RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 268

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconKevin Jordan, Hannah Strong, Rich Snyder and 1 more joined Home Energy Pros
11 hours ago
EnergyLogic Academy posted events
11 hours ago
EnergyLogic Academy updated an event
Thumbnail

RESCAZ- RESNET Combustion Safety Testing: North Carolina at Wilmington, NC

November 7, 2014 from 6pm to 7pm
The health and safety of the home energy auditor’s clients should be the top priority when…See More
11 hours ago
EnergyLogic Academy updated an event
Thumbnail

RESNET Phase 2 Rater Training - Field Training at EnergyLogic Academy - Berthoud CO

September 22, 2014 to September 24, 2014
The EnergyLogic Academy will be hosting the second phase of HERS Rater Training August 4th - 7th,…See More
11 hours ago
Hal Skinner replied to Scott Katznelson's discussion Database of zip code or county by climate zone
"Hi Scott. I dont know of a database that you are referring to.  I was always under the…"
12 hours ago
Rich Snyder joined Rich Brunco's group
Thumbnail

Cape Cod Energy Pros

Recent BPI classmates, a place to share referals and informationSee More
13 hours ago
Scott Katznelson posted a discussion

Database of zip code or county by climate zone

HI.  I'm looking for a database that could help me assess the average energy use of a home (per…See More
19 hours ago
Hal Skinner replied to Hal Skinner's discussion The 'Touchy - Feely' sales pitch. in the group Radiant Control Coatings
"The 2nd bestsales tool I ever came up with.  aI will be happy to send anyone a test strip like…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service