While fully wanting to have the most thermal barrier I can have, should I believe Rem/Rate when it tells me that R-value does so little? By changing the R-value # only for the ceiling (roof) in Rem/Rate, the cost savings is ~$75/yr on my house specifically, and the load reduction and carbon reduction are also nominal.
There is the ongoing discussion about cheating the customers by only spraying R-21 in lieu of R-30 (our local R-value requirement). The diminishing returns after a complete air seal is met with spray foam seems to suggest there is no need for the extra costs. I don't think it is debatable whether or not the greater R-value # you have (thickness), the more thermal resistance you should have if it is installed properly. But should the insulation types be counted as equals? Should we make it so tough to put the ducts in the envelope?
As I understand it, R-value for code has been based on conductance only and not the 2 other types of transfer. By not giving spray foam credit for the air sealing qualities it potentially has seems to make the two types an unfair comparison.
The only thing I think must happen is the enforcement of code regarding air leakage testing of all spray foamed and air sealed houses with blower doors, new and retrofit. With all the homes that I have been testing, there is obviously a need for this service. So many of these installers have been looking at this like painting and not using building science in their approach. There are huge energy saving claims by many of these companies, and the housing stock and clients are not getting a good deal.
Those building envelope gaps are a plenty!! This past summer in the hot/humid environment of Hilton Head Island, SC, those newly spray foamed attics were hot/humid, and those ducts were dripping condensation like crazy! Small mistakes in spray foam seems to be the cause of lots of problems.
One big question that also needs to be addressed is, how do you know if the house is too tight and you need ventilation without testing? Not many around here are testing. Some of these retrofits have gas appliances and are in retirement communities. I see potential concerns for health and safety here.
Of course there is the article titled "It's OK to Skimp On Insulation, Icynene Says" by Green Building Advisor contributor Martin Holladay which clearly states his position. Although I agree that requirements are requirements and codes are codes, what should we do about the ROI and the information our energy modeling software tells us? If we make it too hard and don't give constructive guidance, how are we going to move forward?
What are some thoughts on this?
Tags: Blower door, Building Envelope, R-value, fiberglass insulation, spray foam insulation
Permalink Reply by Hunter Dendy on November 27, 2010 at 5:58pm
Permalink Reply by Evan Mills on November 27, 2010 at 10:44pm
Permalink Reply by Jamie Kaye on November 28, 2010 at 4:39am
Permalink Reply by Carl Seville on November 30, 2010 at 7:59am
Permalink Reply by John Nicholas on December 2, 2010 at 9:16am
Permalink Reply by Jamie Kaye on December 2, 2010 at 11:17am
Permalink Reply by Carl Seville on December 2, 2010 at 11:40am John, every house I have done an air seal verification for was already foamed by the insulation contractor prior to the test. I do record the CFM50 for the ventilation requirements, but normally I run the test at 25 pascals to give me more time to test (keeping a good Delta T). I read David Butler's take on home energy improvements being worth it vs. Solar PV in the comments here. I think that is a great way of thinking about the improvements if we are basing them on their cost effectiveness and ROI. It seems to me that going to R-50 or R-60 with foam would never pay itself as the gains that you are making are continuously diminishing, but the per sq. ft. price of the product remains the same, or close. Maybe style specific though like PassiveHaus or something that uses thermal mass as a means of conditioning. What are the parameters and specifics that you used in order to get a 5-10 year payback?
Carl, I second that emotion "The open cell is more prone to gaps as it expands so quickly that it often folds over on itself and covers up holes before the installer sees them." I don't think its the fault of the installer not seeing them because they are incompetent though, more so it is due to the precarious nature of the product. The blower door and IR do amazing things to uncover these issues, and even then you sometimes have to pull away that top 1" or so to really expose that wind, or uncover the hole (that is where IR helps you even more than blower door alone)! I also agree that you end up paying similar costs with either using a better product or paying more in labor depending on which way you achieve your positive results. I think many of the foam guys still aren't caulking the studs, plates, etc...and only spraying in the cavities and they have a lot of room to improve if they would learn about building science and the diagnostics.
Also Carl, your comment "One place where I would only use closed cell is in floors over unconditioned and damp crawlspaces to avoid any condensation on the floor during cooling seasons." What is the change or a reason why if you had fiberglass existing and had no problems to date (i.e...floors cupping, rot, etc...) that you would only use closed cell? Why if open cell is able to breathe wouldn't it perform just the same as fiberglass, if not a bit better because it will be touching the floor and is an effective air barrier? What is the science that can happen there? I do understand that closed cell will move that condensing surface to the outside of the foam vs. the subfloor or even the paper on the insulation, but I am curious as to why if I had no problems to date and only changing the floor insulation from fiberglass to open cell would that deter me from this more economic version?
Permalink Reply by John Nicholas on December 2, 2010 at 1:59pm John, every house I have done an air seal verification for was already foamed by the insulation contractor prior to the test. I do record the CFM50 for the ventilation requirements, but normally I run the test at 25 pascals to give me more time to test (keeping a good Delta T). I read David Butler's take on home energy improvements being worth it vs. Solar PV in the comments here. I think that is a great way of thinking about the improvements if we are basing them on their cost effectiveness and ROI. It seems to me that going to R-50 or R-60 with foam would never pay itself as the gains that you are making are continuously diminishing, but the per sq. ft. price of the product remains the same, or close. Maybe style specific though like PassiveHaus or something that uses thermal mass as a means of conditioning. What are the parameters and specifics that you used in order to get a 5-10 year payback?
Permalink Reply by Hunter Dendy on December 2, 2010 at 5:26pm
Permalink Reply by Bryce Cramer on December 3, 2010 at 6:23am RE My comment regarding closed cell foam on floors, the point I was trying to make is that I wouldn't use open cell foam in a hot climate with a damp crawlspace. With AC on inside, you can create a condensing surface on the underside of the floor and since open cell is pervious to vapor, there is the potential for condensation that is not visible where the foam touches the floor. Closed cell is impervious (relatively) to vapor, so the problem wouldn't likely occur. You theoretically could have the same problem with fiberglass, but I wouldn't both using it in floors as it is almost impossible to install correctly.
Jamie Kaye said:John, every house I have done an air seal verification for was already foamed by the insulation contractor prior to the test. I do record the CFM50 for the ventilation requirements, but normally I run the test at 25 pascals to give me more time to test (keeping a good Delta T). I read David Butler's take on home energy improvements being worth it vs. Solar PV in the comments here. I think that is a great way of thinking about the improvements if we are basing them on their cost effectiveness and ROI. It seems to me that going to R-50 or R-60 with foam would never pay itself as the gains that you are making are continuously diminishing, but the per sq. ft. price of the product remains the same, or close. Maybe style specific though like PassiveHaus or something that uses thermal mass as a means of conditioning. What are the parameters and specifics that you used in order to get a 5-10 year payback?
Carl, I second that emotion "The open cell is more prone to gaps as it expands so quickly that it often folds over on itself and covers up holes before the installer sees them." I don't think its the fault of the installer not seeing them because they are incompetent though, more so it is due to the precarious nature of the product. The blower door and IR do amazing things to uncover these issues, and even then you sometimes have to pull away that top 1" or so to really expose that wind, or uncover the hole (that is where IR helps you even more than blower door alone)! I also agree that you end up paying similar costs with either using a better product or paying more in labor depending on which way you achieve your positive results. I think many of the foam guys still aren't caulking the studs, plates, etc...and only spraying in the cavities and they have a lot of room to improve if they would learn about building science and the diagnostics.
Also Carl, your comment "One place where I would only use closed cell is in floors over unconditioned and damp crawlspaces to avoid any condensation on the floor during cooling seasons." What is the change or a reason why if you had fiberglass existing and had no problems to date (i.e...floors cupping, rot, etc...) that you would only use closed cell? Why if open cell is able to breathe wouldn't it perform just the same as fiberglass, if not a bit better because it will be touching the floor and is an effective air barrier? What is the science that can happen there? I do understand that closed cell will move that condensing surface to the outside of the foam vs. the subfloor or even the paper on the insulation, but I am curious as to why if I had no problems to date and only changing the floor insulation from fiberglass to open cell would that deter me from this more economic version?
Permalink Reply by Jamie Kaye on December 6, 2010 at 5:13am Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato's discussion was featured
Johnny Ritzo's discussion was featured
Tom Delconte's blog post was featured
Christopher Morin's blog post was featured
Mike Rogers's blog post was featured
Mike Rogers posted a blog post
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase© 2013 Created by Lawrence Berkeley National Laboratory.