When doing a blower door test, do you ever use long term average? Why or why not?

Digital pressure and flow gauges have an option for time averaging, such as 1, 5 or 10 seconds, long term or a manual time average option.

Under what circumstances would you use the long term average and why?

Views: 249

Reply to This

Replies to This Discussion

When the wind is breezy, I use long term averaging. The more the pressure jumps around due to breezes, the longer the term that I use. Even then, I mentally average the readings. This is after I have taken steps to shield the end of the outside hose from the wind.

Wind is caused by a difference in air pressure so the change in air pressure from the wind, or a passing truck, is reflected in the change in the readings of a digital pressure gauge. Keep in mind that 1 pascal is a tiny change of pressure. I find that the best way to get a stable baseline is to insert a "T" fitting into the reference tube and connect 2 reference tubes. Place 1 tube on 1 side of the house and the other tube on the opposite side of the house. Be sure that the tube nearest the blower door is at least 5' (preferably more) from the fan. If the fan needs to be installed where it is blowing into an enclosed porch or mud room (not a good choice unless there is no better alternative) make sure the tube is outside of the porch.

Hi Kim,

Wind is probably the most frequent reason for using the time averaging with our manometers, but there is another that we need to be careful with.  Manometers are unique in that they ignore barometric pressures.  Place your refer tube out the front door and walk your manometer (long tube) upstairs or into the basement and even though the top to bottom pressure may vary (on a cold day) by 50 pascals or more our manometers will register very little.  When the temperature of our tubes and the air inside is the same as in the house, any changes in elevation are canceled out.  However, if those tubes just came out of an ice cold vehicle, or a hot one, and have not fully acclimated, our readings will drift.  In this case, before we start averaging we need to allow those tubes to become room temperature.  The section of tube that goes outside needs to acclimate as well.

Bud

I never use any setting but "long term" average. Any other setting will always give you a less accurate average reading. Under the "long term" setting the manometer automatically calculates a mathematically continuous average. That means that you can "hold " the reading after "any" length of time and it will give the average for all of the seconds that you had the meter running.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Colin Genge posted events
56 minutes ago
John Nicholas replied to Sean Lintow Sr's discussion Duct Testing - is a change in order? in the group Best Practices (Residential)
"Yes,  I was connected to the AH cabinet.  I find it easier in this area, given the common…"
3 hours ago
Colin Genge replied to Kim Tanner's discussion Blower Door Applications Guide in the group Multifamily Buildings
"This is a great guide that anyone testing with multiple fans should get hold  of. "
3 hours ago
Colin Genge added a discussion to the group Multifamily Buildings
Thumbnail

Just posted a lot of Multi-Family oriented blower door videos.

Just posted a lot of Multi-Family oriented blower door videos. Everything to do with Multi-Fan…See More
3 hours ago
Colin Genge joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
3 hours ago
Colin Genge replied to Sean Lintow Sr's discussion Duct Testing - is a change in order? in the group Best Practices (Residential)
"I would assume you tested that high air leakage from the equipment cabinet and not on a flex…"
4 hours ago
Colin Genge replied to Sean Lintow Sr's discussion Blower Doors & Methods Used in the group Best Practices (Residential)
"For those of you who need  a Tectite report, FanTestic's report Generator is powerful…"
4 hours ago
Colin Genge joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
4 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service