RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 269

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconJuan Roca and Elizabeth Coe joined Home Energy Pros
6 hours ago
Casey Gesell posted videos
6 hours ago
Gerald Shechter posted videos
6 hours ago
Hal Skinner replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Bret,  here are the 2 reports I referred…"
9 hours ago
Craig Foley shared George Kopf's discussion on Twitter
9 hours ago
Jan Green replied to George Kopf's discussion Real Estate Professionals need our support - but how?
"Craig, I like your thinking!  With my new broker, I've been able to communicate more…"
10 hours ago
Craig Foley replied to George Kopf's discussion Real Estate Professionals need our support - but how?
"Thanks Jan, your insight, as always, is invaluable. Your suggestions regarding a top down approach…"
10 hours ago
Hal Skinner replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Brett, you just asked the million dollar question when it comes to OUR coating. Now I will let the…"
10 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service