Greetings.  This is my first post/question - many more to follow, I'm sure. 

I live in a rental house that has radiant floor heat and a heat recovery ventilator that pulls warm, moist air out of the baths, kitchen, and laundry room and blows outdoor air warmed through the heat exchanger into the living spaces of the house. 

The  fan started making a high pitched noise this week, so I called and they sent out a service guy (plumber).  The air exchange unit is located in the attic against a south facing wall.  The attic is not heated, but the attic is included within the building envelope (insulation against the roof). 

The plumber, after a bit of effort, pulled out the central core of the exchanger - it looks like a pentagon or hexagon prism with zig-zag filter around the perimeter (not the fan or fan motor).  It was frozen - obviously moisture had gotten in and then the cold make up air froze it.  It's been well under freezing here for several weeks.  The plumber said the ice was restricting the airflow causing the fan motor to work harder.

The plumber changed two small rectangular air filters where the ductwork enters the HRV, put everything back together, turned the fan on, and the sound was gone.  He said the system would be fine. After he left, I checked the air blowing into the house, and it felt like air conditioning - which I really don't need in the dead of winter.

My concern:  When the ice melts, and the water sits within the HRV, will I have a mold problem?

The system looks like it has a light to show that it is frosted up and might auto shut off, but obviously that didn't work. 

Thoughts?  Should I pull the ice core out and let it thaw and dry and reinsert it?  I can live without the air circulation for a couple of days.

Many thanks.

Views: 2092

Reply to This

Replies to This Discussion

It really becomes a what house, what occupancy, what climate question. I like ERVs, but it really depends. What do you want to do with latent heat, expell, keep out, or keep in? You might want both cores, switching between summer and winter.

I'm not sure it makes à huge difference unless the house is crazy tight. The issue is how yoh want/need to manage moisture.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mike Kandel added a discussion to the group Building Performance Institute (BPI)
Thumbnail

BPI's Home Energy Auditing Standard Published as ANSI Standard

The Building Performance Institute, Inc. (BPI) is proud to announce that BPI-1100-T-2014: Home…See More
7 hours ago
Mike Kandel posted a discussion

BPI's Home Energy Auditing Standard Published as ANSI Standard

The Building Performance Institute, Inc. (BPI) is proud to announce that BPI-1100-T-2014: Home…See More
7 hours ago
Hal Skinner posted a discussion
8 hours ago
Todd St.Clair joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
11 hours ago
Todd St.Clair replied to Jim Falakos's discussion Treat Software in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"How long ago did you buy this, if it was good for 5 months? And how much would you take for this."
11 hours ago
Bud Poll replied to Bud Poll's discussion Basing air exchange on house volume??
"Hi Sean, yes I am struggling with this and that is why I opened the discussion, so a definite…"
13 hours ago
Lynda Wright is now a member of Home Energy Pros
13 hours ago
Sean Lintow Sr replied to Bud Poll's discussion Basing air exchange on house volume??
"Sorry Bud but I think you need to clarify your issues with using volumes to calculate ACH As for…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service