RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 268

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"OK.  This might be rudamentary here.  I want to make sure everyone understands how SOLAR…"
10 minutes ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hal - I would disagree that radiant heat "goes through" fibrous insulation. Radiant heat…"
19 minutes ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hi KLurt. I would isagree with the comment that the attic floor is heated by the…"
40 minutes ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Now back to your question - the best data for radiant barriers is the DOE studies from the ORNL.…"
52 minutes ago
Kevin Jordan posted a discussion

Does anyone have pointers on approaching real estate induatry.

Hello All!!I am figuring on approaching the real estate and low income housing industries here in…See More
55 minutes ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Kurt - Radiant heat transfer does not heat the air. It is the passing heat directly from hot object…"
1 hour ago
Steven Turetsky replied to John Shillito's discussion Fixing a water heater?
"Hello John (and everyone else in the forum), I'm a new visitor at this forum and it this is my…"
1 hour ago
Kevin Jordan posted a status
"I have questions about approaching the real estate industry? I need help."
1 hour ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service