I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 243

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Rick Causo posted a video

Swing Green GFX Drain Water Heat Recovery - GreenFoX

PowerHouseTV aired Sept 5 & 6, 2015. Segment 2 of the show highlights Swing Green, Inc. and the 4th generation of Drain Water Heat Recovery system, the Green...
2 hours ago
Matt Thornberry replied to Kim Tanner's discussion Game of Homes
"Thanks Kim! Game of Homes is an exciting new way to earn professional development credits for BPI…"
4 hours ago
Tom White posted a video

Enhabit: the non-profit that helps homes work better

Hear from homeowners Sonia, Amy, Roberta and Ty of Portland, Oregon, and Andy of Beaverton, Oregon, about their experiences with Enhabit. Enhabit is a non-pr...
4 hours ago
Daniel Beauchemin replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Dan Antonioli, You can use a ThermoDrain, drain water heat recovery to preheat your water and…"
5 hours ago
Steve Leombruno replied to Tim Kendzia's discussion Cooling effect from solar panels
"I have been told t"
6 hours ago
Rich Manning replied to Diane Chojnowski's discussion Poll: Where do you go for information on home performance?
"My favorite is Building Science Corp. Its not only comprehensive, its free!"
6 hours ago
Tom Barrett replied to Tim Kendzia's discussion Cooling effect from solar panels
"Any type of shading will help greatly. One of the biggest, if not the biggest, factor for high…"
6 hours ago
Rich Manning replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"80% seems a little  high to me for the solar system. Typically one would size the system to…"
6 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service