I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 197

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Rick Karg replied to Carly@AirCycler's discussion The (Small) Cost of Ventilation Without Recovery
"As a member of the ASHRAE 62.2 committee (and president of Residential Energy Dynamics, the author…"
Friday
Bradford E. White replied to Elizabeth Guinn's discussion ERV in need of backflow preventer.
"I would use an in-line backdraft damper such as Artis Industries or the ones made by Fantech and…"
Thursday
Kim Tanner posted a video

Wireless Air Leakage Testing

This webinar will discuss the use of WiFi technology to conduct and document blower door and duct leakage tests for compliance with local energy codes. The s...
Thursday
Profile IconPerry Grossman, Daniel Pate and Ottawa Furnace Filters joined Home Energy Pros
Thursday
Kirsten Richnavsky added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
Thursday
Kirsten Richnavsky posted a discussion

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
Thursday
Kim Tanner posted events
Thursday
Ottawa Furnace Filters posted a blog post

Some Useful Information about Furnace Air Filters

There is not much we can do about the air pollution outside of a house in Ottawa, Canada, but we…See More
Thursday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service