I'm looking for some insight into why HVAC contractors don't use the ACCA process for sizing and selecting HVAC and Distribution systems. I know part of it is the generational "I've done it this way for twenty years, and I'm not changing now" attitude, and some folks are apprehensive to anything related to a computer. But are there other factors that are at play that keep contractors from using the ACCA process? I'm wondering if it's something as basic as not understanding the value of properly sizing a unit and not undestanding how to explain that value to the customer. Many guys in my area think that running a Manual J takes far longer than it actually does. Any other insights would be appreciated.
Tags:
Permalink Reply by Al DeMatteo on February 16, 2012 at 6:11pm
Permalink Reply by Bob Blanchette on February 19, 2012 at 5:54am If you think load calcs are all BS how should HVAC contractors determine the equipment size? There's the traditional way of sizing per sq ft but thats even worse for accuracy. If the consumer has copies of the utility bills they could be onto something, especially if their house has smartmeter technology and hour by hour usage reports can be obtained. If equipment cycles often on design days it's probably due for downsizing for COMFORT reasons. We have a 88,000 BTU furnace in out 1600sq ft house, when it powers up you get a short blast of hot air followed by 20 of off time. Can't justify replacing working equipment, but when it dies it will be replaced with a furnace 1/2 that size.
lol...love it!
Permalink Reply by Al DeMatteo on February 19, 2012 at 6:07am
Permalink Reply by Al DeMatteo on February 19, 2012 at 11:42am Hi Al,
Actually that's no longer correct, more and more programs allow for a specific CFM50 leakage number. Some programs will even allow for actual duct leakage (to indoors and to outdoors).
I think you are taking Phil's comment too literally. What we need is a load range that we match to equipment range rather than a fixed point. If you look at his software, they are starting down that path and I suspect future versions will offer charting that shows seasonal matching of equipment and sliders for air leakage targets as well.
Instead of using software to come up with a pat answer, software will allow us to say "what if". Often, when you start asking "what if" you stumble upon amazing solutions.
We all need to start thinking "what if" more, rather than accepting the first answer we are given as if it's written in stone.
Permalink Reply by Al DeMatteo on February 19, 2012 at 12:07pm In new construction, in this day and age, not providing a full set of plans, design envelope, energy and HVAC analysis, third party inspections and testing may constitute fraud on the part of contractors and subcontractors, IMHO. Today, there is no reason for any homeowner to buy a new house with a half-a$$ envelope and HVAC system.
When it comes to existing construction, before anyone suggests replacing to a $15-20K+ HVAC system, they should recommend a blower-door, envelope and energy test. We all know the least expensive options to improve energy consumption is to seal the envelope. Now, would an HVAC contractor cut their own business to do the right thing? That’s the $6MM question.
An example to add to Phil's comment -
Even WITH a complete audit including blower door our load came in at 80mbtu for a 3500 sf house on a windy hill in Upstate NY. We installed a 60mbtu Mod and held our breaths.
That thing doesn't go above 45mbtu output at 2f outdoors.
Homeowner sent pictures of his thermostat. I was amazed. In fact, I'm continuously amazed how little horsepower is required to maintain.
But, if he wanted to recover within some arbitrarily defined acceptable time frame we might need to install twice the furnace (which in turn would require duct replacement). So homeowner abandoned aggressive setback and is saving over 30% on total energy costs.
So, do you want throttle control or comfort and efficiency? I don't think you can have both.
Permalink Reply by Bob Blanchette on February 19, 2012 at 12:38pm tedkidd, have you EVER seen a fossil fuel system not able to keep up during design cold weather? It simply doesn't happen in the south, maybe up north it's more of an issue? Unless a building has serious leakage/insulation issues even a small furnace should be able to keep up in all but the coldest climates. Yet very few 45k furnaces are actually sold/installed even in mild climates.
45k to keep a 3500sqft house warm when it's 30 below freezing is evidence of that, yet day in and day out HVAC contractors are installing 90k furnaces in houses 1/2 that size with design temps in the 20's. I was concerned about cutting my HVAC system in HALF when it comes time to replace, but after reading your post, I no longer have concerns about it keeping up.
Permalink Reply by Avery Ray Colter on February 25, 2012 at 11:11am Using EnergyPro at work, I generally use its load calcs as a substitute for Manual J.
As for Manual D, my problem with it is that the distribution of heating capacity to each room is generally different that the distribution of the cooling capacity. If you have a constant volume system and if, in a hypothetical two room case, Room 1 has 75% of the peak heating load but only 25% of the peak cooling load, the procedure leaves you giving 50% of the CFM to each of the rooms, thus guaranteeing that one room will be underheated in the winter and the other undercooled in the summer.
I also HATE the interface for ACCA's spreadsheet, so much so that I ended up using their charts to estimate the logarithmic equation for pressure drop vs velocity and creating a spreadsheet of my own where I can set a duct diameter for a particular segment and have the pressure drop for that segment, and just list each discrete segment and add the pressure drops, arriving at the terminal total pressure drop from the supply plenum to each register and from each return grille to the return plenum. As long as the largest pressure drop on each side is less than the available, I figure I'm good.
Still though, I do see the sense of using Manual D, though in our office I think it will need a different order of work. My mechanical engineers are used to using a simple boilerplate chart of diameter as a function of CFM. I'm going to have to get them used to just sticking out the schematic and then letting me tell them what diameters to write in.
The funny part is this, and I want to ask some of you this. What do you do when you have a room (usually a powder or laundry or small bathroom) which has little to no exposed surfaces and which therefore has essentially zero peak heating load and a cooling load based on fractional occupancy, and which therefore calculates out to demanding 10 or 5 or (yes, I've seen it) 3 CFM of supply???? Are the air balancers going to just have a big belly laugh out of this? Or suggest using a transfer grille instead?
Permalink Reply by Ed Minch on February 25, 2012 at 11:54am Differing loads are usually associated with different floors - it is the height difference and the buoyancy of the air that makes it easier to heat the second floor and cool the first floor of a 2 story house. There are always rooms over garages and many windows in a sunroom besides this, but this is basically what we have to deal with in the mid-Atlantic. It turns out we need about 60% of the heat to the first floor and 60% of the A/C to the second floor.
We have trouble selling this idea because it costs a few hundred dollars, but it works every time: instead of one trunk across the basement with all branch ducts coming off of it, we recommend 2 trunks side by side, one feeding the first floor and one feeding the second floor. Each trunk is slightly oversized for its half of the load, and back at the air handler there are large volume dampers on each trunk. It is a very easy adjustment in the spring and fall to throw more air to the floor that needs it without having to install motorized dampers.
And I would not install a duct if you needed only a couple of CFM
Ed Minch
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Tom Delconte replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Ben Jacobs replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Ben Jacobs replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Tom Delconte replied to Johnny Ritzo's discussion Selecting a Water Heater
Jeena Smith commented on Molly Banton's blog post Install a Pellet-Burning Fireplace Insert and Save Money
Johnny Ritzo posted a discussion
Eric Kjelshus replied to Patrick Michaelyan's discussion Hot Upper Stories
Bud Poll replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans© 2013 Created by Lawrence Berkeley National Laboratory.