RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 342

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Featured Forum Discussions

What's the Most Profitable HVAC Job for Your Company?

Started by Wayne Melancon in HVAC. Last reply by Wayne Melancon 2 hours ago. 3 Replies

Lighting replacement - 300 watt LED flood light

Started by Mary Sinkler in General Forum. Last reply by Jan E. Graveamker 18 hours ago. 4 Replies

Glass Block Windows

Started by Ken Kalke in Best Practices. Last reply by Sean Lintow Sr on Saturday. 1 Reply

EZ Green Home is Hiring!

Started by Chloe Chapman in General Forum Jan 5. 0 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Wayne Melancon replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"I'll agree with you there Ken. We'll get shopped by residential when the customer already…"
2 hours ago
Horace Douglas Hunt, Jr. commented on Horace Douglas Hunt, Jr.'s photo
Thumbnail

IMG_3138

"and....this was the best looking spot in the air handler. Seal the unit if you want to have any…"
4 hours ago
Horace Douglas Hunt, Jr. commented on Horace Douglas Hunt, Jr.'s photo
Thumbnail

IMG_3139

"Beginnings of mold....due in some part to leaks in air handler pulling hot humid air from…"
4 hours ago
Horace Douglas Hunt, Jr. posted photos
4 hours ago
Eric Kjelshus replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"What is your "Key Performance Indicator" dollar per hour? gross dollar per man day? % of…"
13 hours ago
Jan E. Graveamker replied to Mary Sinkler's discussion Lighting replacement - 300 watt LED flood light
"Hi Mary, What is the purpose of lighting the backyard ?  Sense of safety, night time…"
18 hours ago
Chris Laumer-Giddens liked Chris Laumer-Giddens's blog post Rock Wool Insulation for Floor of High Performance Tiny House
19 hours ago
Joe Davis liked Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
22 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service