BPI's April Stump the Chump: What’s Wrong with this Picture?

We know, we know. There’s a lot right with this picture, such as the gorgeous view of Lake Tahoe in the background and the awesome powder for skiing. But from a whole-house-as-a-system perspective, what’s wrong with this picture? What is the owner trying to do, and what would be a better solution?

Thanks to our own Larry Zarker, BPI CEO, for sending in this dandy shot. He offers the following Winston Churchill quote to explain what’s going on here: “You can always trust the Americans to get it right, after they have exhausted every other possibility”.

Think you know what the problem is, as well as the solution? Send it to us at lmcdowell@bpi.org.

 

Tags: April, Chump, Stump, building, newsletter, performance, the

Views: 369

Reply to This

Replies to This Discussion

Problem is Ice Dams.  The home most likely had melting of roof snow which then refroze and created ice dams possibly causing water damage or excessive ice buildup at roof edges. This caused the homeowner to install energy intensive heat strips to melt the ice dams and jack their electric bill through the roof during snow events.  

 

This is caused by:

1)      Air leakage from penetrations near exterior wall

2)      Heat sources close to exterior wall such as heating ducts or recessed lighting cans

3)      Insulation in contact with roof sheathing causing thermal bridging to roof deck

4)      Lack of soffit ventilation

 

The solution:

 

1)      Air seal exterior top plate with spray foam. It is also important to air seal any other penetration which is delivering heat to the underside of the roof deck.

2)      If recessed lighting is installed near exterior walls, the cans should be ICAT rated to prevent air flow through the fixture. An inexpensive air tight trim kit may also be purchased to avoid changing out fixture itself. Heating duct boots can be sprayed with 2 part foam to prevent heating of roof deck.

3)      Install soffit ventilation at code recommended level at EVERY BAY that is affected.

4)      Install insulation baffles at all soffit edges in order to provide a path for ventilation and carry away any remaing heat transferred from house and cool roof deck. This also prevents insulation from contacting the roof deck (causing thermal bridging).

 

Since it is often difficult to get full insulation amounts at the soffit edge due to clearance, an optimal solution would involve installing ventilation baffles and using spray foam insulation against the baffle and as far in until a full amount of blown insulation may be used. This solution also seals any air exfiltration through the wall top plate at the same time. 

 

 

Oh, and most likely, this is the north facing roof your looking at, unless you have tons of winter shade on the southern exposure.

Congratulations to Craig Bird of Preston Insulation in Tucson, Arizona for winning last month’s “What’s wrong with this picture?”contest. Craig was not only the first person to send in the correct answer. His answer was far and away the most comprehensive, and dare we say, the most elegant in illustrating what in the world of home performance was wrong with the picture, and what should be done about it.

The picture shows a snow-bound house in front of Lake Tahoe, its roof zig zagged with heat strips.  Says Craig:

“The problem is ice dams.  The home most likely had melting of roof snow which then refroze and created ice dams possibly causing water damage or excessive ice buildup at roof edges. This caused the homeowner to install energy intensive heat strips to melt the ice dams and jack their electric bill through the roof during snow events.  

 

This is caused by:

1)     Air leakage from penetrations near exterior wall

2)     Heat sources close to exterior wall such as heating ducts or recessed lighting cans

3)     Insulation in contact with roof sheathing causing thermal bridging to roof deck

4)     Lack of soffit ventilation

 

The solution:

1)     Air seal exterior top plate with spray foam. It is also important to air seal any other penetration which is delivering heat to the underside of the roof deck.

2)     If recessed lighting is installed near exterior walls, the cans should be ICAT rated to prevent air flow through the fixture. An inexpensive air tight trim kit may also be purchased to avoid changing out fixture itself. Heating duct boots can be sprayed with 2 part foam to prevent heating of roof deck.

3)     Install soffit ventilation at code recommended level at EVERY BAY that is affected.

4)     Install insulation baffles at all soffit edges in order to provide a path for ventilation and carry away any remaining heat transferred from house and cool roof deck. This also prevents insulation from contacting the roof deck (causing thermal bridging).

 

Since it is often difficult to get full insulation amounts at the soffit edge due to clearance, an optimal solution would involve installing ventilation baffles and using spray foam insulation against the baffle and as far in until a full amount of blown insulation may be used. This solution also seals any air exfiltration through the wall top plate at the same time. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconWes Anderson, Jean-Paul and Bryan joined Home Energy Pros
Friday
Dennis Heidner commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"Dale, good write up. For the landscaping bulbs,  if they had been T3 12V wedge bulbs,  I…"
Friday
Brett Little commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"It's very true! So many people and contractors have tons of insulated attics but no air seal…"
Thursday
Chris Leach replied to Richard Beyer's discussion "The Dangers of Using Spray Foam Insulation"
"The problems will surface soon enough . Why don't we take a second look at this over rated…"
Thursday
Don Fitchett commented on Tom White's video
Thursday
tedkidd replied to Bob Blanchette's discussion How does Cycles Per Hour affect real world AFUE?
"Want to spot a simpleton? It's a guy who thinks EE and comfort are disconnected.  Want…"
Thursday
tedkidd commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"Nice post Tom! I really like how he puts that. Leveraging interests so they can optimize…"
Thursday
Kent Mitchell commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"As a contractor in the region - we frequently wonder how/why you can be a non-profit?  Oregon…"
Thursday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service