RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 265

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Jim Gunshinan commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Thanks Nate for more good stuff to chew on—and nutritional! We may be running out to Home…"
1 hour ago
Tom Conlon commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim,I just got around to re-reading your four-part series and I think this is a really interesting…"
1 hour ago
Nate Adams commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"$50 in health ain't much... not with my crappy high deductible plan. It buys half of a cold…"
1 hour ago
tedkidd commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Yep, this thread has some good discussion. Back to dehumidification.  This may be…"
6 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Thanks for the clarification Nate. If I had the ability to precisely measure what $50 of health…"
7 hours ago
Nate Adams commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, Just a clarification, it's not DEhumidification I'm worried about in your climate,…"
7 hours ago
Chris McTaggart posted events
7 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Hi Nate, I'm glad this post has generated so much good discussion, since that is its main…"
8 hours ago
Diane Chojnowski's group was featured
Thumbnail

Facebook Pages

Does your company or organization have a Facebook Page?This group is for pros who have facebook…See More
8 hours ago
Tom White joined Diane Chojnowski's group
Thumbnail

Facebook Pages

Does your company or organization have a Facebook Page?This group is for pros who have facebook…See More
8 hours ago
David Valley's photo was featured

ceiling_infrared

Cold air infiltrating the lower right portion of this wall and ceiling.
8 hours ago
Christopher Morin's 2 blog posts were featured
8 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service