Insulating Rigid Ducts in attic space - best practices?

We run into a lot of uninsulated ducts in our hot Arizona attics. I would like to know other peoples best practices for insulating - products and retrofit techniques.

I am well aware that it would be best to move ducts into conditioned space, so let's save that for another thread - this is for the customers that do not have that sort of budget but also do not want to leave them uninsulated.

My first design is using a 2" R8 batt which comes in 4' widths - Knauf Friendly Feel® Duct Wrap and fastening with Zip-Ez fasteners. I am thinking of either sealing the seam with butyl tape or duct mastic.

How about one of the bubble wrap products?

How do you deal with duct runs sitting directly on bottom chords?

Thanks for your input,

Craig

Views: 9192

Reply to This

Replies to This Discussion

Bubble wrap is nothing but marketing BS, and the FG isn't even going to be close to R8 when you get it installed

First I would fix the duct leakage, air seal the attic area under & around the ducts & dense pack cellulose under the duct

Wrap duct with foam board on 3 sides - 2 layers offsetting your seams & corners (Liquid Nail actually holds pretty well & not much is needed, though that product you listed may work ok also) - finish off sealing all seams &edges with special UL listed HVAC tape

Finish off the attic air sealing & blowing in cellulose

Sean - I am with you on the duct/air seal - it is in all my scopes. While I like your idea in theory, the practicality is an issue for me. The labor involved would be 3 times as much as a fibrous insulation due to all the cutting and fitting you would need to do. Additionally, most codes do not allow for rigid foam board to be left exposed in the attic, so you would need a thermal barrier.

The compressed R-value on the 2.5in batt(R8.5) is 7.0, the 2.0in batt(R8.2) is 6.4 at 25% compression. It will have to do. It is going to get too hard to install anything thicker. There is a 3" Batt at R10.2 / R8.4 compressed. May try that if it is an easy wrap with lots of clearance.

If the clearance below the duct is too tight, I am thinking spray foam duct to the lid to create an air tight cavity below, bringing it into thermal envelope.

Having been in enough attics out there, I know it can be a nightmare but in reality fitting isn't to difficult  - you simply cut the panels to the average proper width or a fraction larger, adhere, and go (the cutting can be done in the carport or garage). Perfection isn't really required as a little foam can fix any little gaps

Check first with the AHJ, as many simply ignore that piece and/or look at the flame & smoke index rating which eliminates the thermal / ignition issues

Now as for the hallway duct runs where all you can get to is the top - yeah it can be a nightmare but you can easily use foam panels sealed properly above them to bring the ducts into the conditioned space & cover it with more cellulose - voila there is your thermal / ignition barrier 

Craig, are the ducts a mix of round and flat (boxy) sheet metal?

For round ducts, consider slipping flex duct over them (which, if done correctly, can eliminate the need for sealing those ducts).

For flat ducts, I am with Sean. The flame spread ratings are sufficient for attic applications. Also, the install becomes quicker and better with each attempt.

Patrick

I'm not sure some of the replies below adhere to building science principles.  Duct should follow the same principles as the building envelope.  1) The pressure barrier should minimize air flow - seal the duct work at all joints and seams.  Mastic must be used.  Adhesive on tape will not last long term in the heat of an Arizona attic.  Flex duct will not seal rigid duct unless carefully sealed at each end.  2) the thermal barrier should be in contact with the pressure barrier to minimize loss / gain due to convection.  I'm not sure how to do that with a box fabricated with foam board.  The insulation on flex duct is minimal at best.  It would need duct wrap put over it to get anywhere close to R8.  
Best practice required by IECC is to seal with mastic a nickel thick and R-8 duct wrap with minimal compression.  Typically HVAC contractors staple an overlapped seam of duct wrap then seal any exposed fiberglass with foil duct tape.  This keeps moisture (humidity) from infiltration the fiberglass, then condensing on the cold duct.  This may be less of a problem in Arizona than here in Georgia.

We did some studies with a major regional builder in the mid-Atlantic (hot humid).  The spec they finally wrote was: all ducts on the attic floor sitting on the bottom truss chord or the back of the drywall if possible, runs as straight as possible, but gentle curves when needed, sealed tight, then more insulation material blown over the top of the already-insulated duct to about 4-5 inches tapering gradually on the sides.  Computer modeling suggested that this accomplished most of what moving them inside would do - in fact that same builder is finally now moving the ducts inside for V-3.0 of EStar.  

They had an engineer on staff, so complaints from building inspectors were mostly easy to deal with.

For solving problems in this builder's older houses (and all other houses with attic ducts) our policy is cutting all straps holding ducts off the floor of the attic, disconnecting flex at the trunk and re-routing through the truss work to be straight from the boot to the trunk, cutting off excess length of the flex (up to 5-6 feet of duct which is 10-12 ft2 of surface area in a 7" flex duct, and lots of friction), sealing all duct seams, nestling the flex ducts into the existing attic insulation as much as possible, then blowing additional insulation to about an R-20 over the top gradually tapering to the normal attic thickness at the sides.  Some trunks are suspended a foot or so off the attic floor so we will wrap them with another layer of R-8 if blowing is not practical.  This has resulted in about 10-15% more flow out of the treated ducts and also about 4° better temperature on a design day, heating or cooling.  More air with better temperature.

Still leaves that damn air handle sitting there.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

David Eakin replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Kaushal, There was a deep energy retrofit upgrade project (to Passive House standards) in San Jose…"
11 minutes ago
Kim Tanner updated an event

Beyond Residential Testing at The Energy Conservatory

May 14, 2014 to May 16, 2014
The Energy Conservatory (TEC) is hosting a Beyond Residential Testing event. In addition we are…See More
2 hours ago
Casey Gesell posted a video

Super Attic - Attic Insulation System

http://www.drenergysaver.com | 1-888-225-6260 The new Super Attic: Advanced Conversion System -- converts your attic from a vented attic into an unvented at...
2 hours ago

Casey Gesell just added their location.
(via Member Map)

4 hours ago
H.O. Electric posted a video

H.O. Services, Generator, Electrical, Plumbing, Heating, Cooling, Belmont, Lexington, Arlington, MA

H.O. Services is your residential Electric-Plumbing-Heating-Cooling Specialist. We are an electrical contracting company providing homeowners the best Electr...
5 hours ago
Jim Gunshinan's blog post was featured
5 hours ago
Profile IconMichael and michael coleman joined Home Energy Pros
5 hours ago
Luis Hernandez posted a discussion

Air Source Heat pump or mini-split efficiency

Greetings everyone!    I have a technical questions I hope I could get some feedback! I understood…See More
6 hours ago
Jim Gunshinan posted blog posts
yesterday
H.O. Electric posted a photo

about us-team

H.O. Services is your residential Electric-Plumbing-Heating-Cooling Specialist. We are an…
yesterday
H.O. Electric added a discussion to the group News & Announcements
Thumbnail

Stay Cool With Easy To Install Ductless AC System!

Stay Cool With Easy To Install Ductless AC System!   Save $300.00 Off A New AC System For A Limited…See More
yesterday
Richard Wells commented on Diane Chojnowski's group Facebook Pages
"Three thousand home energy efficiency audits, and nearly a thousand retrofits in four short…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service