I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 245

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Colin Genge posted events
6 hours ago
Profile IconJon Turnbaugh, Lights N More and John Kamas joined Home Energy Pros
6 hours ago
Amber Vignieri posted a blog post

Relay Network Targets Multifamily Housing Upgrades Nationwide

Affordable apartment buildings are home to more than 10 million American households, making them a…See More
8 hours ago
Tom White's video was featured

Robby Schwarz on Builder Collaboration

Hear Robby Schwarz, of EnergyLogic discuss the value Owens Corning brings to Thrive Home Builders.
12 hours ago
Crosbey Archery liked Don Hynek's discussion Testing "Magic Pak" units??
14 hours ago
Crosbey Archery joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
14 hours ago
Crosbey Archery liked Crosbey Archery's blog post Energy Tips - Fresh Look at Heating and Cooling the Home
14 hours ago
tedkidd liked Luis Hernandez's discussion Airsealing an old basement ceiling
21 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service