I'm looking for clarification on required ventilation levels in residential settings. For instance if I have a home that indicates an ach rate of considerably less than .35 that would suggest the addition of mechanical ventilation. I'm unclear, however on how much is enough, how much is too much? It would seem that the additional air exchange rate should be based around the actual natural rate difference between the measured amount and .35.
Tags:
Permalink Reply by Tammy Kenworthy on September 14, 2012 at 10:35am hey Don, good to see you chime in here. I absolutely agree with you
Eric - you probably do not need to add mechanical ventilation but you are leaving a lot of energy savings behind.
http://www.gpconservation.com/
Permalink Reply by Robert Riversong on September 16, 2012 at 8:26am Mechanical ventilation costs energy - it does not save it. But the energy penalty is the price of good indoor air quality. And both IAQ requirements and most building codes require mechanical ventilation in any new house.
I just downloaded this from DOE website check out 2nd paragraph
Permalink Reply by Sean Lintow Sr on December 27, 2011 at 1:36pm Just a heads up, check out the date - that is from 2002 and outdated
Is it possible codes, etc... will change - sure as they always are but the most recent & proven one is listed above 7.5+
Seasons Greetings!! Yes, that is old data. The 15 cfm per person or 0.35 ACH numbers were from ASHRAE Standard 62-1989 - 22 years ago!! When we set about updating 62-89 in 1994, we realized that most of the contaminants were related to the number of people and the size of the house, but not the volume. So we reduced the ventilation rate per person from 15 cfm/person to 7.5 cfm/person plus an allowance for the size of the house, 0.01 cfm per square foot. BPI has been slow to change their calculation method to update it to the numbers used in the 2003, 2004, 2007, and 2010 versions of ASHRAE 62.2 but they are finally coming around. DOE now requres that all WX done with federal dollars after January 1st must meet ASHRAE 62.2-2010 so it is well past time to abandon the 15 cfm/person rates that ASHRAE stopped publishing in 2003. As for code, yes, the 2012 International Energy Conservation Code (IECC) and 2012 International Residential Code (IRC) both require mechanical whole house ventilation at these same rates and both require that all new construction be built to 5 ACH50 for the mild climates and 3 ACH50 for the more severe climates. Not everyone will adopt the 2012 I-Codes this year, but they are coming. ASHRAE 62.2 is already the required code in California, Maine, and several other states so it is time to figure out how to do it. 62.2 generally requires only 30 to 80 cfm so it is not a big airflow or energy penalty. So my recommendation is to mimic Nike and Just Do It!! Make it tight and ventilate it right at the 62.2 levels.
Permalink Reply by A. Tamasin Sterner on December 29, 2011 at 9:55am A short and concise brief on this can be found at
http://www.waptac.org/data/files/Website_docs/Technical_Tools/PA%20...
as well as on our own website, www.PureEnergyCoach.com Have fun!
Permalink Reply by John Nicholas on January 5, 2012 at 7:33am Tamasin, Thanks for the pointer. Good info on the control methods (timers) for fans etc.
Permalink Reply by Barry NewDelman on December 29, 2011 at 11:22am Here is excerpt from the International Residential Code.
Check with your local building department
Hope this Helps
R303.1 Habitable rooms. All habitable rooms shall have an aggregate glazing area of not less than 8 percent of the floor area of such rooms. Natural ventilation shall be through windows, doors, louvers or other approved openings to the outdoor air. Such openings shall be provided with ready access or shall otherwise be readily controllable by the building occupants.
The minimum openable area to the outdoors shall be 4 percent of the floor area being ventilated.
Exceptions:
Permalink Reply by Bob Blanchette on July 29, 2012 at 5:15am In other words if it feels stuffy inside open a window :)
Permalink Reply by John Nicholas on December 30, 2011 at 9:59pm Following ASHRAE 62-2-2010 is relatively simple. In my view the continued teaching of the .35 and its use by various programs around the country is less then State of the Art!
Amanda Evans pointed me to Rick Karg's app for the iPhone to calculate this. ResVent62.2 in the app store. It also works on the iPad.
Worthwhile minor investment for major results.
Permalink Reply by Teresa Coffman on July 28, 2012 at 11:20am
Permalink Reply by John Nicholas on July 28, 2012 at 8:44pm Teresa, ACH is a function of rate and volume. Start with the square footage and the volume of the home. 1000 sf home slab on grade. 10 feet ceilings so you have 10,000 cubic feet.
ACH is air change per hour so we are trying to determine the number of times per hour that volume changes. We may have 1, 3, 5, or any number like that. Energy Star has a requirement of 5 ACH measured at 50 pa pressure difference inside to outside.
We usually depressurize to -50pa so we state an air change term of CFM @ 50. That is an accurate repeatable number that does not require the N-Factor approximations and estimates of the auditor as to shielding.
The formula for taking a Blower Door number (measured at -50 pa depressurizaton) to ACH @ 50 is
(BD Reading * 60) / Volume
So our home above built in 1950 could easily test at 2500 CFM at 50.
2500 * 60 is 150,000 now divide that by V(plume) and you have 15 ACH @ 50.
Our home built in the 1990 would test closer to 1200 CFM at 50.
1200 * 60 is 72,000 now divide that by V and you have 7.2 ACH at 50.
I tested an Energy Star 4 Bed Room home for Habitat for Humanity last Tuesday.
1176 sf 12,934 Volume 1001 CFM at 50 Blower Door test.
1001 * 60 is 60060 and divide by V and we get 4.64 ACH at 50 Meet Energy Star < 5 ACH @ 50.
The CFM @ 50 number you are looking for, on my Habitat Build, is around 1400
It is now irrelevant. If the home comes in at 500 or 2000 CFM at 50 Blower Door after air sealing, we still need to add mechanical ventilation. The question is how much and then what strategy; balanced, supply, exhaust.
So 4 Bedrooms (plus 1) at 7.5 is 30 CFM. Plus you add 1 CFM per 100 sf (1176 / 100) = 11.7 so the BASE requirement for Mechanical Ventilation is 41 CFM
You now figure an allowance for A) Building Tightness and B) Spot (Intermittent) ventilation.
I use Rick Karg's iPad app (RESVENT 62 also for iPhone) for this. So the required MV after allowing for the actual BD number was 29. Lower than the Base 41. Adding the 2 Baths and Kitchen with intermittent ventilation did not lower the 29.
If we had a 2500 BD number the app reports 0 CFM needed for MV.
If we had a 1500 BD number the required would be 17 CFM.
If you know the volume of your home and want to predict some ACH numbers for your home with a BD reading you need a couple of magic numbers. You can use the 60 in the formula with 3 and your magic number is 20. Or you use 5 and the 60 in the formula and your magic number is 12.
Divide the volume by 20 and you have the CFM @ 50 reading for 3 ACH at 50 12934 / 20 = 646
Divide the volume by 12 and you have the CFM @ 50 reading for 5 ACH at 50 12934 / 12 = 1077
Actual numbers above.
Does this help?
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
yangxiaohua posted a blog post
Jeena Smith commented on Molly Banton's blog post Install a Pellet-Burning Fireplace Insert and Save Money
Johnny Ritzo posted a discussion
Eric Kjelshus replied to Patrick Michaelyan's discussion Hot Upper Stories
Bud Poll replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Sean Lintow Sr replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato posted a discussion
Dennis Heidner replied to Patrick Michaelyan's discussion Hot Upper Stories
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??© 2013 Created by Lawrence Berkeley National Laboratory.