I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 177

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Jan E. Graveamker replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
11 minutes ago
Everblue posted a status
"Check out this video that Betty Saenz put together about Everblue's BPI training! Betty is a Realtor/EcoBroker in TX. http://bit.ly/1nSxcGJ"
20 minutes ago
David Eakin replied to Jamie Kaye's discussion Flickering LED lights
"I think the comments by Maria and Dennis have some merit for my own situation. I originally used…"
24 minutes ago
Ryan Rutledge commented on Hal Skinner's group Radiant Control Coatings
"Great idea.  Our company has a radiant control coating product so I think we can definitely…"
1 hour ago
Profile IconRyan Rutledge, Tom Mallard and 2 other members joined Hal Skinner's group
Thumbnail

Radiant Control Coatings

A group where people who work with radiant barrier coatings can let others know all of their uses.See More
1 hour ago
Tauran Ivall joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
1 hour ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Graham, Here are some facts Whole house fans preceded air conditioning by decades - example  -…"
1 hour ago
Brice Fawley commented on Brandon Walton's event Efficiency First AZ is Hosting Huge Meeting August 20th!
"This is a must attend. The future of the Home Performance industry in Arizona is a hot topic and we…"
2 hours ago
Graham Irwin replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Kurt, The "large fan" is a whole house fan moving anything from 1000-4000 CFM. By…"
3 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Graham, what "large fan" are you referring to?  I am fascinated by your comment…"
11 hours ago
Graham Irwin replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"I think it is important to check the energy consumption of such a large fan, even assuming it can…"
13 hours ago
Hal Skinner added a discussion to the group Radiant Control Coatings
Thumbnail

Rooftop A/C units and exposed ductwork

Lets start a discussion about rooftop A/C units and exposed ductwork. The worst place to put a…See More
14 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service