Hello to everyone again -- This is an update on a building I'm working on for a NG furnace.  It's been about a month (a very busy month) since I last posted questions and I have been to the building -- I have some answers and another question about reading LOAD CALCULATIONS. 

The 2052 sq. ft. building has only 1.5" insulated garage door panels for the ceiling as the only insulation (in the attic floor along with 2 part foam on the perimeter walls averaging 2.5" to 4" thick) so I'm looking at blowing cellulose to a depth of 1' in the attic after some air-sealing to bring the heating loss down.  The blower door number was 6275 CFM@50 -- there is a construction flaw where 2 part foam applied to the perimeter's stud bays didn't completely reach up behind a top 2 x 6 band joist (is that what it's called if it's at the ceiling and not at floor level?)  Most bays are pulling air during the BD test.  Also the ceiling garage door panel joints are not caulked.  So I'm hoping to bring the CFM down to some reasonable level by caulking the cracks and using bagged inso stuffed into the stud bays.

I found an HVAC company that gets load calc's done and they gave a bid for a Bryant preferred two stage and ductwork installed inside the envelope (ceiling is 9'3").  They're sizing it at 100,000 BTUs.  

They did two load calc's -- one with minimal insulation (present situation) and one if 1' of cellulose is installed in 2052 sq. ft. of attic floor.

This is the first time I've read/seen an actual load calc so I have a question -- (the HVAC co. has a call into the guy in another city who did the calc and I'm still waiting for his answer) --- The software is "Elite RHVAC Residential HVAC Loads" and approved Manual J and Manual D -- 8th Edition, Version 2

On the first page, the "Project Report" down in the "Check Figures" section the number for square foot room area is correct at 2052 --- the "Volume (ft cubed) of Cond. Space" concerns me.  I would get this number by taking the sq. ft of 2052 and multiplying it by the ceiling height of 9.25' (9'3") for a total of  18,981 cu. ft --- The reports however had two different numbers -- minimal insulation calc being 32,832 and the insualtion added calc's number being 20,520.

Can anybody who knows this software tell me why these numbers are not the basic length x width x height number?

Is there a place on this report where I can see whether they considered all the ductwork is run inside the envelope not up in the attic?

And I don't see where the Blower Door number was addressed at all -- or isn't this the type of calc that uses the BD number?

According to both load calc's (minimal insulation) and ($2,000 more insulation added) I need a 100,000 BTU furnace.

Well -- thanks to everybody in advance for input.

Views: 1106

Replies to This Discussion

Thanks for the input -- I don't mind getting training if I could justify it with business income in my area.  I jsut have to do some more research on this.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Profile IconKelly Vaughn, reshma singh and Richard Hale joined Home Energy Pros
10 minutes ago
Helen Best posted a blog post

Low-Flow Shower Heads Save Water

Just about everyone enjoys a nice long hot shower. It does come with some cost for the water and…See More
4 hours ago
Helen Best liked Helen Best's blog post This Might Be the Most Water-Efficient Shower Head Ever Invented
4 hours ago
Therma-HEXX posted blog posts
9 hours ago
Michael Dunseith posted photos
11 hours ago
Jeffrey Anthony posted a discussion

9 Blower Door Frames, 9 Shrouds, and 11 Fans, and 8 Fan Controllers For Sale

We are clearing out some of our redundant inventory. All items are from The Energy Conservatory.9…See More
13 hours ago
Quinn Korzeniecki posted a discussion

Five Retrotec Products Added to BPI Product List

The Building Performance Institute, Inc. (BPI) has recognized five new products in its Product…See More
14 hours ago
Tom White's video was featured

New York energy policy & North American Passive House Network Conference

New York is increasing its energy standards and is investigating the possibility of implementing the Passive House Standard for new construction and retrofit projects. Interviewee: Ken Levenson, with NY Passive House Assoc and 475.
14 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service