Had our furnace and air ducts cleaned today for the first time in years; could have spun an entire dog from all the embedded hair. The serviceman tried to upsell me with both a new reusable filter (to get 94% of the airborne substances), and a UV light to be installed in the furnace to get the other 6% worth of mold spores, bacteria and no-seeums. I bought the filter and also a thorough cleaning of the furnace, but am waiting to decide on the UV light--another $400--until I can determine if this will really improve our indoor air quality. The house is 1000 sq ft, one dog and two dogwalkers live there. Any opinions? One dogwalker (me) has asthma. I couldn't find any research from a casual googling.
Tags:
Permalink Reply by Bob Blanchette on January 28, 2013 at 6:20pm The 4" thick media filters are the best filtration system IMHO.
Permalink Reply by Curt Kinder on January 28, 2013 at 6:42pm Exactly what we supply...4 or 5" media cabinet and deep pleated filter. They generally last 6 months, and we change them during spring / fall PM visits if the client does not want to be bothered.
Permalink Reply by Stanley Sattinger on January 28, 2013 at 7:22pm I agree with Bob about 4" pleated filters, but would add two criteria. First, you will want a MERV rating of 10 or higher to ensure you're trapping small enough particles to guard against asthma. Second, you should consult the filter manufacturer's specifications to be sure that the pressure drop across the filter will be no greater than a few tenths inch water column at the filter face area and air flow velocity of your furnace. Pressure drops higher than this will penalize the furnace's output efficiency (actual vs. nominal BTU/hr delivered) and could shorten the life of the heat exchanger.
Permalink Reply by Bob Blanchette on January 29, 2013 at 4:08am Even the Merv 8 filters are MUCH better than just about any 1" filter you can buy. No they don't catch everything, but static pressure drop is much lower. With Merv 10 filters you need 2 of them to keep static reasonable unless you have a small HVAC system. 4" Merv 8 media is under $10 at our local supply house, Merv 10 is special order. Now if somebody would make 4" media filter cabinets for a reasonable cost then more HVAC contractors would install them.
Permalink Reply by Robert H on January 31, 2013 at 10:21am $400 is over priced.
What you should know about furnace filters is that they should only do a marginal job of removing air borne particulates. The more you filter the more you restrict the air flow and hurt the efficiency of your furnace. Those expensive 1 inch filters start out restrictive and only get worse as they get dirty.
If you look at a 4in filter they are not super efficient but they provide a lot of area so they last long. One brand I see is either a merv 8 or 10 depending what box is checked on the side of the filter.
I recommend a mid level filter, about a merv 8 to 10 for a balance of air flow and filtering. The 94% filter is probably a merv 8.
For UV lights, they are meant to work in conjunction with a filter. They will kill the smaller mold spores that though a filter and also kill airborne viruses and bacteria that arent filtered. They are very safe as long as you dont have direct exposure to the light, contained in HVAC system. They are used in hospital operating rooms and food processing plants. They are also used to purifiy water. Anything over $250 is probably over charging. Also the bulbs must be changed every year as the UV output declines even though they will still put out light.
If you are looking for better filtering get a good room air purifier. I sell Austin Air room air purifiers. They have a very good and long lasting HEPA filter and a very large charcoal filter. The filter should last 5 years.
Permalink Reply by John Nicholas on February 7, 2013 at 7:40am Indoor air quality starts with a lot of things! The last item you do is filter. Why allow everything into your home and then try to find it and remove it.
Large High efficiency filters at the air handler create more problems then they solve. If you got stuff in your duct work, and it is not moving, it isn't much of a problem. EPA does not recommend Duct Cleaning for indoor air quality.
In Floor returns should have a filter at the floor. This will not effect the static pressure of the duct system. If your dog is putting a lot of hair there. Keep it out of the system to begin with.
The only time to worry about Mold Spores, is when you add water. Keep the water out. Mold spores are not an issue. There are more mold spores in the bag of compost or mulch you spread outside on a Saturday, then in your home. Until you add water, they don't cause you a problem.
Permalink Reply by Bob Blanchette on February 7, 2013 at 3:37pm The 4" 8 MERV air filters are low cost, and have good static pressure ratings. There's no reason NOT to use them unless it's difficult/expensive to retrofit a 4" cabinet into the system. IMHO they should be standard on new installations. The 1" fiberglass filters that protected the 8 fins per inch A-coils of the 70's aren't adequate for todays high efficiency coils.
Permalink Reply by Allan Mullaly on February 16, 2013 at 3:38am Try Clean Air Heat to analyze the best condition. I have Amana furnace and it works quite well, For duct cleaning I recommend in a year at least and if there are pets in a home so it should be asked for any good expert.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Jack Sadyak commented on Jack Sadyak's blog post Why Getting a Quantum Heat Pump is a Better Choice?
southernelevations posted a blog post
Dennis Heidner commented on Macie Melendez's blog post Passive Proponent—Q&A with Brandon Weiss
John Wes joined James Sayers's group
John Wes joined Tom White's group
John Wes joined James Sayers's group
John Wes joined allen p tanner's group
Greg Whitchurch commented on Macie Melendez's blog post Passive Proponent—Q&A with Brandon Weiss
Greg Traster posted a blog post
Mark Richardson commented on Mark Richardson's group Renewable Energy
peter chang replied to peter chang's discussion Electrical system data loggers© 2013 Created by Lawrence Berkeley National Laboratory.