RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 259

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Jim Gunshinan posted blog posts
6 hours ago
H.O. Electric posted a photo

about us-team

H.O. Services is your residential Electric-Plumbing-Heating-Cooling Specialist. We are an…
7 hours ago
H.O. Electric added a discussion to the group News & Announcements
Thumbnail

Stay Cool With Easy To Install Ductless AC System!

Stay Cool With Easy To Install Ductless AC System!   Save $300.00 Off A New AC System For A Limited…See More
7 hours ago
Richard Wells commented on Diane Chojnowski's group Facebook Pages
"Three thousand home energy efficiency audits, and nearly a thousand retrofits in four short…"
8 hours ago
Richard Wells joined Diane Chojnowski's group
Thumbnail

Facebook Pages

Does your company or organization have a Facebook Page?This group is for pros who have facebook…See More
8 hours ago
David Baerg replied to Blake Shurtz's discussion Air sealing wood-burning fireplace from the crawlspace below
"Hi Blake, Do you mean around the underside of the hearth?  Are you trying to seal between the…"
9 hours ago
Tom White's video was featured

Rebirth Realty: Restoring Detroit properties for Venture for America Fellows

Its been a long, cold winter, but we've made significant progress in the restoration of 760 Virginia Park. Join Tim Dingman on a walkthrough to see what we've done.
10 hours ago
Kim Tanner added a discussion to the group Multifamily Buildings
Thumbnail

Blower Door Applications Guide

TEC and Camroden Associates have released their big building testing manual, Blower Door…See More
10 hours ago
Profile Iconmichael coleman, Dan Liska and Rob Moreno joined Home Energy Pros
11 hours ago
Christopher Morin's blog post was featured

5 Things New Energy Efficiency HVAC Contractors Need to Know

1. Do not sell on Price! Use 'Simple Payback'The price of High-efficient equipment will undoubtedly…See More
yesterday
Jim Gunshinan's blog post was featured
yesterday
Kim Tanner commented on Diane Chojnowski's group Home Energy Pros on Twitter
"Follow The Energy Conservatory on Twitter! We'll follow…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service