What is the R Value of a 2x6 dense packed cellulose wall?

I am reviewing the requirements of the new Maine Uniform Building and Energy Code that goes into effect 12/1/2010.  The required R value for a wood framed wall is R20. If I assume the Dense Packed Cellulose has an R value of 3.4 per inch and a 2x6 is really only 5.5" deep, then 5.5" of cellulose is only R18.7 which doesn't quite meet the standard.

I could put in R21 fiberglass and meet the standard, but I am sure the cellulose would out perform the glass in the real world.

How does everyone else view this subject?

Views: 6170

Reply to This

Replies to This Discussion

According to National Fiber's website a 2 x 6 wall at 5.5 " thick has an R value of R20 when dense packed at 3.5 lbs per cubic foot. The reason the Code has a minimum wall insulation requirement of R20 is because thats as good as it gets with celluloce, if the cellulose manufacturers hadn't been allowed their input the minimum would be R21 (fiberglass batts).
Thanks for the reply Scott. I found that on the National Fiber site after I posted the message.

What approach do you plan to take to get R49 in a cathedral ceiling where the slope area is greater than 500 ft2 or 20% of the total ceiling area?



  • Add Videos
  • View All


Latest Activity

Benny hani replied to Benny hani's discussion Manual J online
"Thanks Bob"
51 minutes ago
Benny hani replied to Benny hani's discussion Manual J online
"Thank you Isaac"
52 minutes ago
Bob Blanchette commented on Amber Vignieri's blog post Even with Polar Vortex, Hourly Pricing Participants Saved
"Looks like the days of paying a fixed amount per KWh are rapidly coming to an end. Many utilities…"
2 hours ago
Bob Blanchette replied to Benny hani's discussion Manual J online
"Be sure the size that you ACCURATELY calculate actually gets installed. Often…"
2 hours ago
Bob Blanchette replied to Sean Lintow Sr's discussion Water Saver or Gimmick? in the group Best Practices (Residential)
"The problem is these devices NEVER pay for themselves. Water is cheap, about $3 per 1,000 gallons…"
2 hours ago
Bud Poll replied to Rob Madden's discussion Blower Door Testing on Energy Star v3 home
"Where was the blower set up, front door, other?  Was if located in an unobstructed area, not a…"
14 hours ago
David N. Armington liked John Poole's discussion Two Part Epoxy and Repair of Structural Wood
David N. Armington joined John Poole's group

Historic Home

Historic and vintage homes are significant to our cultural heritage, yet often lack energy…See More

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service