I am convinced that a client of mine is the victim of a shoddy crawl space ceiling insulation job, and that he should have it done right. He too in convinced.

So, the question is how best to address it. 

The crawl space is only 200 sf, located below a single-room addition, with ducts in the floor. There are plenty of penetration through the floor and the sill boxes. Air is the least of our worries (it's the darn critters he wants to keep out, and reduced leakage is a bonus). The existing faced fiberglass batts (R-19) are showed into between the joists, with the kraft facing in the wrong direction. The batt insulation is only 5 years old, and it's condition has not been compromised. 

The following is my proposed approach to the problem. Remove the existing batt insulation, apply a flash coat of closed-cell spray foam, cut batts to fit properly, install wire supports to keep batts flush with floor, and install a layer of house wrap to underside of joists to protect batt insulation. Sound like a winner to you pros?

Thanks in advance!

Views: 626

Reply to This

Replies to This Discussion

For the cellulose and rigid I wouldn't worry about the foaming of penetrations unless they are big enough to have a blow out in the living space.

 

For the fiberglass and rigid, I think foaming the perimeter to seal off any leaks would be good, but probably nothing other than that.

Good luck out there.

Thanks, and thank you for your input Cory!

Housewrap as your blowing barrier makes a lot of sense, though it's like wall papering a ceiling getting it in place!!

I dunno about the foam board. Where I come from (cold climate) that might work with unfaced EPS board. But If you use foil-faced Thermax, that leaves you with a vapor retarder on the cold side of the assembly, doesn't it?? Great idea in an A/C-dominant climate. But that's a really bad idea here in Wisconsin.

Don you raise a couple of good points.
As to your points about the rigid foam, the foil facing would be on the cold side, but with Thermax you have foil facing on both sides. Also, I always do all within my power to achieve an effective air seal, which has eliminated any condensation-related issues in the past. Nevertheless, I am going to think further about the points you have raised.
Patrick

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

George Matthews replied to George Matthews's discussion Shortridge 8400 Flowhood for A/C airflow testing in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Here are the pics of the flowhood and airdata manometer"
yesterday
Sarah Holloway posted a photo
yesterday
Joe Urycki added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

TEC blower door and UEI combustion analyzer for sale

For sale is one used TEC Minneapolis blower door system: Includes model 3 fan with rings A and B,…See More
yesterday
John Nicholas replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"The Nay side is well represented with the links already posted. I presented a neutral side, with…"
yesterday
Ray Lehman replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"Hey John, Thanks for the information.  Very good empirical data. While I agree that running…"
Friday
John Nicholas replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"I have no links, just some anecdotal evidence. I had several Blower Door Tests done on my own home.…"
Friday
Chris Laumer-Giddens commented on Chris Laumer-Giddens's blog post Raising the BARrier in North Carolina Mountain Home, Air Tight Ceiling
"@Joe Nagan, We have found this technique to be WAY simpler and A LOT less labor than making a…"
Thursday
Judy Rachel replied to Blake Shurtz's discussion Testing spillage on induced draft furnace?
"I hope the attached picture is clear enough for you to see.  As the caption on the picture…"
Thursday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service