Hey Home Energy Pro's!

Tim Reynolds here in Des Moines Iowa, I have been able to work with a group here that is trying out a hot roof system in a remodel. Now I can get behind the air sealing properties and understand that the foam has a high r value per inch, but there are a few problems that I am concerned about. 

1. The SP-Foam contractors didn't completely seal the roof decking, thermal bridging is occurring and some wicked ice dams have been created.

2. From what I understand here in Iowa we recommend around R-40/R-60 within the attic space,(after an air barrier is installed) with the foam only covering the decking say 3.5 inches  given that the foam R value is true 6.5 we will only have around a R-22 with a great air seal.

3. The stack effect is still in play with the attic now sitting at a average temp of 62 - 65 degrees (wouldn't we want the heat within the living space?) 

4. What if any concerns should I consider if I bring the air barrier from the roof to the attic floor? What if additional insulation is added upon the floor to bring the attic system to a proper r - value?

Thanks for any assistance.

Views: 318

Reply to This

Replies to This Discussion

#1 - it is not a properly done hot roof, the sheathing should have all been sprayed / covered & even the joists

#2 - truthfully you can get less than code minimums when done right, but you should have at least 6" total or at least a 36 - 42

#3 - stack effect is meaningless - you will generally end up with the same or reduced heating & cooling loads with a hot roof system especially if you have any mechanicals in the attic

#4 - the air barrier essentially becomes the foam, but you should still air seal between the living & semi-conditioned spaces (you did remove the attic floor insulation right?)

http://bit.ly/HotRoof

Hey Sean,

Thanks for the response!  I was called into this project after the fact to touch up leaks from SP Foam contractors. 

1. Kind of what I was thinking

2. R-36/ R-42 would be reasonable, but I feel R-22 is too low for our zone. 

3. Maybe stack effect wasn't what I wanted to use there, but you're #4 is more what I was looking for 

4. Yes all existing insulation was removed this was a complete gut and renovation. 

In the above article it states that the attic floor should be sealed to help prevent the spread of fire, and not typically for air sealing - I guess my next question is why would we allow the heat transfer into the attic and not try and keep it within the conditioned living space? 

Thanks 

-Tim

It isn't going to be easy to fix this, problems as Sean noted.  I see two approaches.

1.  Bring the spray foam contractors back and double what they installed and as Sean stated cover the rafters completely.  Check local codes to see if a fire barrier is required.

2.  Abandon the foam on the roof deck and move the air barrier and insulation to the ceiling below.  BUT, you would need to ventilate the attic space as would normally be done.

The problem with just adding insulation to the attic floor is lowering the temperature of the foam above, along with trapping the moisture as it migrates up there.  Even closing off rooms on the second floor of home can result in a mild farm.

A third approach might be to fill out the rafters with other insulation and then apply a layer of rigid foam over the exposed bottoms of the rafters, but there are guidelines for this which I don't have at my finger tips.

The bottom line is to only use a hot roof where absolutely necessary.  In southern climates with mechanical equipment and ducts in the attic, it is necessary.  In a northers climate it is most often less expensive and better to leave the attic as an attic.

Bud

Thanks Bud!!

I think having the foam guys back will ultimately be the best solution. What are your thoughts about sealing the attic floor?

Thanks -Tim

All openings that allow a fire to spread need to be sealed with a fire rated product.  Large bypasses are of course a priority.  One of the issues with a hot roof is the conditioning of the resulting space.  Often they are called semi-conditioned, but some heat and air exchange with the house below is preferred.  Yes, that attic space will get warm, but that ensures that no condensation will form.  Circulating some of the conditioned air from the house controls the humidity.

Bud

I got to say Bud has nailed most of it BUT... in a cold climate a hot roof is still a great option especially for those with cut up roofs, or ones where you cant get full depth out to the edge of the wall sheathing, or you want a higher performing structure

As for the "but all the heat loss" - you are thinking volume & not actual heat loss - air is an amazing conductor, easy to heat & cool, but rarely where you lose or gain heat - most comes from the shell & components - you also got to remember that semi-conditioned crawl & attic spaces are great buffer spaces

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Kari Sauder replied to James White's discussion What happened to Home Energy Pro's website?
"I stopped using Firefox -- too many glitches"
1 hour ago
Hal Skinner replied to Hal Skinner's discussion How our ceramic based RCC works in the group Radiant Control Coatings
"Hey Tom, I will find the ORNL repoprt and post it.  It was a test on a ballasted roof sample.…"
9 hours ago
Tom Mallard replied to Hal Skinner's discussion How our ceramic based RCC works in the group Radiant Control Coatings
"So it seems that what you're saying is for heat-transfer the stuff has little resistance or…"
10 hours ago
Hal Skinner added a discussion to the group Radiant Control Coatings
Thumbnail

How our ceramic based RCC works

How our RCC worksEveryone knows, understands and accepts that RCCs reflect heat away from roofs,…See More
11 hours ago
Mike Kandel posted a discussion

Earn BPI CEUs at 3rd Annual Building Performance Forum

If you're searching for BPI CEUs, you'll find plenty at the 3rd Annual Building Performance Forum…See More
16 hours ago
Mike Kandel added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Earn BPI CEUs at 3rd Annual Building Performance Forum

If you're searching for BPI CEUs, you'll find plenty at the 3rd Annual Building Performance Forum…See More
16 hours ago
Sean Lintow Sr commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"4% TOTAL Ted - Leakage to outside was stripped from the codes & for good reason"
19 hours ago
tedkidd commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"Wait!  4% total leakage or 4% leakage to outdoors? "
20 hours ago