RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 316

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Tom White's video was featured

Multifamily Building Energy Innovation- TrueFlow Capture Box

Video explaining the new tool to help reduce the energy costs of effective ventilation in multifamily buildings.
2 hours ago
Alfie Davis posted a blog post

Utility of a Hardwood Staircase

Everything needs a makeover after a certain time. Your home is one of them.  Sometimes, you…See More
6 hours ago
miguel pace shared a profile on Facebook
11 hours ago
miguel pace liked miguel pace's blog post It is very important to select a fin fan
11 hours ago
Charles Ryan Weitzel posted a discussion

Oil Fired Boiler Being Used as the Heating Source in Two Air Handlers of a Historic Home

I'm not sure this makes any difference, but I've only run into a system like this here, where I…See More
16 hours ago
Ronald Wallis replied to Jonny Fisher's discussion Minneapolis Blower Doors and Duct Blaster for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"interested in your equipment. Do you have pics? Is equipment compliant with new regulations?"
21 hours ago
Ronald Wallis joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
21 hours ago
Joe Crisara replied to Kim Tanner's discussion Article about residential energy efficiency and why sales are low
"Kim, I couldn't agree more. Too many times energy audits are focused on the technical aspects…"
22 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service