RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 325

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Empower Efficiency added a discussion to the group Job Board
Thumbnail

Position Opening: Local Community Outreach Specialist, Energy Efficiency (San Carlos, CA)

Local Community Outreach Specialist, Energy Efficiency (San Carlos, CA) Job Title: Local Community…See More
yesterday
Amber Vignieri posted a blog post

Elevate Energy Mythbusters: Windows & Attics Edition

This blog post is guest written by former staff member Eric Keeley.Great enthusiasm for home energy…See More
Friday
Glen Gallo replied to Diane Chojnowski's discussion Poll: What is you favorite or most important home performance diagnostic or measurement tool?
"I agree with Ted. If I could bring just one piece of equipment it would be the blower door. It has…"
Friday
Glen Gallo replied to Shaun 's discussion Commercial duct testing
"If above the ceiling tiles the wall is a finished assembly and there is insulation on or under the…"
Friday
Tom White's video was featured

Combustion Appliance Zone Testing (CAZ) Made Easy (March 24, 2016)

Combustion Appliance Zone Testing (CAZ) Made Easy (March 24, 2016) -Gauge Fundamentals -Adapting to the new BPI standard -RESNET testing requirements -NFPA testing requirements -Best practices for best results
Friday
Profile IconLaura Capps and Bret Abrams joined Home Energy Pros
Thursday
Olivia Taylor posted a blog post

5 Key Reasons Why Rooftop Solar Is Popular In The US

The rapid switch from traditional electricity to clean, economical and renewable solar energy is…See More
Thursday
Adam Swain posted a blog post

Top 5 Tips For Hiring A Crawl Space Contractor

A homes crawl space is one of the few places most homeowners try to avoid at all cost, and for good…See More
Wednesday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service