Treating crawl spaces (with ductwork) when the adjacent basement ceiling is insulated.

I am currently speaking with a homeowner who would like to replace the existing FG batt insulation in the ceiling above his crawl space. The crawl is connected to the basement, and the basement ceiling is insulated with FG batts as well. The crawl has ducts insulated to R-4.2 throughout it. The crawl floor is a thin layer of concrete (about 1").

I spoke to him of two options:

1. Slap R-19 un-faced FG batts in the ceiling, and then slap 1/2" to 1" of foil-faced rigid foam to the underside of the floor joists.

OR

2. (This is my preference). Lay down 6-mil poly across the floor of the crawl, and adhere the poly to the crawl walls (up a couple of feet). Then install 2" of foil-faced rigid foam to the crawl walls. 

I will also be insulating the rim\band joists throughout the basement.

Any advice?

Views: 261

Reply to This

Replies to This Discussion

I agree with your preferred option.  If the connected space is climate controlled then stopping moisture and outside air from entering is the best option.  Only putting the FG batts in the ceiling of the crawl space would still leave the influx of air to deal with and it would decrease the efficiency and comfort of the home.

Thanks Tim. I have been pushing this option, and I think the homeowner is going to bite.

I would suggest a true vapor barrier product or ASTM  E-1745

From my short education on the product you want to make sure that the product is rated for the application. It is critical that the product is mechanically fastened to the wall and sealed. If there are any piers the product should be fastened and sealed to it as well.All seams sealed with tape approved for the product

I use 1x2  and ramset for fastening and duct mastic for sealing.

It is tedious, boring and often unappreciated in a challenging space.

I would always be concerned about the walls ability to dry. If the outside stem wall is buried I would think twice before insulating it

That is some really valuable input Glen. I definitely will continue to think this one through.

Thanks.

Patrick

RSS

Forum Discussions

Investigating 3257KWH monthly usage issue.

Started by Brent Shapiro in General Forum. Last reply by Mike Pagozalski 13 hours ago. 9 Replies

What made this chimney fall down?

Started by Eric Kjelshus in General Forum. Last reply by Eric Kjelshus Jun 15. 5 Replies

Studies on Home Energy Audit Energy Savings Potential?

Started by Julie Saporito in General Forum. Last reply by Danielle Sass Byrnett Jun 15. 5 Replies

Latest Activity

Caleb Hill is now a member of Home Energy Pros
8 hours ago
Mike Pagozalski replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"I would strongly recommend having an actual licensed electrician come out evaluate the entire…"
13 hours ago
Green ID posted blog posts
yesterday
Brad Cook replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"Jason's suggestion my be a quick way to isolate the high load, IF you have an old style meter…"
yesterday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service