Proper means to "plug" flue pipes after testing gas appliances.

I have seen metal "plugs" (and this may not be the correct term) used for the holes that are drilled in vent pipes, in order to test combustion appliances.

 

I'm referring to the type 1 vent pipe that is standard for atmospherically-vented gas appliances.

 

These plugs appear to be superior to HVAC foil tape. Any thoughts on this?

 

Also, does anybody know how to get their hands on these metal plugs? I use a 5/16" bit to drill probe holes.

 

Thanks in advance!

Views: 2202

Reply to This

Replies to This Discussion

Thanks David.

 

The issue for me still remains whether a quality plug for metal and high heat applications exists. The plug referenced in the discussion from a few months ago was a plastic plug, and therefore it would not hold up under flue gas temperatures that average 300 - 400 degrees.

 

The search goes on...

I know that we don't want to raise any questions from our customers about holes in their flues, but if there is a negative pressure inside the flue, do we HAVE to seal it?  As an example, a conventional gas water heater has 15-20 in2 of opening at the draft hood, and we are just a few inches away from there with our 5/16" diameter hole with less than an additional .1 in2 (one tenth of a square inch).  We use 181 tape and won't feel bad if it falls off - we have never gotten a complaint about this happening.  If you feel you must plug this hole, screw a short stainless slotted head machine screw into the hole, adjusting the drill size to make this easy.  YMMV.

Ed Minch

Thanks Ed!

 

I hear where you're coming from, and I can't think of anything against the point(s) you have raised.

I use the snap in metal plugs. In a previous life, my work in service & installation management-in particular when it came to NFPA situations and the like-  taught me that if you make some sort of modification to a product, you must make a suitable good faith effort to keep the product within the standards intended by the manufacturer. In this situation, I interpret that to mean when drilling a hole in metal for a test, it should be plugged with metal. 

There may be some legal line of reasoning behind this as well. An inexpensive metal plug that is sized properly will leave the homeowner with the impression of the mark of a well-equipped professional and may also avoid a potential liability claim. I have met some homeowners who look for the smallest reason to stir up trouble.  

Thanks a lot Bruce. That's good perspective to have.

 

Here's a link to the metal plugs I use for single wall metal flues. Recommended by my BPI training provider. They have worked well for me. Sorry, there's no picture of the product on their site.

Downside is that the price doubles with shipping charges when you order a single 20 pc bag. 

  a-386, 5/16" hole plug

http://www.dwyer-inst.com/Products/Product.cfm?Group_ID=20005&P...

 

Hope that helps!

Thanks a lot Jeffrey! I think you hit the nail on the head.

 

Patrick

No problem.

Forgot to mention, but it helps to have a flat file with you to clean up the hole from the drilling when necessary.

Be careful with HVAC metal tape may are not rated for the heat a flue produces.

I realize you are looking for a manufactured plug, but good old fashioned hi-temp. silicone always does the job. If Josh Lloyd sees this, perhaps he can chime in on pre made hi-temp. silicone plugs which are used by the program he works with.

Ed

Remember that ALL silicone is hi-temp.  If memory serves, the clear is 580 degrees for some amount of time, and the colored stuff is 20-30 degrees better - red and black being the best.  Just make sure to use pure silicone, not something like acrylic latex with only some silicone.

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Profile IconBenney Dornevil, Mike Norvell Sr and Jen Loomis joined Home Energy Pros
7 hours ago
Joanie Minor posted a status
"Home Performance Institute now offers OSHA 10 and Confined Space Classes. Call 203-536-2151 to register."
8 hours ago
Joanie Minor posted a photo
8 hours ago
John Kaye posted a blog post

FREE Home Efficiency & Safety Assessments in the Los Angeles County area.

Since last June I have been qualifying homeowners in the Los Angeles County for the Home Upgrade…See More
14 hours ago
Eric Kjelshus replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Those 240 Volt aquastats shut off and then on kinda quick back on.  The older the tank the…"
18 hours ago
Rod Fox replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Well I'd love to tell you folks I found an answer, but I did not... I went to my…"
yesterday
Rod Fox replied to Kevin Eigel's discussion What is the best energy auditing software?
"I've been trying to answer this question for many years and have not yet found an answer.…"
yesterday
Jerry Lawrence posted events
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service