Hello All,

We are working on a project with Habitat and our trying to provide recommendations for ventilation. We would like to see them install a Spot ERV like Panasonic's Whisper Comfort, but the small (<1,500sf) home (4 bdr) requires just over 50cfm fresh air. The Panasonic can only provide 40cfm continuous and installing two brings the incremental cost over an air cycler strategy or supply ventilation strategy too far off budget.

Does anyone have any experience / recommendations for how to best address this situation?

We are in Climate Zone 4, in Middle Tennessee, mixed-humid.

Thanks for any information!

Stefan

Tags: 62.2, ERV, ashrae, ventilation

Views: 573

Reply to This

Replies to This Discussion

Buy a larger one & use a timer - trust me when I say you do not want them running 24x7, especially in a humid enviroment

Sean, help a cold-climate guy out here... what's the issue with humidity and 24/7 run-time?

The humidity inside rises to much & in small houses where the AC unit is oversized because we cant buy a small enough unit...

There are a couple of pretty nifty choices from Venmar.  The Kubix unit comes in either an HRV or ERV version.  It uses 60 watts, 77% Apparent Sensible Effectiveness (ASE).  It's like a 16" cube using 4" ducting.  A more energy efficient alternative is the EKO version.  The ERV version is 73% ASE.  It uses between 26 and 37 watts with flows up to 84 cfm.  It doesn't require a drain in the ERV version.

These are not ceiling mounted units like the Panasonic, but I think getting the supplies and exhausts separated is a better way to go if possible.

I also work with Habitat and like yours, our houses have oversized units because of the extreme tightness, low UA numbers and limitations on ASHP systems.  We use a cycle timer and motorized damper for supply air ventilation. We are also considering ERV/HRV but before choosing and ERV I would have to ask if the manufacturer  can supply a certification that the latent energy (water) recovery does not include any VOC, airborne pathogens or aerosols from toilets. My request to Venmar got circled back to our sales rep who was unsure if such a certification was required.

RSS

Videos

  • Add Videos
  • View All

Latest Activity

Jan Green liked Chris Laumer-Giddens's blog post Rock Wool Insulation for Floor of High Performance Tiny House
2 hours ago
Carly Maltais posted a discussion

Comparing the AirCycler g2 and HRV [Infographic]

AirCycler is excited to share that we have recently launched a new version of our…See More
6 hours ago
SolyMoly, Inc posted discussions
8 hours ago
Home Energy Magazine's blog post was featured
13 hours ago
Brad Cook replied to Jim Tenhundfeld's discussion LED's and motion sensors
"I don't know what it stands for. See RAB.com"
Saturday
Jim Tenhundfeld replied to Jim Tenhundfeld's discussion LED's and motion sensors
"That makes sense since the same thing happened with dimmable CFL's.  I have never heard…"
Saturday
Brad Cook replied to Jim Tenhundfeld's discussion LED's and motion sensors
"My first thought is whether the motion sensor and/or the LED lamp is a cheap one. I had so many…"
Saturday
John Wagner joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
Friday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service