Strategies for insulating on top of & around heat sources in attics (such as recessed light fixtures).

I have been going by the rules of the program admins in my region when it comes to how to treat heat sources in attics when preparing to insulate attics with blown-in insulation. The standard operating procedure is to "dam" around heat sources (mainly recessed light fixtures) using un-faced FG batt insulation. The damming must be at least a few inches higher than the installed depth of the blown-in insulation. The end result is that blown-in insulation does not end up covering the heat source and potentially cause a fire-related problem.

But, I have been pushing for the fabrication of "boxes" made of materials such as gypsum board or aluminum flashing so that insulation can be blown on top of & around the boxes. Any thoughts on this strategy, or other strategies you'd like to put on the table?

Thanks in advance.

Patrick

Views: 193

Reply to This

Replies to This Discussion

Hi Patrick, If you have looked at those dams with IR with the heat source on you know they are dumping heat like mad.  Exactly what you can do should be discussed with the local code official.  IMO, a proper covering that would allow a full insulation layer over it is needed.  Doing such without breaking the rules, the fire codes, and electrical codes is the trick and only the AHJ can answer that.  But don't apply the same solution to another district without talking to that official as each may have their own rules.  Personally, I advise they replace the fixture with a IC/AT rated, but the real world needs an easier fix.

Bud

Very good and proper advice. Looks like it's back to the conversation with the code officials.

One of your arguments to present to your code official is that lights can be installed in small enclosed drop ceilings, like a kitchen drop that was created after the drywall was installed.  I have not seen instructions stating that the area above has to be open to an attic and many are installed in joist cavities between floors.  Logic is on the side of the Gypsum box Bob is suggesting, just need the ok to use it.

Bud

This was my sense as well, so I appreciate you raising that example.

Gypsum board would be good to make the "box" out of. It's easy to work with and cheap. probably wouldn't be a bad idea to box in all of the attic electrical boxes/bathroom fans and use some foam sealer or drywall mud to seal them up.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Tom Mallard replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"Right, that reinforces my understanding of how it works, I was after what to plug in for values in…"
6 minutes ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"Products like these dont have an R-rating. You still have to have the R-rated insulation to meet…"
51 minutes ago
Graham Irwin replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Thanks for the input. The next question to ask is "how much cooling power is delivered in each…"
1 hour ago
Brandon Walton commented on Brandon Walton's blog post 12 Things Every Home Performance Contractor Should Have on Their Work Truck
"Totally off topic William, but yeah could use a bit more I suppose "
1 hour ago
William H Nickerson commented on Brandon Walton's blog post 12 Things Every Home Performance Contractor Should Have on Their Work Truck
"One more thing...you need a little more bend in that cap"
2 hours ago
Tom Mallard replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"Sounds like the perfect, thin insulator adding enough thermal inertia to separate two masses and/or…"
2 hours ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"OK Tom, I think I am on the last questionow,,,I think.  LOL Going under the building and…"
4 hours ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"Tom, sorry for having to break this up but my responses I guess are too long. You talking about the…"
4 hours ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
" "
6 hours ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"I guess I got too mlong winded ther, it cut me off. 1.  Spray the coating on the ducts, plenum…"
6 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Jan, Here are some facts. the 30 inch fan from Home Depot (not one I would recommend) is rated at…"
6 hours ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group Radiant Control Coatings
"Hi Tom. It looks like I will have to start off most of my answers to questions with this…"
7 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service