Proper means to "plug" flue pipes after testing gas appliances.

I have seen metal "plugs" (and this may not be the correct term) used for the holes that are drilled in vent pipes, in order to test combustion appliances.

 

I'm referring to the type 1 vent pipe that is standard for atmospherically-vented gas appliances.

 

These plugs appear to be superior to HVAC foil tape. Any thoughts on this?

 

Also, does anybody know how to get their hands on these metal plugs? I use a 5/16" bit to drill probe holes.

 

Thanks in advance!

Views: 1555

Reply to This

Replies to This Discussion

Thanks David.

 

The issue for me still remains whether a quality plug for metal and high heat applications exists. The plug referenced in the discussion from a few months ago was a plastic plug, and therefore it would not hold up under flue gas temperatures that average 300 - 400 degrees.

 

The search goes on...

I know that we don't want to raise any questions from our customers about holes in their flues, but if there is a negative pressure inside the flue, do we HAVE to seal it?  As an example, a conventional gas water heater has 15-20 in2 of opening at the draft hood, and we are just a few inches away from there with our 5/16" diameter hole with less than an additional .1 in2 (one tenth of a square inch).  We use 181 tape and won't feel bad if it falls off - we have never gotten a complaint about this happening.  If you feel you must plug this hole, screw a short stainless slotted head machine screw into the hole, adjusting the drill size to make this easy.  YMMV.

Ed Minch

Thanks Ed!

 

I hear where you're coming from, and I can't think of anything against the point(s) you have raised.

I use the snap in metal plugs. In a previous life, my work in service & installation management-in particular when it came to NFPA situations and the like-  taught me that if you make some sort of modification to a product, you must make a suitable good faith effort to keep the product within the standards intended by the manufacturer. In this situation, I interpret that to mean when drilling a hole in metal for a test, it should be plugged with metal. 

There may be some legal line of reasoning behind this as well. An inexpensive metal plug that is sized properly will leave the homeowner with the impression of the mark of a well-equipped professional and may also avoid a potential liability claim. I have met some homeowners who look for the smallest reason to stir up trouble.  

Thanks a lot Bruce. That's good perspective to have.

 

Here's a link to the metal plugs I use for single wall metal flues. Recommended by my BPI training provider. They have worked well for me. Sorry, there's no picture of the product on their site.

Downside is that the price doubles with shipping charges when you order a single 20 pc bag. 

  a-386, 5/16" hole plug

http://www.dwyer-inst.com/Products/Product.cfm?Group_ID=20005&P...

 

Hope that helps!

Thanks a lot Jeffrey! I think you hit the nail on the head.

 

Patrick

No problem.

Forgot to mention, but it helps to have a flat file with you to clean up the hole from the drilling when necessary.

Be careful with HVAC metal tape may are not rated for the heat a flue produces.

I realize you are looking for a manufactured plug, but good old fashioned hi-temp. silicone always does the job. If Josh Lloyd sees this, perhaps he can chime in on pre made hi-temp. silicone plugs which are used by the program he works with.

Ed

Remember that ALL silicone is hi-temp.  If memory serves, the clear is 580 degrees for some amount of time, and the colored stuff is 20-30 degrees better - red and black being the best.  Just make sure to use pure silicone, not something like acrylic latex with only some silicone.

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Christopher Morin posted a blog post

5 Things New Energy Efficiency HVAC Contractors Need to Know

1. Do not sell on Price! Use 'Simple Payback'The price of High-efficient equipment will undoubtedly…See More
3 hours ago
David Eggleton commented on David Eggleton's group Considering Permaculture &/or Transition
"In August 2014, in Minnesota, there's another unprecedented opportunity to meet and mix with a…"
10 hours ago
Glen Gallo commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Nate, RE: Duct test On my own home and a rental I have tested more than once over the last many…"
11 hours ago
Profile Iconangela hines and Charles Goldman joined Home Energy Pros
15 hours ago
Jeff Flaherty joined Diane Chojnowski's group
Thumbnail

Tools of the Trade

A hammer and a saw used to be the key tools for home contractors. Today, the best-in-breed also use…See More
yesterday
Jeff Flaherty joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Debra Little joined David Eggleton's group
Thumbnail

Considering Permaculture &/or Transition

Some who work to increase energy efficiency and intelligent/wise use of energy are, and some will…See More
yesterday
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Thanks for all the comments. Yes, it is interesting how the duct leakage grew over the years. Maybe…"
yesterday
Ed Minch commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"What sort of energy bill do you have now, what is  your target bill, and what will it cost to…"
yesterday
Nate Adams commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I look forward to hearing more about the inside of the program! The big question that came to mind…"
yesterday
Glen Gallo commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"It is curious to see a 15% difference in the duct test from the test out of 2007 to the current…"
yesterday
John Proctor commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"So Jim, any idea as to how your ducts sprung another 15% leakage between 2007 and 2014? You also…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service