RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 269

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Jim Gunshinan posted a blog post
3 hours ago
Mike Kandel posted discussions
3 hours ago
Mike Kandel added 3 discussions to the group Building Performance Institute (BPI)
3 hours ago
Hal Skinner replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"I am curious now.  They require a penetration firewall in the wall system but do not require a…"
8 hours ago
Hal Skinner replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"WOW.  30 years working and m,eeting with every kind of contractor and never heard of this…"
9 hours ago
Tony Rigdon replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"The building inspector when he inspected my footing told me about the drywall on the outside being…"
11 hours ago
Profile IconSuskin Lockett Jr, Yoomie Ahn, Lindy Wordlaw and 6 more joined Home Energy Pros
11 hours ago
Tony Rigdon replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"Bud, I'm in Columbia, MO so Zone 4 Mixed Humid. I had never heard about drywall on the outside…"
11 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service