Proper means to "plug" flue pipes after testing gas appliances.

I have seen metal "plugs" (and this may not be the correct term) used for the holes that are drilled in vent pipes, in order to test combustion appliances.

 

I'm referring to the type 1 vent pipe that is standard for atmospherically-vented gas appliances.

 

These plugs appear to be superior to HVAC foil tape. Any thoughts on this?

 

Also, does anybody know how to get their hands on these metal plugs? I use a 5/16" bit to drill probe holes.

 

Thanks in advance!

Views: 2827

Reply to This

Replies to This Discussion

I use furnace cement.  Up to 3000 degree tolerance, inexpensive and easy to apply.  I carry a small jar with an applicator inside.

I like to leave things as close to the way I found them.

Patrick,

These are what works for the programs I am involved in New Jersey and Pennsylvania. They are specifically made for the purpose of plugging test holes. The price is good too. Make sure you use a step drill bit, otherwise they may not snap in and hold.

http://www.trutechtools.com/metalplug

Andrew

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Carrie Sturrock posted an event

Making an Old Home More Livable: Where to Start and When to Ask for Help at Webinar

September 15, 2016 from 11am to 12pm
Making an Old Home More Livable: Where to Start and When to Ask for HelpUpgrading and weatherizing…See More
55 minutes ago
Carrie Sturrock posted photos
1 hour ago
Carrie Sturrock posted a status
"Hi Diane! Thank you so much. Indow is excited to be a part of this home performance conversation -"
1 hour ago
Quinn Korzeniecki posted a discussion

Healthy Home Evaluator Pilot Exam Closes September 9, 2016

Malta, NY, August 29, 2016 - The Building Performance Institute, Inc. (BPI) will complete the…See More
1 hour ago
Chris Champagne is now a member of Home Energy Pros
6 hours ago
Diane Chojnowski replied to John Nicholas's discussion Slab Edge Insulation - A Side Thread to Melissa's Question
"Great videos Daniel. Would you please add them to our videos…"
yesterday
David Holtzclaw replied to Steve Mann's discussion Alnor 6200 LoFlo Capture Hood in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Steve I'm interested 402-213-3788 dholtzclaw@transductiontechnologies.com thanks david "
yesterday
Eric Kjelshus replied to Steve Mann's discussion Alnor 6200 LoFlo Capture Hood in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"call me Monday 816-537-5100 "
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service