent responses got me thinking. 

I tell myself I should know the answer to this question but I found myself wavering a bit.

I have “Cold Climates” but it has been awhile since I have reviewed it and looked at this wall profile.

 

Out of curiosity I searched the web and here is what I found at an EPA site.

http://www.epa.gov/indoorairplus/technical/moisture/1_12.html

 

“An appropriate assembly for the inside of a basement wall consists of 1 in. of plastic foam board or closed-cell polyurethane spray foam followed by a stud wall with fiberglass insulation filling the cavities. This assembly is covered with moisture- and mold-resistant gypsum board covered by two coats of latex paint. The foam board serves two purposes: providing a capillary break between the foundation wall and the stud wall and keeping warm, humid basement air away from the earth-chilled foundation. It is good practice to put 1 in. of foam board beneath the sole plate of the stud wall and the basement floor and to leave a ½-in. gap between the basement floor and the bottom of the gypsum board. Doing so provides protection from minor floods and damp concrete floors.”

 

Clicking the link provides additional explanation and context for this strategy.

I wonder if this is consistent with the other resources mentioned. If not i would like to hear others thoughts.

You can find an excellent publication on this question at http://www.buildingscience.com/documents/reports/rr-1003-building-a....  The publication presents many solutions and rates them on several criteria.  They also conducted detailed thermal and moisture modeling.

I put 2" XPS on my basement walls as a temporary way to add some insulation before I got to the task of finishing the basement walls. I did not seal the joints between the sheets or the gaps at the top and bottom of the sheets.  I had lots of ice on the top of the foundation wall and ice at every joint and gap down to the soil line.  A well sealed vapor barrier at the foundation wall is absolutely critical to preventing moisture problems.

After seeing the moisture/ice problems first hand, I think I will insulate the stud walls with closed cell foam to assure that I have no air leaks.  This will cost more but the peace of mind is worth it.  I live in a very cold climate near Yellowstone National Park.  We have had many consecutive days of -20 to -30 F this winter.  I am sure this contributed the ice formation behind the XPS and on top of the foundation wall.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconDon Hughes, Julian Sark, James Hatheway and 4 more joined Home Energy Pros
1 hour ago
Meagan Foster posted events
2 hours ago
Meagan Foster updated an event

EnergyLogic's RaterFest! at Black Hawk, CO

September 13, 2013 at 10am to September 15, 2013 at 12pm
Join us for one of the best home energy conferences available!  This retreat will provide…See More
2 hours ago
Meagan Foster updated an event

Homes 401: Green Rater Training at Berthoud, CO

June 25, 2013 to June 26, 2013
This highly interactive workshop builds upon the material presented in the online course, further…See More
2 hours ago
Meagan Foster updated an event

HERS Rater Training - Online at Online

July 1, 2013 to July 26, 2013
NEW - our great RESNET HERS Rater online training is now completely self-paced, so you can start at…See More
2 hours ago
Meagan Foster updated an event

BPI Building Analyst Training - Online at Online

June 3, 2013 to June 28, 2013
Join the EnergyLogic Academy for our BPI BA online training - we just went to a completely open…See More
2 hours ago
Anna Svensson posted a discussion

Looking for residential building and remodeling experts

Making sure you residential building and remodeling professionals out there are aware of the call…See More
3 hours ago
Bryce Cramer joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
6 hours ago
Bryce Cramer replied to Mike Kandel's discussion June's Stump the Chump: What's Wrong with this Picture? in the group Building Performance Institute (BPI)
"Key is this was done in warm weather. The back wall of the room was also uninsulated, but the lower…"
6 hours ago
James Hatheway added a discussion to the group Job Board
Thumbnail

Quality Assurance Verification Specialist - Little Rock, Arkansas

CLEAResult (clearesult.com) is looking for a QA Verification professional who wants to leverage…See More
8 hours ago
Profile IconJames Hatheway and Mike Wallis joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
8 hours ago
tedkidd commented on Mike Rogers's blog post HOMES Act introduced with Bi-Partisan Sponsorship
"% savings programs suck.  Ask the folks in CA.  When your incentive structure pits…"
10 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service