Proper means to "plug" flue pipes after testing gas appliances.

I have seen metal "plugs" (and this may not be the correct term) used for the holes that are drilled in vent pipes, in order to test combustion appliances.

 

I'm referring to the type 1 vent pipe that is standard for atmospherically-vented gas appliances.

 

These plugs appear to be superior to HVAC foil tape. Any thoughts on this?

 

Also, does anybody know how to get their hands on these metal plugs? I use a 5/16" bit to drill probe holes.

 

Thanks in advance!

Views: 1559

Reply to This

Replies to This Discussion

Thanks David.

 

The issue for me still remains whether a quality plug for metal and high heat applications exists. The plug referenced in the discussion from a few months ago was a plastic plug, and therefore it would not hold up under flue gas temperatures that average 300 - 400 degrees.

 

The search goes on...

I know that we don't want to raise any questions from our customers about holes in their flues, but if there is a negative pressure inside the flue, do we HAVE to seal it?  As an example, a conventional gas water heater has 15-20 in2 of opening at the draft hood, and we are just a few inches away from there with our 5/16" diameter hole with less than an additional .1 in2 (one tenth of a square inch).  We use 181 tape and won't feel bad if it falls off - we have never gotten a complaint about this happening.  If you feel you must plug this hole, screw a short stainless slotted head machine screw into the hole, adjusting the drill size to make this easy.  YMMV.

Ed Minch

Thanks Ed!

 

I hear where you're coming from, and I can't think of anything against the point(s) you have raised.

I use the snap in metal plugs. In a previous life, my work in service & installation management-in particular when it came to NFPA situations and the like-  taught me that if you make some sort of modification to a product, you must make a suitable good faith effort to keep the product within the standards intended by the manufacturer. In this situation, I interpret that to mean when drilling a hole in metal for a test, it should be plugged with metal. 

There may be some legal line of reasoning behind this as well. An inexpensive metal plug that is sized properly will leave the homeowner with the impression of the mark of a well-equipped professional and may also avoid a potential liability claim. I have met some homeowners who look for the smallest reason to stir up trouble.  

Thanks a lot Bruce. That's good perspective to have.

 

Here's a link to the metal plugs I use for single wall metal flues. Recommended by my BPI training provider. They have worked well for me. Sorry, there's no picture of the product on their site.

Downside is that the price doubles with shipping charges when you order a single 20 pc bag. 

  a-386, 5/16" hole plug

http://www.dwyer-inst.com/Products/Product.cfm?Group_ID=20005&P...

 

Hope that helps!

Thanks a lot Jeffrey! I think you hit the nail on the head.

 

Patrick

No problem.

Forgot to mention, but it helps to have a flat file with you to clean up the hole from the drilling when necessary.

Be careful with HVAC metal tape may are not rated for the heat a flue produces.

I realize you are looking for a manufactured plug, but good old fashioned hi-temp. silicone always does the job. If Josh Lloyd sees this, perhaps he can chime in on pre made hi-temp. silicone plugs which are used by the program he works with.

Ed

Remember that ALL silicone is hi-temp.  If memory serves, the clear is 580 degrees for some amount of time, and the colored stuff is 20-30 degrees better - red and black being the best.  Just make sure to use pure silicone, not something like acrylic latex with only some silicone.

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Richard Vito joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
3 minutes ago
Richard Vito joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
4 minutes ago
Richard Vito joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
4 minutes ago
Richard Vito joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
5 minutes ago
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I had a revelation while attending Bruce Manclark's session of duct leak testing at the Energy…"
14 hours ago
George J. Nesbitt commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Blower Door; the 2007 test was a depressurization test, and the 2014 a pressurization test, which…"
14 hours ago
George J. Nesbitt replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Plan, plan, plan, plan. The 1st step to is to understand the house, how it's built, the…"
14 hours ago
George J. Nesbitt posted an event

High Performance Windows - A Panel of Experts at Pyramid Alehouse`

April 26, 2014 from 3pm to 5pm
Join a lively panel discussion on high performance windows. We'll cover some basics, as well as…See More
16 hours ago
Kaushal Bharath Raju replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Hi David, Thanks for pointing out Martin Holiday's article. I do not wish to engage in the…"
16 hours ago
Profile IconAdam Penberthy, Scot Davidson and j jarvella joined Home Energy Pros
16 hours ago
David Eakin replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"More food for thought on this subject - read this (fairly) recent blog by one of the most respected…"
21 hours ago
Curt Kinder commented on Christopher Morin's blog post 5 Things New Energy Efficiency HVAC Contractors Need to Know
"You left out air distribution...Without at least a passing glance at how much air moves through the…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service