Well I have to admit that I'm stumped with an energy audit I've been working on for the past two months. Perhaps someone can point me in the right direction...
My client contacted me concerned that his electric bills were atrocious. They were, to the tune of 34,680 kWh per year (average monthly at 2,890 kWh, and a baseline of 2,347 per month!). And after my first visit to his home, it was very obvious to me that, although he has a big house (3700 sq-ft), he and his family of four were energy frugal, being careful to shut off lights when not in use, using power strips for entertainment centers, etc.
He was particularly concerned about the phantom consumption when he and his family would leave for several weeks at a time. When they did he'd shut off everything but the alarm system. And even then he'd see a bill of 1900 kWh for that month, and for what?
So I dove in deep, taking this on as a personal project, since he'd had an auditor from the utility company come out previously and they couldn't find anything. One of the first things I did was to install a PowerSave EnviR monitor on the two mains into the main circuit panel and let that thing collect data for exactly two weeks. I compared this kWh total to what the utility company's meter read and found a discrepancy of about 500 kWh in favor of the utility company. This closely paralleled the additional 10k kWh per year that I could not account for in my projected analysis. Hmmm.... found it! (or so I thought)
So I got on the phone and was soon in touch with the supervisor of the electric meter department. I told him my findings so he and I got together at the client's home one day so that he could test their equipment, which consisted of a transformer/transducer system which reduces the incoming current from the main transformer at the street. After a good hour of testing he informed me that their equipment tested okay. Hmmmm.... bummer.
After many hours of monitoring individual circuits, extrapolating the long-term consumption, I still can't account for this additional 10k kWh per year anomaly. I even looked for hidden conduits coming off the wiring gutter under the transformer, assuming a neighbor might be "borrowing" some power for their growing operation. Nothing. Absolutely nothing.
And now that I've been so thorough with my investigation and extrapolation, I'm left scratching my head, wondering if, even though the utility company tested their equipment as good, perhaps it is not over a long term. I honestly don't know where to go from here... Suggestions?
Permalink Reply by Ed Minch on July 19, 2012 at 7:53am I have a good friend who is head of demand side management for a large regional utility. He tells me that if someone complains that the meter is bad and pushes the issue, they will replace it. They will always test the meter just to see, and he says they see far less then 1% that are bad.
Not sure how to add to watch list... (sorry for the post)
Permalink Reply by David Meiland on July 19, 2012 at 6:39pm
Permalink Reply by Diane Chojnowski on July 20, 2012 at 6:32am Ted, There is a Follow link just under the Reply box above, but by default you automatically follow any discussion that you comment on or reply to.
Permalink Reply by peter chang on July 21, 2012 at 4:31pm Rod, your case interests me. I also have a client who is having these sorts of issues. The problem has only come to light in the past few months, and I believe that they are located in your neck of the wood. I have begun basic evaluation of the 3 services on the property but am most troubled about one of them in particular. I have not yet installed independent metering equipment because I don't see how this could solve anything. I have a feeling this will settle itself out in the coming months but I have a distrust of some of the utility and communications companies based on a studied paranoia and am always looking to become more informed. I have some ideas about strategies that might reduce the disadvantages of buying power from monopolies.
Permalink Reply by Rod Fox on July 23, 2012 at 11:12am Peter, if you "have some strategies that might reduce the disadvantages of buying power from monopolies", by all means, you might want to share those. I'm sure everyone would love to hear about it. Otherwise, your posting might look as though it is a phishing or spamming attempt. Sure hope it isn't.
Independent monitoring equipment is really the only way in which you can identify the problem. If the problem has only come to light in the past few (record heat) months, then I would certainly focus my attention on sources of cooling, like A/C and fans. And if they have a pool, I'd also look there.
I intend to post more of my findings after my return to NM on the 7th of August. I hope to find out more when I'm able to perform a few more onsite diagnostics and monitoring. Stay tuned....
Permalink Reply by peter chang on July 23, 2012 at 5:59pm
Permalink Reply by Rod Fox on July 23, 2012 at 8:45pm So sorry about that phishing comment, Peter. I think I read your comment immediately after I read this article by Bill McKibben and my blood was still boiling in anger over the whole mess. Seems our jobs in this industry might not make a difference whatsoever...
But I continue to plod on, 'cause it's got to make a difference...
Anyways, I'm still going to monitor this client for another complete 7 days. But this time I'll do it with another manufacturer's product. I've asked the utility guy to get me the make/model of the monitoring system they use. I'm still waiting for that reply. I'm optimistic that he will. If not, I'll suspect something is askew and become the newest Bill McKibben...
Permalink Reply by peter chang on July 24, 2012 at 8:16pm
Permalink Reply by Tom Delconte on July 25, 2012 at 9:58am GE seems to think electric meters are super-duper accurate! : Ask the Ge engineer . Waiting to see how your client issue plays out.
Permalink Reply by Rod Fox on July 25, 2012 at 11:12am An update for you all...
The utility guy has used their own 3rd party monitoring system twice now at my client's place. The first was for a week while the clients were home and the second was for a week while they were out of town and had shut off all circuits except the one for the alarm system.
It had been a while since I last heard from the utility guy so I sent an email with a request that he provide all of the data he'd collected. No response. I've tried calling and left messages. No response. Not sure what's going on with this, so I called his boss and left a message. No response yet.
Hmmmmm......... makes me wonder what's in that data?
Why don't people realize that honest mistakes are only honest when you don't hide them?! Only transparency can set them free!?!
We are all human, so we all are likely to make multiple mistakes every DAY. We are all juggling a LOT of balls, isn't dropping them once in a while to be expected? Addressing a small problem up front prevents it from becoming magnified 1000's of times, turning into a Federal case. Prevents it from turning into a fire-able offense.
Hiding an honest mistake can turn it criminal really quickly. That kind of bad judgement should get people fired.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Nick Helmholdt replied to Joshua Knittel's discussion Google Thermal View? in the group INFRARED THERMOGRAPHY USERS
Paul Scheckel posted a blog post
Tom Delconte posted a blog post
Joe Huang posted a discussion
Joseph Lamy commented on Jim Gunshinan's blog post The Universe Is Made of Stories
J.C. Martel replied to J.C. Martel's discussion Disasters & sustainable energy
Judi Lyall joined allen p tanner's group© 2013 Created by Lawrence Berkeley National Laboratory.