I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 190

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Dennis Heidner commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"Dale, good write up. For the landscaping bulbs,  if they had been T3 12V wedge bulbs,  I…"
14 hours ago
Brett Little commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"It's very true! So many people and contractors have tons of insulated attics but no air seal…"
16 hours ago
Chris Leach replied to Richard Beyer's discussion "The Dangers of Using Spray Foam Insulation"
"The problems will surface soon enough . Why don't we take a second look at this over rated…"
17 hours ago
Don Fitchett commented on Tom White's video
19 hours ago
Profile IconJean-Paul, Bryan and Erica Sullivan joined Home Energy Pros
21 hours ago
tedkidd replied to Bob Blanchette's discussion How does Cycles Per Hour affect real world AFUE?
"Want to spot a simpleton? It's a guy who thinks EE and comfort are disconnected.  Want…"
21 hours ago
tedkidd commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"Nice post Tom! I really like how he puts that. Leveraging interests so they can optimize…"
21 hours ago
Kent Mitchell commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"As a contractor in the region - we frequently wonder how/why you can be a non-profit?  Oregon…"
23 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service