Hello All,

We are working on a project with Habitat and our trying to provide recommendations for ventilation. We would like to see them install a Spot ERV like Panasonic's Whisper Comfort, but the small (<1,500sf) home (4 bdr) requires just over 50cfm fresh air. The Panasonic can only provide 40cfm continuous and installing two brings the incremental cost over an air cycler strategy or supply ventilation strategy too far off budget.

Does anyone have any experience / recommendations for how to best address this situation?

We are in Climate Zone 4, in Middle Tennessee, mixed-humid.

Thanks for any information!


Tags: 62.2, ERV, ashrae, ventilation

Views: 565

Reply to This

Replies to This Discussion

Buy a larger one & use a timer - trust me when I say you do not want them running 24x7, especially in a humid enviroment

Sean, help a cold-climate guy out here... what's the issue with humidity and 24/7 run-time?

The humidity inside rises to much & in small houses where the AC unit is oversized because we cant buy a small enough unit...

There are a couple of pretty nifty choices from Venmar.  The Kubix unit comes in either an HRV or ERV version.  It uses 60 watts, 77% Apparent Sensible Effectiveness (ASE).  It's like a 16" cube using 4" ducting.  A more energy efficient alternative is the EKO version.  The ERV version is 73% ASE.  It uses between 26 and 37 watts with flows up to 84 cfm.  It doesn't require a drain in the ERV version.

These are not ceiling mounted units like the Panasonic, but I think getting the supplies and exhausts separated is a better way to go if possible.

I also work with Habitat and like yours, our houses have oversized units because of the extreme tightness, low UA numbers and limitations on ASHP systems.  We use a cycle timer and motorized damper for supply air ventilation. We are also considering ERV/HRV but before choosing and ERV I would have to ask if the manufacturer  can supply a certification that the latent energy (water) recovery does not include any VOC, airborne pathogens or aerosols from toilets. My request to Venmar got circled back to our sales rep who was unsure if such a certification was required.



  • Add Videos
  • View All


Latest Activity

Debra Little posted a video

Building Carbon Zero 2015, PHCA

Building Carbon Zero 2015. Passive House CA with City of Palo Alto 2015 summit. Produced by Debra Little. Shot on iPhone 5. Everyone can make videos with the tools in your back pocket!
1 hour ago
Home Energy Magazine's blog post was featured
11 hours ago
Profile IconDave Chamberlain, angela stanzione and Bruce Zahn joined Home Energy Pros
11 hours ago
Paul Holder added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase

Blower Door frame

Looking for a blower door frame for Minneapolis blower door. Needing a 2nd. frame if anyone has one…See More
15 hours ago
Joe Urycki replied to Joe Urycki's discussion TEC blower door and UEI combustion analyzer for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Yes, I do still have the equipment.  Are you interested in it?"
Amber Vignieri commented on Amber Vignieri's blog post Even with Polar Vortex, Hourly Pricing Participants Saved
"Thanks for your comment Bob! We couldn't be more excited about the increasing prevalence of…"
Home Energy Magazine posted a blog post
Noah Ray Sanders replied to Steve Mann's discussion TEC Blower Door Frame in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"If so please contact me 8329717862 or email noahraysanders@hotmail.com"

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service