Installing an indoor swim spa and what type of insulation to use.

     I am consulting on an addition to house an indoor swim spa or endless pool.  I am getting all kinds of feedback from the different insulation companies about what type of insulation to use.  I don't want to recommend something that might be prone to rot in the future, however the spa company has no real guidelines in this area.  Their only suggestion is to install a bath fan in the room.  If the drywall is sealed with bathroom paint and the drywall is caulked impeccably, is moisture in the insulation cavity even an issue?

     I can find no one for whom excessive moisture with one of these things has been an issue.  Is blown in cellulose an option here?  I hate batt insulation because getting a good install is so difficult.  Anyone with some insight would be greatly appreciated.

Views: 2439

Reply to This

Replies to This Discussion

My first thought is to detach the "addition" from the house in order to not introduce the excessive moisture into the house.  My second thought is, if it's going to be a conditioned space, use durock (or similar) and tile on the walls and, ideally, the ceiling.  It's more expense up front, but more durable with the moisture.  I don't see much concern between types of insulation at that point --but I wouldn't use cellulose of using steel studs (moisture concerns again).  You will most likely want a ventilation fan and controlled intake for the space.  I'm open to suggestions / corrections!

If building in cold climate in priority sequence:

- As Marshall Minshew says detach the spa area as much as possible form the rest of the house or at the very least contain the spa's mechnicals within the spa's thermal envelope / extension. 

- As you and the spa company suggest, the room MUST be depressurised to the outdoors to the tune of a few pascals to keep the moist air from driving into the thermal envelope. You can turn it off if the humidity outside ever becomes greater.

 - Avoid skylights (condensation issues in skylight shaft),

 - Keep penetrations through the vapour barrier to an absolute minimum,

 - Air tightness test the envelope before the drywall goes on and make it as tight as possible,

 - Don't run any duct work through the attic space.

 - Isolate the spa's attic from the rest of the house.

 

In the attached picture the ductwork was providing descicated air from a 'Decatron'. Some of that conditioned air was piped into the pool room and some into the flat attic space (see small pipe going up into drywall) so that each skylight shaft could be "washed" with conditioned air (you can faintly see teh grill) to minimise condensation. The result is the drywall was saturated under the domed skylights and the pressurised air ducts running into the flat attic space were likely driving moisture up into the flat roof.

 

Attachments:
What are you spec'ing for the insulation around the pool itself or is it a turnkey factory-built unit?
Most of the design was already decided by the homeowners.  The room is attached, this is southern VA so mixed humid environment.  The room itself will be block walls to match the foundation of the ex. house which will be insulated on the inside with rigid foam.  The pool/spa will sit directly on the concrete.  There will be a floor built 4 inches below finished floor of the house made from manufactured decking that will have panels that lift out for maintenance and repair of the pool unit.  The first run of drywall around the room will be concrete board.  And the owners did specify that it must have two skylights.  The drywall will be painted with a bathroom type paint to seal it from moisture.  There is a bath fan planned for the room which has doors to separate it from the rest of the house.  There is a cover that stays on the pool when not in use to keep grandchildren out.  The room will be serviced by its own mini split.

HI Elizabeth,

 

Some of my thoughts as I finish my lunch...out here from Seattle area...maybe similar winter weather to yours, but you're summers are more humid, for sure.

 

I agree with much of what has been said...detach (if possible, or isolate at the very least from rest of conditioned space of home ), manage to slight negative pressure, mechanical balanced ventilation, basically all comments made about tightness of envelope (with balance mechanical ventilation!)  Seems to me your challenge from a vapor drive issue is on those cool winter days when relative humidity outside is 30% or below and you're 70 Fand 60+% RH indoors...monumental vapor drive forces at work from indoors through building envelope to dew point surfaces within wall and roof assemblies. Bad.

 

As far as insulation, I'd consider the relatively higher cost option of a full cavity fill of expanding polyurethane foam insulation shaved to the studs (polyurethane is key here, no open cell foams!).  The full cavity fill will do a great job of preventing air movement through any of those inevitable penetrations through finished wall and roof (maybe even floor) penetration. Upfront cost hurdles yes, but great control of vapor drive through wall and roof assemblies (note roof ventilation, or non-ventilated roof assemblies with foam insulation, may or may not be acceptable to local building officials).  In the absence of full cavity spray foam, I would be giving great air sealing attention to junction boxes for switches and outlets and any other penetration through interior finished surfaces like can lights and supply and return register penetrations.  These are the areas where a good deal of very warm and very moist air are going to drive into the wall and roof assemblies in search of dew point surfaces to condense back into liquid water to begin those dangerous biological experiments.  My assumption is that in summer your indoor environment and outdoor (warm and humid) environments will be more closely matched with a corresponding lower vapor drive potential...right or wrong?

 

Best of luck,
Greg.

 

 

Thanks for the advice.  I appreciate all your time.

Given that it is a large hot tub with a cover the moisture load will not be as great as a pool. I would use an interior poly vapor barrier and making sure the roof is vented so it can dry to the outside. I would not have any penetrations in the ceiling drywall. Use paperless drywall.  I think dense pack cellulose would work.

 

I would go to  buildingscience.com and look at the air tight drywall approach. For cellulose use only 100% borate.

 

I think winter is a bigger issue for vapor drive from the inside to out, cold temps and low humdity. Will the room have its own air and thermal barriers? 

 

I would also install a high quality bathroom fan with a humidity sensor. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Richard L. Sanderson replied to Bud Poll's discussion Inconsistant Local Authority
"Bud: I like the idea of a third party review board. My own experience in local government is that…"
6 hours ago
Matthew Lutz commented on Kaplan Clean Tech's blog post The Difference Between Home Inspection and Energy Auditing [Infographic]
"I would have to agree with Steve on this.  I am a Certified Energy Manager and have performed…"
12 hours ago
Matthew Lutz joined Diane Chojnowski's group
Thumbnail

Hall of Shame

In this group, members share an array of images from the field, showing the kinds of issues…See More
12 hours ago
Matthew Lutz replied to Kari Sauder's discussion Easy Water Heater Venting in the group Hall of Shame
"I have been in the HVAC trade since 1986. I have recently completed a Home or Real Estate…"
12 hours ago
Susan E. Buchan posted an event

EEBA Houses That Work at Hilton Asheville Biltmore Park

November 3, 2014 from 8am to 4:30pm
Registration: 8:00 amSession: 8:30 am to 4:30 pmWorkshop Covers:Introduction to EEBA and its…See More
16 hours ago
Susan E. Buchan posted a status
"EEBA has scholarships to our Houses That Work Sessionsfor Vets! Contact info@eeba.org for more info"
16 hours ago
EnergyLogic Academy posted events
17 hours ago
Andrew Peel posted an event

Using PHPP in Building Design and Certification at Queen's Quay

November 24, 2014 at 9am to November 25, 2014 at 5pm
In this two-day course, participants will learn how to use the PHPP for residential building design…See More
18 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service