Can anybody tell me what the 1.0920 "constant" charge is?

Views: 186

Reply to This

Replies to This Discussion

For doing a BTU/temp rise test on my furnace should the meter dials register be used? Or should correction factor be applied to the meter reading?
Clocking a Gas Meter

My furnace spins the 1/2 cuft dial in 49 seconds, how many BTU is it actually burning?

look at the meter and says what the rate is.  10 CFM at one turn?   I find to large of number with long run times.  I bring my own diaphragm meter with flex hose and then can rate my own use.   To make sure the furnace is running right still must use a flue gas meter  

less than 100 PPM CO  6 to 9% O2  and temp of flue gas is a must and then the do not need to clock the gas meter

Bob, is there a mechanism that compares the amount of gas that enters that pipeline circuit and compares it with the amount that is metered and billed.  Accounting for losses in the delivery infrastructure must be included in the rates, but I am unsure of the method used to do this. If this "Constant" is only a pressure adjustment, where do the line losses fit in the billing equation?? The constant of 1.092 can create some serious coin for a utility that bills out millions of dollars a month, but meters that read 8% high can create an astounding amount of revenue.

  I have metered my LPG use for over 4 years, using an Elster BK-G4  diaphragm meter.  I collect hourly cfm data and am able to compare metered use to the "time stamped" delivered amount.  The "fudge factor" for this brand new meter has averaged 1.08 with a range from 1.04 to 1.10.  When I start the discussion with a gas service provider, the room get very cold, very fast.  The delivery trucks are certified twice a year and I am confident that they are as accurate as the pumps that measure my unleaded fuel.  Fuel measurements are temperature compensated on delivery and at my meter. 

    As I am currently on the winning side of this "measurement", I have not pursued a more accurate (expensive) measurement system.  However, a natural gas pipeline is now accessible and I am trying to evaluate the cost benefits of  installation fees and long term savings.  The cost per therm is much less, but connecting costs have been estimated at several thousand dollars (200 feet from building access to main connecting point). Would you include meter accuracy in a cost comparison formula??

As Nat gas or Lp meter get used the vain & bearing  get tared up and dirty.   I have seen  older meter drag down 30-40%.   When a meter gets changed  the usage going up.   Look inside a LP or gas pipe after being used 30 yr.   The under  ground gas line leak with high water table, the  water vabors up in flame but rots all the insides.  

This bill has 2 "fudge"  factors A) BTU factor  most will have a base  970 BTU  or what ever is used  then when they test the gas burn rate.   I was with a group that rated gas BTU and the rate changed from 951 to 1023 BTU some times in 24 hours.  Now the higher BTU is mined out better and the sulfer is taken out also.  B) "Constant"   ask about it  Looks the loss rate or leak rate.  the compresser( to raze presser) run on gas to so some is used there also less than one persent

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Robert Leone added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door Package for Sale

Hi,I am selling my blower door with extras as a package or individually. These items are used but…See More
5 hours ago
Profile IconRobert Leone and Richard Vito joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
5 hours ago
Richard Vito joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
13 hours ago
Richard Vito joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
13 hours ago
Richard Vito joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
13 hours ago
Richard Vito joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
13 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I had a revelation while attending Bruce Manclark's session of duct leak testing at the Energy…"
yesterday
George J. Nesbitt commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Blower Door; the 2007 test was a depressurization test, and the 2014 a pressurization test, which…"
yesterday
George J. Nesbitt replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Plan, plan, plan, plan. The 1st step to is to understand the house, how it's built, the…"
yesterday
George J. Nesbitt posted an event

High Performance Windows - A Panel of Experts at Pyramid Alehouse`

April 26, 2014 from 3pm to 5pm
Join a lively panel discussion on high performance windows. We'll cover some basics, as well as…See More
yesterday
Kaushal Bharath Raju replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Hi David, Thanks for pointing out Martin Holiday's article. I do not wish to engage in the…"
yesterday
Profile IconAdam Penberthy, Scot Davidson and j jarvella joined Home Energy Pros
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service