Hi, in order to test spillage on an induced draft furnace, the BPI tech specs say to test at the base of the flue. Does this mean that spillage should be tested directly next to the draft inducer inside the furnace? Or does this mean elsewhere?

Views: 284

Reply to This

Replies to This Discussion

I hope the attached picture is clear enough for you to see.  As the caption on the picture states - There are a surprising number of potential spillage sites on an induced draft furnace.  Basically anywhere there is a connection, joint or hole.  Burners are the largest hole.  Combustion gases can exit out past the burners rather than continue their path up the heat exchanger and out the intended flue vent.

Attachments:

Monitor the pressure in the vent, if its positive in the vent for more than a minute it is most likely backdrafting.

Use smoke at the hole you've drilled to take your CO measurement.

When sharing a vent with a water heater check for spillage at the water heater draft hood.

I've never had any luck determining spillage at the base of the flue as theres a lot of moving air there from the inducer motor.

RSS

Groups

Latest Activity

Safe-R Insulation commented on Chris Laumer-Giddens's blog post Rock Wool Insulation for Floor of High Performance Tiny House
"Thanks for sharing this much information about roof wall…"
13 hours ago
Lindsay Bachman's 4 events were featured
yesterday
Profile IconChris Hoskins and Ken Goodrich joined Home Energy Pros
yesterday
Diane Chojnowski commented on Diane Chojnowski's event Better Buildings Peer Exchange Call: Home Improvement Catalyst: Keeping the Ball Rolling with Homeowners by Delivering More Value
"Hi Victor, All the BBRN Peer Exchange Calls are archived so you can listen anytime. Check out over…"
yesterday
Victor Rols Lindsay commented on Diane Chojnowski's event Better Buildings Peer Exchange Call: Home Improvement Catalyst: Keeping the Ball Rolling with Homeowners by Delivering More Value
"Hi Diane, Unfortunately some of us are unable to partake in this webinar/ forum. Is there a…"
yesterday
Ken Summers replied to Gregory Cisco's discussion Abandoning under-slab HVAC ductwork which fills with groundwater seasonally.
"My largest concern is moisture. I have seen mold forming on interior walls in the heating season…"
Thursday
Seth Romme replied to Sonja Persram's discussion Energy Savings Guarantee for single family dwellings in cold climate??
"Hi Sonja We provide home energy optimization services and provide a 5-year heating and cooling…"
Thursday
Lindsay Bachman posted events
Thursday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service