Hello to everyone again -- This is an update on a building I'm working on for a NG furnace.  It's been about a month (a very busy month) since I last posted questions and I have been to the building -- I have some answers and another question about reading LOAD CALCULATIONS. 

The 2052 sq. ft. building has only 1.5" insulated garage door panels for the ceiling as the only insulation (in the attic floor along with 2 part foam on the perimeter walls averaging 2.5" to 4" thick) so I'm looking at blowing cellulose to a depth of 1' in the attic after some air-sealing to bring the heating loss down.  The blower door number was 6275 CFM@50 -- there is a construction flaw where 2 part foam applied to the perimeter's stud bays didn't completely reach up behind a top 2 x 6 band joist (is that what it's called if it's at the ceiling and not at floor level?)  Most bays are pulling air during the BD test.  Also the ceiling garage door panel joints are not caulked.  So I'm hoping to bring the CFM down to some reasonable level by caulking the cracks and using bagged inso stuffed into the stud bays.

I found an HVAC company that gets load calc's done and they gave a bid for a Bryant preferred two stage and ductwork installed inside the envelope (ceiling is 9'3").  They're sizing it at 100,000 BTUs.  

They did two load calc's -- one with minimal insulation (present situation) and one if 1' of cellulose is installed in 2052 sq. ft. of attic floor.

This is the first time I've read/seen an actual load calc so I have a question -- (the HVAC co. has a call into the guy in another city who did the calc and I'm still waiting for his answer) --- The software is "Elite RHVAC Residential HVAC Loads" and approved Manual J and Manual D -- 8th Edition, Version 2

On the first page, the "Project Report" down in the "Check Figures" section the number for square foot room area is correct at 2052 --- the "Volume (ft cubed) of Cond. Space" concerns me.  I would get this number by taking the sq. ft of 2052 and multiplying it by the ceiling height of 9.25' (9'3") for a total of  18,981 cu. ft --- The reports however had two different numbers -- minimal insulation calc being 32,832 and the insualtion added calc's number being 20,520.

Can anybody who knows this software tell me why these numbers are not the basic length x width x height number?

Is there a place on this report where I can see whether they considered all the ductwork is run inside the envelope not up in the attic?

And I don't see where the Blower Door number was addressed at all -- or isn't this the type of calc that uses the BD number?

According to both load calc's (minimal insulation) and ($2,000 more insulation added) I need a 100,000 BTU furnace.

Well -- thanks to everybody in advance for input.

Views: 646

Replies to This Discussion

Thanks for the input -- I don't mind getting training if I could justify it with business income in my area.  I jsut have to do some more research on this.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Casey Gesell replied to Casey Gesell's discussion Looking for home improvement companies to join our dealer network!
"Hi Patrick, I'd be glad to have a conversation with you about the details on our program. What…"
1 hour ago
Amina Lang posted an event

19th International Passive House Conference at Congress Center Leipzig

April 17, 2015 at 9am to April 18, 2015 at 6pm
The Passive House Standard enables every building owner to benefit from the energy revolution, with…See More
3 hours ago
Don Hynek replied to Luis Hernandez's discussion Non-continuous exterior insulation
"This is a matter of far more than R-values. Average exterior temp, heating load vs. cooling load,…"
19 hours ago
Patrick Michaelyan replied to Luis Hernandez's discussion Non-continuous exterior insulation
"Don, I'd like to ask you specifically about your comments on putting the structure at great…"
yesterday
Patrick Michaelyan replied to Casey Gesell's discussion Looking for home improvement companies to join our dealer network!
"Casey, Time frame for relocating is late spring to early summer. I am considering both counties…"
yesterday
Dennis Heidner replied to Patrick Michaelyan's discussion Vinyl Siding with Integral Insulation
"The observation about rot is important.   I agree. One of my complaints with some of the…"
Friday
Jennifer Schenk added a discussion to the group Job Board
Thumbnail

Job Opening - Energy Programs Manager - Frisco, CO

Energy Programs Manager - High Country Conservation CenterJob DescriptionGeneral Description of…See More
Friday
Jennifer Schenk joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
Friday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service