RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 338

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Profile IconElaine Williamson and kevin mack joined Home Energy Pros
1 hour ago
Eric Kjelshus replied to Beverly Lerch's discussion Fireplace drafts
"A brick chimney will take some 70,000 BTU's to heat up to draft on a fireplace.   A…"
9 hours ago
Ed Voytovich replied to Beverly Lerch's discussion Fireplace drafts
"Our solution was to install a Lopi Answer wood burning insert that vents directly through a metal…"
16 hours ago
Jim Gunshinan's blog post was featured

A Healthy Home and a Healthy Bottom Line

There has been a lot of interest of late in the weatherization and broader home performance…See More
yesterday
Jonathan Beers commented on Home Energy Magazine's blog post Natural Gas is Becoming Less Attractive
"The carbon intensity of electricity use (lbs. of CO2/MWh) varies a lot from region to region. For…"
yesterday
Diane Chojnowski posted events
yesterday
Home Energy Magazine posted a blog post

Natural Gas is Becoming Less Attractive

The United States and Canada have been fortunate to have access to natural gas for space heating,…See More
yesterday
Jim Gunshinan posted a blog post

A Healthy Home and a Healthy Bottom Line

There has been a lot of interest of late in the weatherization and broader home performance…See More
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service