Strategies for insulating on top of & around heat sources in attics (such as recessed light fixtures).

I have been going by the rules of the program admins in my region when it comes to how to treat heat sources in attics when preparing to insulate attics with blown-in insulation. The standard operating procedure is to "dam" around heat sources (mainly recessed light fixtures) using un-faced FG batt insulation. The damming must be at least a few inches higher than the installed depth of the blown-in insulation. The end result is that blown-in insulation does not end up covering the heat source and potentially cause a fire-related problem.

But, I have been pushing for the fabrication of "boxes" made of materials such as gypsum board or aluminum flashing so that insulation can be blown on top of & around the boxes. Any thoughts on this strategy, or other strategies you'd like to put on the table?

Thanks in advance.

Patrick

Views: 206

Reply to This

Replies to This Discussion

Hi Patrick, If you have looked at those dams with IR with the heat source on you know they are dumping heat like mad.  Exactly what you can do should be discussed with the local code official.  IMO, a proper covering that would allow a full insulation layer over it is needed.  Doing such without breaking the rules, the fire codes, and electrical codes is the trick and only the AHJ can answer that.  But don't apply the same solution to another district without talking to that official as each may have their own rules.  Personally, I advise they replace the fixture with a IC/AT rated, but the real world needs an easier fix.

Bud

Very good and proper advice. Looks like it's back to the conversation with the code officials.

One of your arguments to present to your code official is that lights can be installed in small enclosed drop ceilings, like a kitchen drop that was created after the drywall was installed.  I have not seen instructions stating that the area above has to be open to an attic and many are installed in joist cavities between floors.  Logic is on the side of the Gypsum box Bob is suggesting, just need the ok to use it.

Bud

This was my sense as well, so I appreciate you raising that example.

Gypsum board would be good to make the "box" out of. It's easy to work with and cheap. probably wouldn't be a bad idea to box in all of the attic electrical boxes/bathroom fans and use some foam sealer or drywall mud to seal them up.

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Profile IconTirso De Ubago, Hamed Ghanbari, Bob Eldredge and 1 more joined Home Energy Pros
5 hours ago
Hamed Ghanbari replied to Brian's discussion Everything you need to become a energy auditor for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hello, I am interested to buy a Minneapolis Blower Door DG700. How much is your unit? Thanks. "
8 hours ago
Hamed Ghanbari joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
8 hours ago
Colin Genge updated an event
Thumbnail

Measuring HVAC Performance webinar at Online

February 23, 2016 from 11am to 12pm
If you install, service or test HVAC systems you will want be there for this special webinar.…See More
12 hours ago
Colin Genge updated an event
Thumbnail

Testing for IECC Code Compliance for duct and house leakage webinar at Online

February 16, 2016 from 11am to 12pm
The International Energy Conservation Code (IECC) is in use or adopted in 47 states, the District…See More
12 hours ago
Jan Green posted a status
"I'm honored to be selected to speak at the 2016 RESNET Conference right here in sunny Scottsdale 2/29-3/2/16 with SRP & others!"
13 hours ago
Joe Konopacki posted an event

Duct & Envelope Tightness (DET) Verifier at Temperature Equipment Corporation

February 26, 2016 from 8:30am to 4:30pm
The Duct & Envelope Tightness Certification (DET) was designed by the Midwest Home Performance…See More
14 hours ago
Diane Jackson liked Don Hynek's discussion Superinsulation retrofit is Complete!
15 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service