I've heard that measured performance of actual, installed geoexchange systems can be much lower than advertized COP numbers.
Is anyone aware of any accessible, reliable reports about real-world performance of these systems?
If not an academic-level paper, anyone have any good anecdotal information?
Thanks in advance,
Doug
Tags: geothermal
Permalink Reply by Polly Ledvina on March 7, 2013 at 11:37am Residential Ground-Source Heat Pumps: In-Field System Performance and Energy Modeling
by Srikanth Puttagunta, Robb A. Aldrich, Douglas Owens, and Pallavi Mantha
Steven Winter Associates, Inc., Norwalk, CT
GRC Transactions, Vol. 34, 2010
http://www.builditsolar.com/Projects/SpaceHeating/InField%20Perform...
This page has a link to a Manitoba Hydro study, as well as the Steven Winter study:
http://www.mge.com/home/appliances/heatpumps/
The Feb. 2013 issue of Energy Design Update has an interview w/ Steve Kavanaugh, ASHRAE fellow and heat pump guru. He's calling out the industry on misleading ratings, and he's a long-time GSHP researcher (literally, wrote the book on GSHPs).
This page allows you to compare heating costs using different heating systems. As always, choose your assumptions carefully:
www.eia.doe.gov/neic/experts/heatcalc.xls
Thanks Danny Parker, for the link to the study.
Jon
Permalink Reply by Bob Blanchette on March 12, 2013 at 4:23am Natural gas is hard to beat for fuel cost, it's the deliver/meter charges that get you. Gas is only 50 cents per therm in our area but the meter fees add up to $360/yr. For people with well insulated homes the meter fee doesn't justify having gas installed in the home. If you have a gas meter installed, make ALL appliances natural gas. Based on our local electric/gas price structure if your house is well insulated going all electric with a standard heat pump will be the most economical operation. Our local electric company has about 1/2 price power for use over 600KWH in winter. For the most part Geothermal makes no economic sense in our area, but I see a few systems installed. Over half of all electric homes use RESISTANCE HEAT as the primary heating method. They won't pay $800 for a normal heat pump, much less $10K+ for geo.
"Why is further geothermal heat pump research needed in cold climates?
The measured performance of geothermal heat pumps in cold climates in studies that we are aware of suggests that heat pump systems don't work as efficiently as people would expect. We also have heard from customers who have geothermal heat pumps and are unhappy because they see higher heating costs than they expected."
Permalink Reply by Bret Curry on April 2, 2013 at 4:13pm I have a Water Furnace Envision V in my own home. Open vaulted environment with 23' ceilings. 2000 square feet. North wall is 75% glass with Low-E, low-U and low SHGC. Demilac SealEction 500 foam encapsulation of vault, walls, floor. The Envision has the domestic hot water/desuper heater feature. I DO NOT have any electric resistance back-up strips. Winter heating mode daily average consumption is 10-15 kilowatts. Purrs like a kitten... Average year-round daily consumption is 9-kilowatts. Again...no back-up heat strips or dual fuel.
Permalink Reply by Bob Blanchette on April 3, 2013 at 4:16am This gets me to thinking about the installation cost of Geo. I'm thinking if your unit can do the job w/o any heat strips it's on the large side relative to the load in your home. With Geo, a lot of the installation cost is the ground loop. If the Units were sized for cooling load the downsizing may make the installation practical where it may otherwise not be. Running heat strips for a few of the coldest winter nights could be cheaper than installing another ton or 2 of ground loop and ductwork.
Permalink Reply by Curt Kinder on April 4, 2013 at 9:19am "I'm thinking if your unit can do the job w/o any heat strips it's on the large side relative to the load in your home."
Could be...could be not. Much depends on the climate. In some areas (south) cooling load exceeds heating load. In north Florida that is often the case. We do incorporate heat strips with air source heat pumps, mostly for defrost cycles, but we do not include heat strips with geo systems.
Permalink Reply by Bob Blanchette on April 4, 2013 at 5:57pm My bad, I wasn't considering the deep south.
Following Curt's comment - a house this well insulated and air tight, & possibly with thermal mass, may not really experience the "peak" load you think about with a leaky house in Upstate NY (or anywhere else)... Mass, and insulation thermal inertia, can really flatten out cold spikes.
At 2000 sf, might be hard to find a Geo system that would be "undersized" and require supplemental heat.
Permalink Reply by Bob Blanchette on April 4, 2013 at 5:59pm Thermal inertia is NOT considered in Manual J calculations!! Equiptment can be sized a bit smaller once inertia is considered, just don't expect quick recovery times.
Permalink Reply by Bob Pietrangelo on April 4, 2013 at 12:34pm
Permalink Reply by Bob Blanchette on April 4, 2013 at 5:56pm With NG at current prices, no way Geo will ever have a reasonable payback time. Geo's real market is all electric homes, or those on oil/propane.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato's discussion was featured
Johnny Ritzo's discussion was featured
Tom Delconte's blog post was featured
Christopher Morin's blog post was featured
Mike Rogers's blog post was featured
Mike Rogers posted a blog post
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase© 2013 Created by Lawrence Berkeley National Laboratory.