RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 329

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Diane Chojnowski replied to John Nicholas's discussion Slab Edge Insulation - A Side Thread to Melissa's Question
"Great videos Daniel. Would you please add them to our videos…"
1 hour ago
David Holtzclaw replied to Steve Mann's discussion Alnor 6200 LoFlo Capture Hood in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Steve I'm interested 402-213-3788 dholtzclaw@transductiontechnologies.com thanks david "
17 hours ago
Eric Kjelshus replied to Steve Mann's discussion Alnor 6200 LoFlo Capture Hood in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"call me Monday 816-537-5100 "
17 hours ago
Steve Mann added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Alnor 6200 LoFlo Capture Hood

I've got an Alnor 6200 Balometer (Flowhood) I'd like to get rid of. No longer needed--I have a big…See More
18 hours ago
Paul Raymer posted an event
Thumbnail

MA Crew Chief/BPI Building Analyst Training at Bristol Community College at Commonwealth Landing

September 12, 2016 at 9am to September 16, 2016 at 4:30pm
Bristol Community College has created a hands-on training cabin in their laboratory.  This class…See More
22 hours ago
Daniel Morrison replied to John Nicholas's discussion Slab Edge Insulation - A Side Thread to Melissa's Question
"John, I just collaborated with Steve Baczek on a few videos for ProTradeCraft about slab insulation…"
yesterday
Profile IconMichael Sumpter and Bill Gartner joined Home Energy Pros
yesterday
Malcolm Jackson joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
Friday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service