Is any one familiar with the Peak Energy Saver from www.peakenergytech.com  The unit is intended to store energy from motors used in the home and then supply the stored energy back to the home, thus reducing consumption.  Clames to reduce energy consumption between 10% and 25%.   Fact or Fiction, does any one know?   

Thanks PJ Stevens 

Views: 1255

Reply to This

Replies to This Discussion

Thanks Bob.  This providing me a quick uptake on the whole issue...greatly appreciated!

You're welcome Fred. Good luck to you.

Power factor correction is old, well established technnlogy which is widely used across industry and larger electricity power users. However this technology is used to reduce wasted power measuured as Kvar to bring KVA closer to KW and is not well known industry wide to be used for the above application. Further information can be seen at http://www.streamline-power.com/power_factor_correction.html
Therefore there would need to be authoritative offical independent research conducted for reliable information.

Power Factor Correction is ONLY worth considering for electricity users who are penalized (billed) for inadequate power factor by the utility. All others are billed for kW, not KVA, so it is a complete waste of money for all others to fall prey to scammers hawking power factor correction devices to homeowners and typical commercial customers.

Unfortuantely that is not the whole picture. Granted billing is in KW however improving power factor in an industrial/commercial environment will have a saving as motors will now be operating optimally hence be more efficent so last longer with less maintenance.

Because also KVA is closer to KW then any voltage optimisiation equipment will also make more savings.

Horsefeathers!

Improving a building or plant's power factor does NOTHING for individual motors. I sincerely hope you are not hawking your views for personal gain.

I like your phrase horsefeathers though here in the UK we may say rockin' horse dung!.... joking aside though I can only vouch for how industrial 3phase sites are billed here, the US may be different billing. So installing PFC equipment will (a) reduce the Kvar known as the reactive charge (b) potentially reduce the availability or capacity charge and (c) reduce the load on the transformer, the I2R losses or load losses. Potentially also reduce line losses but that will depend where the capacitors are placed.

Well, I work with the conservation guys at a big local electric utility. One of them told me, by way of agreeing that residential power factor correction is a complete scam, that out of their 400,000 (yes - four hundred thousand) electric customers, only FOUR are on power factor billing.

I imagine those four are large industrial sites, such as paper mills, with access to engineers to evaluate and implement alternatives.

4 out of 400K? All 4 are most likely large industrial customers with 3 phase power. There is absolutely no reason for any residential customer to be concerned about this. I've never seen/heard of any time of PF charge on single phase power.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

George Matthews replied to George Matthews's discussion Shortridge 8400 Flowhood for A/C airflow testing in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Here are the pics of the flowhood and airdata manometer"
yesterday
Sarah Holloway posted a photo
yesterday
Joe Urycki added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

TEC blower door and UEI combustion analyzer for sale

For sale is one used TEC Minneapolis blower door system: Includes model 3 fan with rings A and B,…See More
Friday
John Nicholas replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"The Nay side is well represented with the links already posted. I presented a neutral side, with…"
Friday
Ray Lehman replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"Hey John, Thanks for the information.  Very good empirical data. While I agree that running…"
Friday
John Nicholas replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"I have no links, just some anecdotal evidence. I had several Blower Door Tests done on my own home.…"
Friday
Chris Laumer-Giddens commented on Chris Laumer-Giddens's blog post Raising the BARrier in North Carolina Mountain Home, Air Tight Ceiling
"@Joe Nagan, We have found this technique to be WAY simpler and A LOT less labor than making a…"
Thursday
Judy Rachel replied to Blake Shurtz's discussion Testing spillage on induced draft furnace?
"I hope the attached picture is clear enough for you to see.  As the caption on the picture…"
Thursday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service