Proper means to "plug" flue pipes after testing gas appliances.

I have seen metal "plugs" (and this may not be the correct term) used for the holes that are drilled in vent pipes, in order to test combustion appliances.

 

I'm referring to the type 1 vent pipe that is standard for atmospherically-vented gas appliances.

 

These plugs appear to be superior to HVAC foil tape. Any thoughts on this?

 

Also, does anybody know how to get their hands on these metal plugs? I use a 5/16" bit to drill probe holes.

 

Thanks in advance!

Views: 3167

Reply to This

Replies to This Discussion

I use furnace cement.  Up to 3000 degree tolerance, inexpensive and easy to apply.  I carry a small jar with an applicator inside.

I like to leave things as close to the way I found them.

Patrick,

These are what works for the programs I am involved in New Jersey and Pennsylvania. They are specifically made for the purpose of plugging test holes. The price is good too. Make sure you use a step drill bit, otherwise they may not snap in and hold.

http://www.trutechtools.com/metalplug

Andrew

RSS

Latest Activity

Thayne Brunswold is now a member of Home Energy Pros
1 hour ago
Martin Newmark posted a discussion

Best Practice for Retrofit Insulation on Modern Knee Walls in Attics

I'm wondering what folks are doing to add air-sealing and insulation to knee walls in modern…See More
1 hour ago
Don Hynek replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"First of all (as has been noted) it's good you are getting an electrician in there. The…"
7 hours ago
Margaret Okuzumi liked Home Energy Magazine's blog post The Results Are In: These Are The Most Energy-Efficient Utilities in the US
9 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service