Hello energy pros.

I need your combined wisdom before I proceed to help a client of mine address what appears to be mold growth and draftiness after I completed attic air sealing and other miscellaneous measures on her home.

The HO owns a split level in Northern VA. She, her husband, and three children have lived in this house for three years.

The house has existing exterior wall insulation, and some attic insulation. No rim joist air sealing or insulation and no foundation wall insulation. 

We sealed the entire attic above the two-story section of their split level (above the bedrooms), and replaced the existing blown-in fiberglass. We also insulated a section of exterior wall in their laundry room that was driving discomfort in their house with closed-cell spray foam. Finally, we insulated the floor between the 1st and 2nd story (between bedrooms) for sound attenuation purposes.

About one month after completing the work the HO e-mailed me to say that surface mold had begun to form on the exterior wall of the 1st story bedroom that we insulated the ceiling above and adjacent to the wall we spray foamed. This is the main concern at this point.

Before I run over there later this week and try to determine what is going on, I'd like to tap the knowledge that you all bring to the table.

My sense is that there is cold air rushing into this exterior wall through the rim joists in the basement. The cold air is mixing with warm conditioned air that is leaking into the walls through outlets and baseboards, and the air sealing of the top plates is keeping the air in the walls, but also allowing cold air to mix with warm, introducing condensation within the wall.

The HO also mentioned condensation on some of the glazing. One final detail I want to mention is that they have a gas insert in the 2-story section of the house (on the 1st floor).

Any ideas on what may be taking place, or tips on how best to proceed? 

Thanks in advance!

Views: 737

Reply to This

Replies to This Discussion

Thanks Kevin.

You leave me with a lot to consider.

I will likely need to follow-up on the matter.

Good point on the gas insert. Those do put out a lot of moisture.

 

The condensation on the windows is a clear indicator that humdity in the house is high enough to expect moisture accumulation on cold walls.

 

The question is whether the cause is a damp fall or a source in the house.

 

In my experience, DC houses that are weatherized don't typically have summertime humidity problems. AIr sealing sharply reduces the added humidity from infiltrating humid air. Since many projects don't improve wall insulation or glazing, AC loads don't go down all that much and dehumidification is adequate. In many cases the reduced humid infiltration seems to more than offset the lost dehumidification of lower runtime. In my experience anway.

Patrick, what is ACH50? ACHnat?

Where is the dryer vent located? Has it been moved or damaged during work? Was it inspected? Is the hose full of lint?

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Anthony Adams posted a status
"Trying to figure heat load for HVAC on bonus room over a garage. Lots of wall space exposed to arttic."
48 minutes ago
Profile IconTirso De Ubago, Hamed Ghanbari, Bob Eldredge and 1 more joined Home Energy Pros
9 hours ago
Hamed Ghanbari replied to Brian's discussion Everything you need to become a energy auditor for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hello, I am interested to buy a Minneapolis Blower Door DG700. How much is your unit? Thanks. "
12 hours ago
Hamed Ghanbari joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
12 hours ago
Colin Genge updated an event
Thumbnail

Measuring HVAC Performance webinar at Online

February 23, 2016 from 11am to 12pm
If you install, service or test HVAC systems you will want be there for this special webinar.…See More
16 hours ago
Colin Genge updated an event
Thumbnail

Testing for IECC Code Compliance for duct and house leakage webinar at Online

February 16, 2016 from 11am to 12pm
The International Energy Conservation Code (IECC) is in use or adopted in 47 states, the District…See More
16 hours ago
Jan Green posted a status
"I'm honored to be selected to speak at the 2016 RESNET Conference right here in sunny Scottsdale 2/29-3/2/16 with SRP & others!"
17 hours ago
Joe Konopacki posted an event

Duct & Envelope Tightness (DET) Verifier at Temperature Equipment Corporation

February 26, 2016 from 8:30am to 4:30pm
The Duct & Envelope Tightness Certification (DET) was designed by the Midwest Home Performance…See More
18 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service