I have seen metal "plugs" (and this may not be the correct term) used for the holes that are drilled in vent pipes, in order to test combustion appliances.
I'm referring to the type 1 vent pipe that is standard for atmospherically-vented gas appliances.
These plugs appear to be superior to HVAC foil tape. Any thoughts on this?
Also, does anybody know how to get their hands on these metal plugs? I use a 5/16" bit to drill probe holes.
Thanks in advance!
Tags:
Here's a related discussion from months ago.
Permalink Reply by Patrick Michaelyan on November 30, 2011 at 10:19am Thanks David.
The issue for me still remains whether a quality plug for metal and high heat applications exists. The plug referenced in the discussion from a few months ago was a plastic plug, and therefore it would not hold up under flue gas temperatures that average 300 - 400 degrees.
The search goes on...
Permalink Reply by Ed Minch on November 30, 2011 at 5:56pm I know that we don't want to raise any questions from our customers about holes in their flues, but if there is a negative pressure inside the flue, do we HAVE to seal it? As an example, a conventional gas water heater has 15-20 in2 of opening at the draft hood, and we are just a few inches away from there with our 5/16" diameter hole with less than an additional .1 in2 (one tenth of a square inch). We use 181 tape and won't feel bad if it falls off - we have never gotten a complaint about this happening. If you feel you must plug this hole, screw a short stainless slotted head machine screw into the hole, adjusting the drill size to make this easy. YMMV.
Ed Minch
Permalink Reply by Patrick Michaelyan on December 1, 2011 at 6:16am Thanks Ed!
I hear where you're coming from, and I can't think of anything against the point(s) you have raised.
Permalink Reply by Bruce Navin on December 21, 2011 at 11:36am I use the snap in metal plugs. In a previous life, my work in service & installation management-in particular when it came to NFPA situations and the like- taught me that if you make some sort of modification to a product, you must make a suitable good faith effort to keep the product within the standards intended by the manufacturer. In this situation, I interpret that to mean when drilling a hole in metal for a test, it should be plugged with metal.
There may be some legal line of reasoning behind this as well. An inexpensive metal plug that is sized properly will leave the homeowner with the impression of the mark of a well-equipped professional and may also avoid a potential liability claim. I have met some homeowners who look for the smallest reason to stir up trouble.
Permalink Reply by Patrick Michaelyan on December 21, 2011 at 12:22pm Thanks a lot Bruce. That's good perspective to have.
Permalink Reply by Jeffrey Sauls on December 1, 2011 at 8:13am Here's a link to the metal plugs I use for single wall metal flues. Recommended by my BPI training provider. They have worked well for me. Sorry, there's no picture of the product on their site.
Downside is that the price doubles with shipping charges when you order a single 20 pc bag.
a-386, 5/16" hole plug
http://www.dwyer-inst.com/Products/Product.cfm?Group_ID=20005&P...
Hope that helps!
Permalink Reply by Patrick Michaelyan on December 1, 2011 at 11:09am Thanks a lot Jeffrey! I think you hit the nail on the head.
Patrick
Permalink Reply by Jeffrey Sauls on December 1, 2011 at 11:22am No problem.
Forgot to mention, but it helps to have a flat file with you to clean up the hole from the drilling when necessary.
Permalink Reply by Glen Gallo on December 1, 2011 at 8:22am Be careful with HVAC metal tape may are not rated for the heat a flue produces.
Permalink Reply by Ed Ballard on December 1, 2011 at 2:36pm I realize you are looking for a manufactured plug, but good old fashioned hi-temp. silicone always does the job. If Josh Lloyd sees this, perhaps he can chime in on pre made hi-temp. silicone plugs which are used by the program he works with.
Permalink Reply by Ed Minch on December 1, 2011 at 4:55pm Ed
Remember that ALL silicone is hi-temp. If memory serves, the clear is 580 degrees for some amount of time, and the colored stuff is 20-30 degrees better - red and black being the best. Just make sure to use pure silicone, not something like acrylic latex with only some silicone.
Ed Minch
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato's discussion was featured
Johnny Ritzo's discussion was featured
Tom Delconte's blog post was featured
Christopher Morin's blog post was featured
Mike Rogers's blog post was featured
Mike Rogers posted a blog post
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
Orvil D Boyer joined allen p tanner's group© 2013 Created by Lawrence Berkeley National Laboratory.