We recently installed a Buderus high efficency direct vent condensing boiler in a closed furnace room. The homeowner reports significant unpleasant smells coming into the house. Ambient air testing does not show any by-products of combustion, and the company technician inspected the unit and says it is installed properly and operating properly. 

 

The room is enclosed and gets hot. The smell seems to be off-gassing from the unit itself and from the copper pipes. 

 

The install was over a month ago and the homeowner is still bothered by the smell.

 

Has anyone else dealt with this problem ?  What can be done?

Views: 887

Reply to This

Replies to This Discussion

It looks like this boiler could run a positive pressure inthe combustion chamer. There might be leakage in the boiler or the vent system. It could be smoke tested to visually find the leak. I have done this on other power burners. Not sure what the model is but here is a link ot a manual that you might get some ideas from.

 

http://www.buderus.us/files/201001241621170.6720615078GB125Burner.pdf

 

 

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Eric Kjelshus on Saturday. 4 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy Mar 23. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas Mar 23. 2 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Chris Dorsi commented on Home Energy Magazine's blog post The Elephant in the Room
"This was a great session, witness the fact that we had to schedule a second showing to accommodate…"
6 hours ago
Chris Dorsi liked Home Energy Magazine's blog post The Elephant in the Room
6 hours ago
eric anderson added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Equipement still for sail (what is left from what I was selling before)

For some reason I can't reply to my previous thread.  I sold the blower door and duct blaster/flow…See More
13 hours ago
Mark Sackerson replied to angela stanzione's discussion Used Weatherization and auditing equipment for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Angela, Do you have any blower door sets left? mark"
14 hours ago
Mark Sackerson replied to Jeffrey Anthony's discussion Blower Door Kits in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Jeffrey, do you have any blower door kits left? mark msackerson@franzoso.com"
14 hours ago
Mark Sackerson joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
14 hours ago
Profile IconMark Sackerson and Matt Ward joined Home Energy Pros
14 hours ago
Quinn Korzeniecki's discussion was featured

Join BPI's New Professional Website Focus Group

Want to be part of the elite group of individuals that views the new BPI professional website…See More
14 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service