Strategies for insulating on top of & around heat sources in attics (such as recessed light fixtures).

I have been going by the rules of the program admins in my region when it comes to how to treat heat sources in attics when preparing to insulate attics with blown-in insulation. The standard operating procedure is to "dam" around heat sources (mainly recessed light fixtures) using un-faced FG batt insulation. The damming must be at least a few inches higher than the installed depth of the blown-in insulation. The end result is that blown-in insulation does not end up covering the heat source and potentially cause a fire-related problem.

But, I have been pushing for the fabrication of "boxes" made of materials such as gypsum board or aluminum flashing so that insulation can be blown on top of & around the boxes. Any thoughts on this strategy, or other strategies you'd like to put on the table?

Thanks in advance.

Patrick

Views: 213

Reply to This

Replies to This Discussion

Hi Patrick, If you have looked at those dams with IR with the heat source on you know they are dumping heat like mad.  Exactly what you can do should be discussed with the local code official.  IMO, a proper covering that would allow a full insulation layer over it is needed.  Doing such without breaking the rules, the fire codes, and electrical codes is the trick and only the AHJ can answer that.  But don't apply the same solution to another district without talking to that official as each may have their own rules.  Personally, I advise they replace the fixture with a IC/AT rated, but the real world needs an easier fix.

Bud

Very good and proper advice. Looks like it's back to the conversation with the code officials.

One of your arguments to present to your code official is that lights can be installed in small enclosed drop ceilings, like a kitchen drop that was created after the drywall was installed.  I have not seen instructions stating that the area above has to be open to an attic and many are installed in joist cavities between floors.  Logic is on the side of the Gypsum box Bob is suggesting, just need the ok to use it.

Bud

This was my sense as well, so I appreciate you raising that example.

Gypsum board would be good to make the "box" out of. It's easy to work with and cheap. probably wouldn't be a bad idea to box in all of the attic electrical boxes/bathroom fans and use some foam sealer or drywall mud to seal them up.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Mary Knox replied to Kim Tanner's discussion Game of Homes
"Sounds interesting. I will definitely try it."
53 minutes ago
Judy Roberson joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
5 hours ago
Peter Cantone liked Tom White's blog post Energy Raters and Builders Raise the Bar for Home Performance at RESNET’s Building Performance Conference
14 hours ago
Diane Chojnowski's 6 events were featured
14 hours ago
Diane Chojnowski posted events
14 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

What's the Value of a Life Saved?

With the recent release of the Healthy Home Evaluator (HHE) credential, we thought it timely to…See More
15 hours ago
Laurel Elam liked Tom White's blog post Energy Raters and Builders Raise the Bar for Home Performance at RESNET’s Building Performance Conference
16 hours ago
Hannah Finch liked Tom White's blog post Energy Raters and Builders Raise the Bar for Home Performance at RESNET’s Building Performance Conference
16 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service