RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 268

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Bud Poll replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"Hi Hal, Search "Basecalc basement heat loss".  From memory Canada (nrcan) has/had a…"
59 minutes ago
Michael Dunseith posted photos
13 hours ago
Hal Skinner replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"II just remembered seeing a report by a federal adency, many years ago, that basically said …"
16 hours ago
Don Fitchett commented on Tom White's video
Thumbnail

Alliant Energy's PowerHouse TV: Sealing Leaky Ductwork

"Very educational. thanks for sharing Tom."
19 hours ago
Hal Skinner posted a discussion

How much heat energy is lost through the floor of a house?

I am asking this as I do not recall anyone speaking of any study to this end.  Many comments about…See More
19 hours ago

Mike Braun just added their location.
(via Member Map)

20 hours ago
Bud Poll replied to Bud Poll's discussion Another benefit from air sealing
"From my work in NY City many years ago, the critters I saw would never have fit through a quarter…"
yesterday
Barbara Smith replied to Bud Poll's discussion Another benefit from air sealing
"Eliminating quarter sized holes can impede rats from entering a building, in areas where rats tend…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service