Hi, in order to test spillage on an induced draft furnace, the BPI tech specs say to test at the base of the flue. Does this mean that spillage should be tested directly next to the draft inducer inside the furnace? Or does this mean elsewhere?

Views: 284

Reply to This

Replies to This Discussion

I hope the attached picture is clear enough for you to see.  As the caption on the picture states - There are a surprising number of potential spillage sites on an induced draft furnace.  Basically anywhere there is a connection, joint or hole.  Burners are the largest hole.  Combustion gases can exit out past the burners rather than continue their path up the heat exchanger and out the intended flue vent.

Attachments:

Monitor the pressure in the vent, if its positive in the vent for more than a minute it is most likely backdrafting.

Use smoke at the hole you've drilled to take your CO measurement.

When sharing a vent with a water heater check for spillage at the water heater draft hood.

I've never had any luck determining spillage at the base of the flue as theres a lot of moving air there from the inducer motor.

RSS

Groups

Latest Activity

Alfie Davis posted a blog post
yesterday
Profile IconSam Compton, Cameron Home Insulation, Seth Shoneman and 2 more joined Home Energy Pros
yesterday
Home Energy Magazine's blog post was featured
Monday
Eric Kjelshus replied to Gregory Cisco's discussion Abandoning under-slab HVAC ductwork which fills with groundwater seasonally.
"In Kansas City a lot of "cardboard" for supply was used in slab on grade.  1950-1970…"
Friday
Richard L. Rue replied to Sonja Persram's discussion Energy Savings Guarantee for single family dwellings in cold climate??
"Try EnergyWise Structures (www.energywisestructures.com) They are a NASA spin-off company that has…"
Friday
Debra Little commented on Home Energy Magazine's blog post NREL Research Finds That 22% of New Homes Completed in the U.S. in 2016 Were HERS Rated
"The avg scores are interesting. Are there comparative numbers for previous years? I thought they…"
Friday
Home Energy Magazine posted a blog post
Friday
Robert Zockoff replied to Gregory Cisco's discussion Abandoning under-slab HVAC ductwork which fills with groundwater seasonally.
"Public water systems regularly "reline" the interior of existing 50 year old water mains…"
Friday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service