I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 178

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Bud Poll replied to richard gaughan's discussion Advice for heating a 3-story Vermont home built in 1900?
"To add to Richards list of what might have"
1 hour ago
Hal Skinner replied to richard gaughan's discussion Advice for heating a 3-story Vermont home built in 1900?
"Hi Richard. If we are talking a circa 1900 home, is there any insulation in the walls at all? …"
2 hours ago
David Meiland replied to richard gaughan's discussion Advice for heating a 3-story Vermont home built in 1900?
"Bud is right on. Get a professional auditor to assess the building. Finding the right person may…"
3 hours ago
Bud Poll replied to richard gaughan's discussion Advice for heating a 3-story Vermont home built in 1900?
"Hi Richard, Being a science writer and this being rental units, here is a moral dilemma you…"
7 hours ago
richard gaughan posted a discussion

Advice for heating a 3-story Vermont home built in 1900?

I'm a science writer, as opposed to an energy professional, and I joined this group to try to keep…See More
11 hours ago
Christopher Talarico posted a discussion

Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace

Hi,I've looked around online and haven't found a lot of good information on home heating with…See More
21 hours ago
Profile IconSara Sabol, Christopher Talarico and Aaren Stewart joined Home Energy Pros
23 hours ago
Hal Skinner replied to Andy Gostisha's discussion Disguising Ductless Heat Pump Units
"Hi Andy. The bare metal units on a roof stick out like a sore thumb .  Coating them with our…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service