RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 270

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mark Wozniak posted a status
"I am looking for energy efficiency software training in Massachusetts."
1 hour ago
daniel manriquez replied to Trip Smith's discussion Starting a Home Weatherization Business. Considering it...
"Here's a contractor perspective on incentives. Not that I agree with all of it, but its a good…"
1 hour ago
Rick Wertheim joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
3 hours ago
Rick Wertheim joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
3 hours ago
Casey Gesell posted a video

How Dr. Energy Saver Helped Me Grow My Home Services Business | Dealer Testimonials

http://www.drenergysaverdealerships.com | 1-877-479-3637 Real Dr. Energy Saver dealers explain how the proven marketing, sales and training programs allowed ...
4 hours ago
Casey Gesell commented on Tom White's video
Thumbnail

Ducts in an Attic

"Hi Tom, Thank you for sharing our Dr. Energy Saver video!"
4 hours ago
Diane Chojnowski posted a discussion

EEBA 2014 Conference Presentations

EEBA has posted many of the presentations from their conference in St. Louis last week. Check them…See More
4 hours ago
Profile IconJames Tucker, Dean Brewer and CPB Mechanical joined Home Energy Pros
5 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service