Got Data? How much leaking electricity is there in HVAC systems?

I poked around when shopping for fuel-firedboilers and couldn't find anything official.  Ran across estimates ranging from a few watts to 30 watts.  Anyone have data or pointers to data?  A lot of effort has been spent on understanding "leaking electricity" from appliances, but what about HVAC? Seems like a sleeper to me.

Views: 116

Reply to This

Replies to This Discussion

This is what I have from some of our Baseload auditing:
Compressor Crankcase Heater in AC: 40 W
Zone Dampers on Air Handler: 30 W
Thermostat transformer: 4W
And... of course the 't-stat fan setting set to "on" always' which can be:
Airhandler fans on 24/7 (@400-600W)
500W x 24 hours x 365 days x .001kW/W = 4,380 kWh/yr @$.16 = $701 per year
Tamasin:

You are really making every opportunity to hammer home that "fan on" issue :-).

Regarding the math, I usually skip a term by going straight to 8760 hr/yr...sounds much more impressive :-). Anything multiplied by that number is a bunch :-)

And $0.16/kWh !! I'm crying the blues at $0.14 in NV!

Can not be said too often!
Can't tell you anything about boilers, but I could look up measured data for my own ECM furnace if that helps. If memory serves it was on the order of 10 watts total. I believe Scott Pigg of the Energy Center of Wisconsin has data for furnaces, but probably not boilers - he might have published the furnace standby in his Home Energy Magazine article of Nov/Dec 2003.

You might try posting this question on "The Wall" at HeatingHelp.com. This is Dan Holohan's web site, and some experienced hydronic contractors often give prompt answers to questions.

Alan Meier sent me to the Australian Standby Power study linked here: http://standby.lbl.gov/docs.html several years ago, but I don't recall if boilers were measured. Great study because it measured a lot of hard-wired sleepers, as you called them.

If you find good data please publish it - inquiring geeks want to know!

Upstate NY is coming in at $.17/kWh

Steve Waclo said:

Tamasin:

You are really making every opportunity to hammer home that "fan on" issue :-).

Regarding the math, I usually skip a term by going straight to 8760 hr/yr...sounds much more impressive :-). Anything multiplied by that number is a bunch :-)

And $0.16/kWh !! I'm crying the blues at $0.14 in NV!

Can not be said too often!

Mark:

 

"Upstate NY is coming in at $.17/kWh"

Does the meter reader wear a Lone Range mask on his rounds :-)??

Spent the coldest winter ever in Corning back in 99-00 and noticed how the state seemed to load up utility bills with surcharges. Corning Glass was booming at the time, but pity folks who had to pay the heating costs when things declined there later.Understand CG is now coming back.

The only electrical stand by losses I believe would be from the control transformer. If there is no call for heat.



Steve Waclo said:

Mark:

 

"Upstate NY is coming in at $.17/kWh"

Does the meter reader wear a Lone Range mask on his rounds :-)??

Spent the coldest winter ever in Corning back in 99-00 and noticed how the state seemed to load up utility bills with surcharges. Corning Glass was booming at the time, but pity folks who had to pay the heating costs when things declined there later.Understand CG is now coming back.

 

They wear a mask, but it ain't Lone Ranger or Robin Hood!

Actually just about HALF of the electric cost (I'm in Central Hudson territory) is fees and transmission charges. You 'only' pay about $.08-.09/kWh for the electricity, the rest is delivery.

Just got some measurements from one boiler.

 

Heating mode: 936W

Circ pump and air handler: 396

Circ pump only: 216W

Cooldown (internal fan): 120W

All "off": 3.6W

If it's leaking, while it certainly does affect efficiency, wouldn't this nevertheless already have been calculated?

If not, then a 14 seer pump is not a 14 seer.

If I may chime in, the newer hydronic boilers, (Viessmann Vitodens 200 being one I have personally installed, but others as well), often do cause an unexpected electrical consumption jump -at least the first time you install one. In our case, the internal blower fan and internal circulator (an ECM based Grundfos just the same), drew over 130 Watts over our previous baseline. The heating efficiency was admirable and worth it, but we paid no mind to the electrical consumption until we got the bill. I installed a Kill-A-Watt meter at the power supply unit for a season and it recorded over 600 kWH for a ten month period. This does not include the secondary circulator for the heating loop. We average about 18 cents per kWH here in Boston, BTW.

These are net boiler numbers. Our first month was double this but we found the culprit: When the boiler fired it created the tell-tale condensing boiler plume. The plume in turn activated the IR/Motion Detector on our outdoor flood lights... live and learn.

Tamasin illustrates the much larger parasitic losses of moving air. All that mass of low specific heat vs. water, it is not an efficient delivery method. The Btu per Watt ratio is rather low.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Bob Blanchette replied to Hal Skinner's discussion Any success getting landlords to energy upgrade a single family rental unit?
"The landlords don't want the improvements done even if they don't have to pay for it?…"
8 hours ago
Hal Skinner posted a discussion
8 hours ago
Hal Skinner replied to Hal Skinner's discussion Any success getting landlords to energy upgrade a single family rental unit?
"Hi Bob, The tenants all say they cant do anything to the building.  We would get referred…"
10 hours ago
Tom White commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"Ben's Kickstarter documentary, The Future of Housing, was fully funded. The grand premiere…"
18 hours ago
Tom White's video was featured

Simon Sinek: How great leaders inspire action

TED Talks Simon Sinek has a simple but powerful model for inspirational leadership all starting with a golden circle and the question "Why?"
18 hours ago
peter chang's discussion was featured

Programmable tstat for electric baseboard?

Ok, just want to throw this out there. I live in the high desert, 6800' or so. My house is pretty…See More
18 hours ago
Tom White posted a video

Simon Sinek: How great leaders inspire action | Video on TED.com

TED Talks Simon Sinek has a simple but powerful model for inspirational leadership all starting with a golden circle and the question "Why?" His examples include Apple, Martin Luther King, and the Wright brothers ... (Filmed at TEDxPugetSound.)
19 hours ago
Michael Dunseith posted a photo
23 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service