I am convinced that a client of mine is the victim of a shoddy crawl space ceiling insulation job, and that he should have it done right. He too in convinced.

So, the question is how best to address it. 

The crawl space is only 200 sf, located below a single-room addition, with ducts in the floor. There are plenty of penetration through the floor and the sill boxes. Air is the least of our worries (it's the darn critters he wants to keep out, and reduced leakage is a bonus). The existing faced fiberglass batts (R-19) are showed into between the joists, with the kraft facing in the wrong direction. The batt insulation is only 5 years old, and it's condition has not been compromised. 

The following is my proposed approach to the problem. Remove the existing batt insulation, apply a flash coat of closed-cell spray foam, cut batts to fit properly, install wire supports to keep batts flush with floor, and install a layer of house wrap to underside of joists to protect batt insulation. Sound like a winner to you pros?

Thanks in advance!

Views: 517

Reply to This

Replies to This Discussion

For the cellulose and rigid I wouldn't worry about the foaming of penetrations unless they are big enough to have a blow out in the living space.

 

For the fiberglass and rigid, I think foaming the perimeter to seal off any leaks would be good, but probably nothing other than that.

Good luck out there.

Thanks, and thank you for your input Cory!

Housewrap as your blowing barrier makes a lot of sense, though it's like wall papering a ceiling getting it in place!!

I dunno about the foam board. Where I come from (cold climate) that might work with unfaced EPS board. But If you use foil-faced Thermax, that leaves you with a vapor retarder on the cold side of the assembly, doesn't it?? Great idea in an A/C-dominant climate. But that's a really bad idea here in Wisconsin.

Don you raise a couple of good points.
As to your points about the rigid foam, the foil facing would be on the cold side, but with Thermax you have foil facing on both sides. Also, I always do all within my power to achieve an effective air seal, which has eliminated any condensation-related issues in the past. Nevertheless, I am going to think further about the points you have raised.
Patrick

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Fresh Air Duct Cleaning posted a status
15 hours ago
Jim Gunshinan posted a blog post
15 hours ago
Fresh Air Duct Cleaning posted a blog post

KANATA DUCT CLEANING COMPANY

A duct cleaning in kanata is one of the best ways to improve your …See More
17 hours ago
Fresh Air Duct Cleaning posted a status
17 hours ago
Laura Palombi joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
22 hours ago
Profile IconJerrad Pierce, tracylee, Nevada Heating and 4 more joined Home Energy Pros
yesterday
Shawn Weeks posted a blog post
yesterday
Kirsten Richnavsky's discussion was featured

New BPI Standard for Conducting Energy Audits Published as an ANSI Standard!

The Standard Practice for Basic Analysis of Buildings defines the minimum criteria and specific…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service