When doing a blower door test, do you ever use long term average? Why or why not?

Digital pressure and flow gauges have an option for time averaging, such as 1, 5 or 10 seconds, long term or a manual time average option.

Under what circumstances would you use the long term average and why?

Views: 249

Reply to This

Replies to This Discussion

When the wind is breezy, I use long term averaging. The more the pressure jumps around due to breezes, the longer the term that I use. Even then, I mentally average the readings. This is after I have taken steps to shield the end of the outside hose from the wind.

Wind is caused by a difference in air pressure so the change in air pressure from the wind, or a passing truck, is reflected in the change in the readings of a digital pressure gauge. Keep in mind that 1 pascal is a tiny change of pressure. I find that the best way to get a stable baseline is to insert a "T" fitting into the reference tube and connect 2 reference tubes. Place 1 tube on 1 side of the house and the other tube on the opposite side of the house. Be sure that the tube nearest the blower door is at least 5' (preferably more) from the fan. If the fan needs to be installed where it is blowing into an enclosed porch or mud room (not a good choice unless there is no better alternative) make sure the tube is outside of the porch.

Hi Kim,

Wind is probably the most frequent reason for using the time averaging with our manometers, but there is another that we need to be careful with.  Manometers are unique in that they ignore barometric pressures.  Place your refer tube out the front door and walk your manometer (long tube) upstairs or into the basement and even though the top to bottom pressure may vary (on a cold day) by 50 pascals or more our manometers will register very little.  When the temperature of our tubes and the air inside is the same as in the house, any changes in elevation are canceled out.  However, if those tubes just came out of an ice cold vehicle, or a hot one, and have not fully acclimated, our readings will drift.  In this case, before we start averaging we need to allow those tubes to become room temperature.  The section of tube that goes outside needs to acclimate as well.

Bud

I never use any setting but "long term" average. Any other setting will always give you a less accurate average reading. Under the "long term" setting the manometer automatically calculates a mathematically continuous average. That means that you can "hold " the reading after "any" length of time and it will give the average for all of the seconds that you had the meter running.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Profile IconBenjamin Mailian and Michael Laurie joined Home Energy Pros
22 minutes ago
SmithWatson posted a blog post

It is time to replace your boiler, isn’t it?

Have you suddenly started noticing a spike in your energy bills? If yes, one of the main things you…See More
1 hour ago
Theresa L Gilbride's blog post was featured

Find out whose building some of the best-performing homes in the country today with DOE’s Tour of Zero

Home buyers across the country can find out where the home of the future is available today with…See More
16 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Obama Announced New Actions to Bring Energy Efficiency to Households across the Country

Big news out of The White House last week for the ‪‎clean energy‬ housing sector: HUD and DOE have…See More
19 hours ago
Theresa L Gilbride posted a blog post

Find out whose building some of the best-performing homes in the country today with DOE’s Tour of Zero

Home buyers across the country can find out where the home of the future is available today with…See More
20 hours ago
Colin Genge commented on Chris Laumer-Giddens's blog post Building Science is Worthless...
"We has passive house tester complaining the Aluminum Frame leaked too much so we measured them at…"
22 hours ago
Michael Dunseith posted a photo
23 hours ago
Michael Dunseith replied to Kim Tanner's discussion Fantastic innovation
"It was designed for air handlers to determine the total system air flow. I It would be installed in…"
23 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service