Hello to everyone again -- This is an update on a building I'm working on for a NG furnace.  It's been about a month (a very busy month) since I last posted questions and I have been to the building -- I have some answers and another question about reading LOAD CALCULATIONS. 

The 2052 sq. ft. building has only 1.5" insulated garage door panels for the ceiling as the only insulation (in the attic floor along with 2 part foam on the perimeter walls averaging 2.5" to 4" thick) so I'm looking at blowing cellulose to a depth of 1' in the attic after some air-sealing to bring the heating loss down.  The blower door number was 6275 CFM@50 -- there is a construction flaw where 2 part foam applied to the perimeter's stud bays didn't completely reach up behind a top 2 x 6 band joist (is that what it's called if it's at the ceiling and not at floor level?)  Most bays are pulling air during the BD test.  Also the ceiling garage door panel joints are not caulked.  So I'm hoping to bring the CFM down to some reasonable level by caulking the cracks and using bagged inso stuffed into the stud bays.

I found an HVAC company that gets load calc's done and they gave a bid for a Bryant preferred two stage and ductwork installed inside the envelope (ceiling is 9'3").  They're sizing it at 100,000 BTUs.  

They did two load calc's -- one with minimal insulation (present situation) and one if 1' of cellulose is installed in 2052 sq. ft. of attic floor.

This is the first time I've read/seen an actual load calc so I have a question -- (the HVAC co. has a call into the guy in another city who did the calc and I'm still waiting for his answer) --- The software is "Elite RHVAC Residential HVAC Loads" and approved Manual J and Manual D -- 8th Edition, Version 2

On the first page, the "Project Report" down in the "Check Figures" section the number for square foot room area is correct at 2052 --- the "Volume (ft cubed) of Cond. Space" concerns me.  I would get this number by taking the sq. ft of 2052 and multiplying it by the ceiling height of 9.25' (9'3") for a total of  18,981 cu. ft --- The reports however had two different numbers -- minimal insulation calc being 32,832 and the insualtion added calc's number being 20,520.

Can anybody who knows this software tell me why these numbers are not the basic length x width x height number?

Is there a place on this report where I can see whether they considered all the ductwork is run inside the envelope not up in the attic?

And I don't see where the Blower Door number was addressed at all -- or isn't this the type of calc that uses the BD number?

According to both load calc's (minimal insulation) and ($2,000 more insulation added) I need a 100,000 BTU furnace.

Well -- thanks to everybody in advance for input.

Views: 696

Replies to This Discussion

Thanks for the input -- I don't mind getting training if I could justify it with business income in my area.  I jsut have to do some more research on this.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Green Training USA posted events
31 minutes ago
Crosbey Archery posted a photo

Timber-Double-doors

This door is made and hand finished at Bradford workshops by skilled craftsmen.…
33 minutes ago
Green Training USA updated an event
Thumbnail

BPI CEU's - Online Anytime at Online

December 4, 2014 to December 3, 2015
Get All 30 BPI CEUAvoid BPI's Written Exams for Certification Renewal…See More
52 minutes ago
David I. Shepherd-Gaw added a discussion to the group Job Board
Thumbnail

JOB: Energy Efficiency Specialist @ Cowlitz PUD

Primarily a position with a residential focus in a great community. Opportunities to expand your…See More
6 hours ago
David I. Shepherd-Gaw joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
6 hours ago
John Wilkerson posted a discussion

Aeroseal Machine for Sale

Hello All, We have an Aeroseal SmartSeal system (w/ compressor and plenty of leftover…See More
6 hours ago
Rob Buchanan commented on Jose Macho's blog post Why Don't Homeowners Spend Money on Energy Saving Upgrades??? Blame "Cognitive Biases"
"I think this is an interesting comparison, but I would also want to know whether similar surveys…"
14 hours ago
Bob Blanchette commented on Jose Macho's blog post Why Don't Homeowners Spend Money on Energy Saving Upgrades??? Blame "Cognitive Biases"
"The bigger problem is the way water is billed. Most of the charges are a fixed monthly amount that…"
14 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service