I am convinced that a client of mine is the victim of a shoddy crawl space ceiling insulation job, and that he should have it done right. He too in convinced.

So, the question is how best to address it. 

The crawl space is only 200 sf, located below a single-room addition, with ducts in the floor. There are plenty of penetration through the floor and the sill boxes. Air is the least of our worries (it's the darn critters he wants to keep out, and reduced leakage is a bonus). The existing faced fiberglass batts (R-19) are showed into between the joists, with the kraft facing in the wrong direction. The batt insulation is only 5 years old, and it's condition has not been compromised. 

The following is my proposed approach to the problem. Remove the existing batt insulation, apply a flash coat of closed-cell spray foam, cut batts to fit properly, install wire supports to keep batts flush with floor, and install a layer of house wrap to underside of joists to protect batt insulation. Sound like a winner to you pros?

Thanks in advance!

Views: 615

Reply to This

Replies to This Discussion

For the cellulose and rigid I wouldn't worry about the foaming of penetrations unless they are big enough to have a blow out in the living space.

 

For the fiberglass and rigid, I think foaming the perimeter to seal off any leaks would be good, but probably nothing other than that.

Good luck out there.

Thanks, and thank you for your input Cory!

Housewrap as your blowing barrier makes a lot of sense, though it's like wall papering a ceiling getting it in place!!

I dunno about the foam board. Where I come from (cold climate) that might work with unfaced EPS board. But If you use foil-faced Thermax, that leaves you with a vapor retarder on the cold side of the assembly, doesn't it?? Great idea in an A/C-dominant climate. But that's a really bad idea here in Wisconsin.

Don you raise a couple of good points.
As to your points about the rigid foam, the foil facing would be on the cold side, but with Thermax you have foil facing on both sides. Also, I always do all within my power to achieve an effective air seal, which has eliminated any condensation-related issues in the past. Nevertheless, I am going to think further about the points you have raised.
Patrick

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Home Energy Magazine's blog post was featured
9 hours ago
Hannah Finch posted a blog post
9 hours ago
Profile Iconpank and Carrie Sturrock joined Home Energy Pros
10 hours ago
tedkidd commented on Amber Vignieri's blog post Chicago Winter No Match for Retrofitted Logan Square Building
"This case study is an example of how hard it is simply to do a compelling case study. Everyone has…"
12 hours ago
B. M. Lubin posted an event
Thumbnail

GPRO Construction Management Class at USGBC-LI headquarters in Hauppauge, NY at USGBC-LI Headquarters

September 19, 2016 at 9am to September 20, 2016 at 2pm
Taught by industry experts using real-life classroom exercises, GPRO CM gives experienced building…See More
16 hours ago
B. M. Lubin is now a member of Home Energy Pros
yesterday
Eric Kjelshus replied to tedkidd's discussion Dear DOE, PACE sucks - please fix or make it go away...
"Most HVAC system upgrade - change outs and attic seals-R-49 end up $20-30K   Most house -…"
yesterday
Brennan Less replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"Anyone interested in this realm should check out the EPA-funded project at the South Coast Air…"
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service