I have seen mold growing under a radiant barrier installed over blown in insulation.  I am looking for any articles, etc.... about this problem to forward to a customer.  Can anyone help?

Views: 2915

Reply to This

Replies to This Discussion

Hi Rob,

We need more information, the type of insulation, the climate, is there heat and ac, is there a vapor barrier, and what air sealing measures have been taken?

One explanation would be warm moist air leaking up through the blown in insulation and encountering a cold radiant barrier where condensation would form.  Once you have some moisture, you are almost certain to grow mold.  For reading I would start with the energy nerd http://www.greenbuildingadvisor.com/blogs/dept/musings/radiant-barr... .

Bud

The radiant barrier needs at least 1 inch of air on the side that it is supposed to be reflecting heat.  If it is touching something on that side, it will act as a conductor instead of a reflector.  By laying it on top of the insulation, it has very little chance of doing its job in the winter.  The best place to put it is under the roof rafters.  That way it can keep radiated heat out in the summer and keep radiated heat from leaving via the roof deck in the winter.  There are two types of radiant barriers available commercially: the bubble wrap type and the perforated foil type.  The second is better for preventing moisture issues like the ones you are talking about, and it is less expensive.  The "R-value" which the bubble wrap promises is not something you should take into consideration.  If you want more R-value, spend the extra money on insulation.

Thom Price

Berea, KY

Umm, the required 1" space is correct, but by the way you worded it is off & the placement depends on ones climate. In the south it should be under the sheathing or rafters to reflect heat back out of the attic. Up north due to venting, ice-dams, etc... if one is crazy enough to use it, it should be on top of the insulation to help reflect it back down.

I definitely agree on the last statement with the caveat that they fix the air leaks first in the attic & not just try to cover over them

fix the air leaks first in the attic & not just try to cover over them

 

+1 on that. The RB material is performing as a condensing surface instead. What a perfect way to demonstrate attic leakage.

Considering that most of us live in areas that have heating and cooling seasons, a radiant barrier that doesn't work in both ways is counterproductive for at least part of the year.  Some might argue that for many, it is counterproductive for most of the year.  It would be nice to be able to move it around or even remove it under certain conditions, but that isn't an option, so the challenge is to find the best location for the average conditions throughout the year in a specific location. 

If you are are going to have it in contact with the insulation, it should be on the proper side of the insulation to do much good.  That would be the warm side of the insulation, not the top, and it requires a minimum of 1' air space above the ceiling plane, which isn't very easy to achieve for most installers.  Laying a radient barrier on top of insulation in an attic seems like a very poor choice to me in any climate.  If the point is to stay warmer, I'd say you'll be hard pressed to see much difference.    Also, placing it on top of the insulation guarantees that the top surface will no longer reflect in a matter of years because it will be covered with dust.

Placing it under the rafters, as I suggest, means that radiant heat has a harder time making it to the insulation in the summer, and if you have a good ridge vent and soffit vents, you can get good convection currents between the rafters to get the heat out of the structure, and it will take much longer for dust to build up.  Placing it in contact with the roof deck often doesn't permit the proper air space for the product to perform properly.

Conclusion: Radiant barriers can work well to reduce the cooling load, but are problematic if you are trying to use them to keep heat in the house.

If the radiant barrier in an attic does not "Maintain an intimate bond" with the structure, then it is not going to do much at all.

 

If it is placed on or above blown in or rolled insulation, or it is installed on the rafters, air will get around, above or below it.  That air always has humidity.  In the process of radiant heat transfer, that humidity goes along for the ride.  The radiant heat enters the walls, roof but the humidty stops there.  Wet walls, roof.

 

The radiant barrier, if it is worth anything at all, is supposed to stop that radiant heat transfer and prevent the humidy from gathering on the walls, roof or radiant barrier material.

 

If a radiant barrier material is placed over the insulation on the attic floor and the insulation is getting wet, your radiant barrier material is a joke!

 

www.ct-texas.com

 

This thing about a radiant barrier maintaining an intimate bond with the structure is new to me.  Could you cite a source?  I am not able to find anything to verify the claim, other than what you have written in your publicity post about the product you sell.  Could you not build a dome around a house of just radiant barrier and effectively block radiant heat?  Moist air goes along for the ride with convective currents, not with radiant heat transfer.  Radiant heat can travel through a vaccuum.  It seems like you are confusing radiant barriers with vapor barriers, since your product does both. Vapor barriers do need to maintain an intimate bond with the structure.  It seems like you don't want people to get up in their attics and staple foil under their rafters, because you want to sell another, more costly, product.

Hi Tom.

 

For starters, this product is only sold to exclusive distributors.  They are only permitted to sell the coating to factory trained and certified applicators.  If you sent me a chck for 100-gallons, I would have to send it back, I could not sell it to you. 

 

There is a big difference in radiant barriers and radiant barrier coatings.  Someone mentioned suspending the radiant barrier (aluminum foil?) an inch above the blown in insulation.  Whether it is one inch or two feet above the attic floor, how much good is that going to accomplish?  In the hot months the roof is heated by the sun, conductive heat transfer to the under decking.  The underdecking then transfers that heat energy by radiation and also some by convection as the air in the attic also absorbs that heat energy.

 

The 'Aluminum foil' allows air to travel below and above it.  It gets warmed by the heated air and radiates the heat energy below it into the insulation.  The insulation slows that process down but does not stop it, it still absorbs the heat energy and it is transferred through the ceiling into the living space.  If that radiant barrier still allows the attic to receive any heat anergy, what good is it actually doing?  Heat building in the attic is still transferring into the living area.

 

Please understand I cannot speak for other coating products, only the one I work with.  I think the way our coating functions is what is confusing to many / most people. 

 

With the 'aluminum foil', the coolest that material can possibly be is whatever the ambient air temperature is at that level in the attic at that time.  THE HEAT ENERGY HAS ALREADY ENTERED THE ATTIC AND CAUSED THE HEAT BUILDUP.  The aluninum foil does not stop the buildup from happening or stop it from transferring to the living space below.

 

With our coating applied to the roof underdecking, that heat energy does not enter the attic.  The heat energy is not allowed to radiate out past the coating's surface..  This is how an effective 'Radiant Barrier' material.is supposed to work but they do not in most cases.  I think this is where the confusion lies.  People only seem to associate the term 'Radiant Barrier' as something that ONLY is effective against the sun's solar load.

 

You can coat the exterior of the roof, it will reflect and emit the heat away in the hot months AND retain heat in the cold months.

You can coat the plywood on the roof  and then install the shingles, it will still do the same thing acting as a conductive heat barrier.

You can apply it to the attic underdecking.  OR, you can apply it to the floor of the attic prior to installing the insulation. 

OR, you can paint the ceiling of the home and get the exact same results.  IT IS A THERMAL BARRIER, not just a radiant barrier.

 

As an example;  I supervised the application of our coating to hospital boilers and steam pipes.  The surface temperature of the metals prior, 267 degrees, after 155 degrees, a 35% reduction in heat loss through the metals per the engineer.  This application was performed on graveyard shifts.  At 11 pm one night I got a call from them and went down there.  

 

 He took a surface temperature measyrement, 155 degrees.  He then asked ne to place the back of my fingers about an inch or so from that 155 degree surface.  I did and he asked what I felt.  I held it there not knowing what I was supposed to feel.  After several second I said I did not feel anything.   He then said "That's what I'm saying here, we should feel the heat radiating out and it isnt happening.  How do I explain this to Big Mike?".  I said I didnt know.  This was the first time, of many over the years, that someone told me "This is some really weird sh.. you got here." .  I have been told that MANY times over the years.

 

Just one more thing to add to that "Weird sh,," folder:  If you paint a wall or coat a roof with our coating and give it a week to cure, then hit it with an infra-red gun (thermometer)  you will not get a reading.  Now do your research and try to explain that one.

 

We have proven to break the laws of physics many times.

 

www.ct-texas.com 

  

Sounds like a lot of words to me.  I still don't see the science behind it.

LOL & Amen - that is because most of them are nothing but smoke & mirrors

Now Thomas - as for the IR doesn't show anything, the words that come to mind is no $hit Sherlock. When you look in a mirror, do you see the wall directly behind it? No, of course not, but that doesn't mean that the wall isn't there, right? Well you coating basically is the equivalent of putting a mirror there and all the camera sees is reflected IR temps from everywhere but there.

If you want to know more about Infrared, try our FAQ section, or maybe check out the group dedicated to it here

The miltary and some of our competitors heard this about our coating.  They applied some to a roof as well as several other coatings.  They took their IR thermometer guns and got readings from all of them, except ours.

 

Then the other coating companies tried to re-work their ceramic materials to make ceramic platelets, like ours.  It didnt work, they still got readings off alll the rest but not ours.

 

 

Sorry, Hal, but what I am looking for is some source that backs up what you are saying. I've always read and practiced that the radiant barrier needs at least an inch of air space to be effective.  You claim that it needs to be an integral part of the structure. 

Telling me that the military didn't get a reading on your product doesn't make any sense to me.  Are you saying it doesn't have a temperature?  Did they put a piece of tape or something non-reflective on the point they measured?  If not, they may have been measuring the temperature of deep space, as Sean points out.  In any case, I would think that a better test would be to see how it effected the temperature of what you were trying to protect, not the outside surface. 

What I am looking for is the science behind your claim and a published, peer reviewed study that demonstrates that radiant barriers are more effective when they maintain an intimate bond with the structure then when they have at least an inch of air space. 

Don't get me wrong: if you have a great product that has a high savings to investment ratio, I want to know about it.  But if you are just trying to make a buck without regard to SIR, I'm going to try to show that too.  For example, I doubt that your product would go over very well in Kentucky where our heating and cooling loads are both significant and electricity only costs six cents a kWh.  You would have to have a product that works well in both directions and is inexpensive.  Otherwise you might as well blow another six inches of insulation.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Kevin Jordan shared a profile on Facebook
15 minutes ago
Profile IconKimberly Loewen, Bob Whelan, Russ Pittis and 1 more joined Home Energy Pros
1 hour ago
Kari Sauder replied to James White's discussion What happened to Home Energy Pro's website?
"I stopped using Firefox -- too many glitches"
3 hours ago
Tom Mallard replied to Hal Skinner's discussion How our ceramic based RCC works in the group Radiant Control Coatings
"So it seems that what you're saying is for heat-transfer the stuff has little resistance or…"
12 hours ago
Mike Kandel posted a discussion

Earn BPI CEUs at 3rd Annual Building Performance Forum

If you're searching for BPI CEUs, you'll find plenty at the 3rd Annual Building Performance Forum…See More
18 hours ago
Mike Kandel added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Earn BPI CEUs at 3rd Annual Building Performance Forum

If you're searching for BPI CEUs, you'll find plenty at the 3rd Annual Building Performance Forum…See More
18 hours ago
Sean Lintow Sr commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"4% TOTAL Ted - Leakage to outside was stripped from the codes & for good reason"
21 hours ago
tedkidd commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"Wait!  4% total leakage or 4% leakage to outdoors? "