I've been on a tear of late to eliminate or minimize standby loads. This arises from data revealing that during spring and fall, when HVAC use is minimal, standby loads comprise 25%, 5 kwh / day of our home's total usage.

5 kwh / day exceeds the total usage of our entire kitchen - fridge, chest freezer, range, dishwasher, etc.

At national average electric rates of $0.11 / kwh, each Watt of standby usage works out to a buck a year, so the sneaky little loads add up fast.

An early victory came in the form of learning that the starting battery trickle charger on our standby genny consumes 30-35 Watts. A $40, 10 Watt PV panel from Amazon has allowed me to kill that load while still maintaining the genny's cranking battery.

We have 3 garage door openers, specifically Overhead Door Phantoms. They are quiet and have been relatively trouble-free. Imagine my shock at learning each uses 14.5 Watts while sitting and doing nothing.

Doing the math, the three (aptly named) Phantoms have cost us $200 in standby power since we built the house in early 2008.

Thoughts, anyone?

Views: 4292

Reply to This

Replies to This Discussion

Ok, I don't have time to read this whole thread, but let me just ask, do you really need 3 garage door openers? Is your garage heated and what do you think the energy loss is through those doors? How bis is your house and how many people live in it full time? I have a client who is very nice and well meaning and wealthy. She doesn't work, doesn't have to. She has a stunning home of probably 4000ish square feet in which she lives alone. I do not know if she has any other homes. She started bugging me on the phone about phantom loads from her $10000 entertainment center. Then she was bugging me because she was worried her 30 or so recessed lighting cans might be leaky. Then she paid some guy to do one of those air leak tests on her house. and had a whole host of other questions. Sometimes I see her driving around town in her $80k SUV and I can't help but wonder, who is she trying to kid, me or herself. We are rampant consumers in this country and we all seem to think we "deserve" our lifestyles because we work so "hard".
Unplug two of the openers and use only one. The other two will be fine spares when the active one wears out.

Coincidentally, your recommendation is how we are now operating - 1 bay is unplugged, 1 bay is left plugged in (wife and kids) and 1 bay is rigged with an extension cord for intermittent use (my occasional use car)


House is 3400 SF, 5 residents, future aging family apartment included.

We don't "need" 3 garage door openers, and this thread wandered off into a multi-page debate about lifestyles, but my original complaint / inquiry was about excessive standby loads by the garage door openers and how I might mitigate them.

As to your client, start assisting her, but be sure to invoice for advice given and value received

I must admit, that client really means well. She is very nice and trying to educate herself about waste and consumption. I believe she bought this house before she had ever spent much time considering these issues. She had some electrical use issues and I recommend she look at her water use and well system. It turned out she had some buried leaks in the supply for her drip irrigation.
I came to the realization a long time ago that the quickest way to reduce my "everything" footprint would be to simplify where practical, and add only after serious consideration. Now if only I could explain that to my wife!

I appreciate everyone's feedback regarding the specifics of my garage door opener standby power.

As to the much wider philosophic differences, I'm "through with engines"

Seems to me the quick easy would be to install a simple switch to shut off power once all the vehicles are in the garage for the night.  Most garages have all of their garage door switches centrally located near the entry door to the home.  bundle up the positive leads to a switch and let the owner turn it off once the garage is full and on again the following morning.

Unless they are night owls, they should be able to cut their yearly phantom load by 1/3.  Cost = $5 plus install time.

Thanks, but alas not so easy - door opener receptacles in ceiling hardwired back to elec panel dedicated breaker. No handy wall switch...

I haven't tried it myself, as we don't pay that much attention to phantom loads in my shop, we're more about the bigger stuff.  Still, I would think there would be a way that if you kill the on/off switches, which send a singal to the motor unit, there would be a way to shut that off by the same means.  Might have to add ind. relays at the main units as well.  Just a thought - trying to brainstorm here is all...

I appreciate the extra set of eyes on this one - I just don't want to incorporate extra complications into operating the doors as such would eat into the convenience of having them in the first place.

The first time I or my wife rolls up and the door won't open, necessitating a walk up around in down and back will be cause for complaint...same when kids are all loaded up and have to get back out and turn power on - we often run late anyway.

I will solve this in a manner transparent to users.

This is a long thread.  Quick question.  Did you ever find an acceptable solution.

Not yet - the motors are DC, and I've toyed with the idea of running all three off just one of the three standby-hungry big iron transformers. Another option would be to lose the iron altogether and run all three from a mid size deep cycle 12 VDC battery on a very small trickle charger. That would be a substantial rebuild of the openers and I haven't time to take that on. I haven't come up with a wiring diagram, either.

Ironically, newer generation openers take advantage of the DC motors by way of offering a battery backed up opening capability during power outages.

The situation still annoys me greatly - those 3 comprise 1/4 of total house standby load.

Thanks for the feedback.  My situation is not as bad.   My opener takes 6 Watt at idle, but it still really bothers me.  I'm not sure if I would have the ambition dig in to changing the power supply to the opener.

Curt are you sure they are DC?  The original transformer if I remember correctly was 12VAC 180VA.  That is about a 15Amp max 12volt AC circuit.  (per your early thread).

Check and see if you can get service manual either online or from manufacturer.  The 12VAC circuit when rectified would get you 1.414 X the 12VAC -- roughly 17Volts DC,  so they must have some kind of regulation circuit for the motor - and some really good filtering.  My guess is the only time you really hit the full load on the transformer is if the door is jammed.  

You can find 12VDC switched mode power  supplies (SMPS) that are much closer to the 90% efficient when under load.  But they less efficient when lightly loaded.   So the suggestion -- if you can find the service manual -- is to separate the motor onto its own power supply - put the receiver on its own small supply.  Only enable the big transformer / or new 12VDC SMPS when receiver says open/close.

But then for all the effort and cost of making the changes -- it can be easier just to replace the openers.

Remember that worse case for the motor - is when it is jammed and must immediately reverse.  This can happen if a small child falls and is trapped under the door.  Garage openers in the last twenty or thirty year are designed to sense the jam and ALWAYS be able to open the door,  Changing out power supplies,  moving to a battery, or solar panels - if not carefully done - might negate the safety feature.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconWes Anderson, Jean-Paul and Bryan joined Home Energy Pros
yesterday
Dennis Heidner commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"Dale, good write up. For the landscaping bulbs,  if they had been T3 12V wedge bulbs,  I…"
yesterday
Brett Little commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"It's very true! So many people and contractors have tons of insulated attics but no air seal…"
yesterday
Chris Leach replied to Richard Beyer's discussion "The Dangers of Using Spray Foam Insulation"
"The problems will surface soon enough . Why don't we take a second look at this over rated…"
yesterday
Don Fitchett commented on Tom White's video
yesterday
tedkidd replied to Bob Blanchette's discussion How does Cycles Per Hour affect real world AFUE?
"Want to spot a simpleton? It's a guy who thinks EE and comfort are disconnected.  Want…"
yesterday
tedkidd commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"Nice post Tom! I really like how he puts that. Leveraging interests so they can optimize…"
yesterday
Kent Mitchell commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"As a contractor in the region - we frequently wonder how/why you can be a non-profit?  Oregon…"