Installing an indoor swim spa and what type of insulation to use.

     I am consulting on an addition to house an indoor swim spa or endless pool.  I am getting all kinds of feedback from the different insulation companies about what type of insulation to use.  I don't want to recommend something that might be prone to rot in the future, however the spa company has no real guidelines in this area.  Their only suggestion is to install a bath fan in the room.  If the drywall is sealed with bathroom paint and the drywall is caulked impeccably, is moisture in the insulation cavity even an issue?

     I can find no one for whom excessive moisture with one of these things has been an issue.  Is blown in cellulose an option here?  I hate batt insulation because getting a good install is so difficult.  Anyone with some insight would be greatly appreciated.

Views: 3662

Reply to This

Replies to This Discussion

My first thought is to detach the "addition" from the house in order to not introduce the excessive moisture into the house.  My second thought is, if it's going to be a conditioned space, use durock (or similar) and tile on the walls and, ideally, the ceiling.  It's more expense up front, but more durable with the moisture.  I don't see much concern between types of insulation at that point --but I wouldn't use cellulose of using steel studs (moisture concerns again).  You will most likely want a ventilation fan and controlled intake for the space.  I'm open to suggestions / corrections!

If building in cold climate in priority sequence:

- As Marshall Minshew says detach the spa area as much as possible form the rest of the house or at the very least contain the spa's mechnicals within the spa's thermal envelope / extension. 

- As you and the spa company suggest, the room MUST be depressurised to the outdoors to the tune of a few pascals to keep the moist air from driving into the thermal envelope. You can turn it off if the humidity outside ever becomes greater.

 - Avoid skylights (condensation issues in skylight shaft),

 - Keep penetrations through the vapour barrier to an absolute minimum,

 - Air tightness test the envelope before the drywall goes on and make it as tight as possible,

 - Don't run any duct work through the attic space.

 - Isolate the spa's attic from the rest of the house.

 

In the attached picture the ductwork was providing descicated air from a 'Decatron'. Some of that conditioned air was piped into the pool room and some into the flat attic space (see small pipe going up into drywall) so that each skylight shaft could be "washed" with conditioned air (you can faintly see teh grill) to minimise condensation. The result is the drywall was saturated under the domed skylights and the pressurised air ducts running into the flat attic space were likely driving moisture up into the flat roof.

 

Attachments:
What are you spec'ing for the insulation around the pool itself or is it a turnkey factory-built unit?
Most of the design was already decided by the homeowners.  The room is attached, this is southern VA so mixed humid environment.  The room itself will be block walls to match the foundation of the ex. house which will be insulated on the inside with rigid foam.  The pool/spa will sit directly on the concrete.  There will be a floor built 4 inches below finished floor of the house made from manufactured decking that will have panels that lift out for maintenance and repair of the pool unit.  The first run of drywall around the room will be concrete board.  And the owners did specify that it must have two skylights.  The drywall will be painted with a bathroom type paint to seal it from moisture.  There is a bath fan planned for the room which has doors to separate it from the rest of the house.  There is a cover that stays on the pool when not in use to keep grandchildren out.  The room will be serviced by its own mini split.

HI Elizabeth,

 

Some of my thoughts as I finish my lunch...out here from Seattle area...maybe similar winter weather to yours, but you're summers are more humid, for sure.

 

I agree with much of what has been said...detach (if possible, or isolate at the very least from rest of conditioned space of home ), manage to slight negative pressure, mechanical balanced ventilation, basically all comments made about tightness of envelope (with balance mechanical ventilation!)  Seems to me your challenge from a vapor drive issue is on those cool winter days when relative humidity outside is 30% or below and you're 70 Fand 60+% RH indoors...monumental vapor drive forces at work from indoors through building envelope to dew point surfaces within wall and roof assemblies. Bad.

 

As far as insulation, I'd consider the relatively higher cost option of a full cavity fill of expanding polyurethane foam insulation shaved to the studs (polyurethane is key here, no open cell foams!).  The full cavity fill will do a great job of preventing air movement through any of those inevitable penetrations through finished wall and roof (maybe even floor) penetration. Upfront cost hurdles yes, but great control of vapor drive through wall and roof assemblies (note roof ventilation, or non-ventilated roof assemblies with foam insulation, may or may not be acceptable to local building officials).  In the absence of full cavity spray foam, I would be giving great air sealing attention to junction boxes for switches and outlets and any other penetration through interior finished surfaces like can lights and supply and return register penetrations.  These are the areas where a good deal of very warm and very moist air are going to drive into the wall and roof assemblies in search of dew point surfaces to condense back into liquid water to begin those dangerous biological experiments.  My assumption is that in summer your indoor environment and outdoor (warm and humid) environments will be more closely matched with a corresponding lower vapor drive potential...right or wrong?

 

Best of luck,
Greg.

 

 

Thanks for the advice.  I appreciate all your time.

Given that it is a large hot tub with a cover the moisture load will not be as great as a pool. I would use an interior poly vapor barrier and making sure the roof is vented so it can dry to the outside. I would not have any penetrations in the ceiling drywall. Use paperless drywall.  I think dense pack cellulose would work.

 

I would go to  buildingscience.com and look at the air tight drywall approach. For cellulose use only 100% borate.

 

I think winter is a bigger issue for vapor drive from the inside to out, cold temps and low humdity. Will the room have its own air and thermal barriers? 

 

I would also install a high quality bathroom fan with a humidity sensor. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Malcolm McKelvie replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"yes I would pay the delivery fee!"
yesterday
Alan Gindt replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Malcolm, If you want to pay delivery from USA we can talk. Otherwise no thanks."
yesterday
Malcolm McKelvie replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"How old is it? I assume it is in good working order? I'm interested in it but the price needs…"
yesterday
William H Nickerson replied to Kim Tanner's discussion Fantastic innovation
"So that's where you use those True Flow plates....."
yesterday
Colin Genge updated an event
Thumbnail

Passive House Testing Webinar with Kevin Brennan of the Passive House Academy at Online

September 29, 2015 from 1pm to 2pm
Tests needed to qualify as a passive houseWhy we’re seeing an increase in PH buildingsBest…See More
yesterday
Colin Genge updated an event
Thumbnail

DM32 Smart Gauge 101 Webinar at Online

September 22, 2015 from 1pm to 2pm
Webinar Learning Objectives:Gauge settings and operationCalculate results in the gaugeUpdate the…See More
yesterday
Colin Genge updated an event
Thumbnail

Blower Door 101 Webinar at Online

September 15, 2015 from 1pm to 2pm
See how easy it is to do your first test. Learn tips to perform your first duct test in only twenty…See More
yesterday
Colin Genge updated an event
Thumbnail

Zone Pressure Diagnostics (ZPD) with Bill Eckman of NME$A Webinar at Online

September 10, 2015 from 1pm to 2pm
Benefits and limitations of Zonal Pressure Diagnostics (ZPD).Best practices for accurate…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service