I'd like the experts here to weigh in on this.  I've been hearing a lot of claims about the better IAQ you get with geothermal systems.  In my mind, a forced air system is still a forced air system, so I'm not sure if there is any validity to that claim.  But I'm not an expert.  If you feel one way or another, please post, and substantiate your position with the facts.  Thanks!  I really look forward to everyone's response on this!

Views: 325

Reply to This

Replies to This Discussion

Hi Trish,

I cannot think of any reason why a ground source unit would provide any better IAQ than a conventional heat pump, with one exception. The ground source unit has no need to defrost. So there will be no reverse cycle cooling calls in the heating season. Consequently, the risk of "dirty sock syndrome" could be reduced. But the dirty sock microbe doesn't visit every household. So it seems a stretch to make much of an issue about it. 

On the other hand, if you are comparing ground source with a gas or oil fired forced air furnace, there are considerable differences. One that is seldom talked about is the compounds that can emit from heat exchangers. Some chemically sensitive individuals will have difficulty with the cutting oils and other chemicals evaporating in the air through the ductwork. It seems about 25% of the population are disposed to have such reactions (based primarily on hereidty). Of course any time you have a fire in the cave, it increases the risk of gas or oil leaks and combustion byproducts. CO will get you regardless of your DNA.

With very long run times the GS heat pump can clean the air better with  wet coil than most filters.  I took an air advice particulate counter to compare dry coils VS wet coil and wet coil was = to merv 8.    I hear that GS HP do not need yearly cleaning  I disagree.  the coil still get dirty, filter still need to get cleaned/replaced, parts still need to be replaced - motors relays get pitted, go down,  stick, drag.  I find most GS heat pumps still need 2 hr yr "tune up"  " cleaning"  I do not put gages on but will cheak amp draw, SP, temps, stat and operation.  Back to better IAQ  over all yes only with better air flow and better filter. 

RSS

Forum Discussions

Origin of guarded blower door testing

Started by Kim Tanner in General Forum. Last reply by Eric Kjelshus yesterday. 9 Replies

Electro Magnetic Fields (EMF)

Started by Barry L NewDelman in General Forum. Last reply by Daniel Cullen Aug 10. 5 Replies

When is it too windy to use blower door?

Started by Brandon Walton in General Forum. Last reply by Iain Walker Aug 10. 17 Replies

Latest Activity

Profile IconArmstrong SMith, Eric Buchalter, Liza Gonzalez and 3 more joined Home Energy Pros
9 hours ago
Eric Kjelshus replied to Kim Tanner's discussion Origin of guarded blower door testing
"That same house that meet highest sealing rate in early 1980 we went back and super sealed it and…"
yesterday
Jill Cliburn posted an event
Thumbnail

National Solar Conference and NZE Decathlon at University of Colorado

October 9, 2017 at 6pm to October 12, 2017 at 7pm
yesterday
tedkidd replied to Kim Tanner's discussion Origin of guarded blower door testing
"Brendan, Eric, great stuff!"
yesterday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service