Last week I was doing a rough-in w/air handler installed duct test.  I taped all the supply boots and installed the fan to the return grill just as always. When I set up the manometer, I noticed a pressure reading of 135Pa, this without the fan being turned on.  If I disconnected the hose from the manometer, pressure fell to zero.  Assuming I had done something to cause this I checked and rechecked everything, even installed fresh batteries.  Finally, I moved the hose to another supply boot, this resulted in a proper reading so I went ahead with the test.

Does anyone have any idea what was going on to give such a reading?  Let me know if you need more information.  Thanks for help solving this perplexing question.

Views: 254

Reply to This

Replies to This Discussion

Hard to see how there could be +135 in one supply duct without at least some positive reading everywhere else. Maybe someone accidentally (?) tied a bath fan into that duct.......

No power to the house at time of testing.

someone stepping on the hose?

No.

I would tend to agree with Glen, as a blocked tube will clock up rather fast.  If there is still a pin hole I suspect the pressure would stabilize at some point, although I'm not going to test it.  It could have been a kink somewhere that unfolded when you moved the hoses.  If it was a positive pressure the block was on the input.  If negative it would have been on the reference, DG700 at least.

Bud

I just submitted this to the Energy Conservatory.  If I get something useful back from them, I'll post it here.

As promised, I asked the folks at The Energy Conservatory about my funky duct test results.  Paul Morin, a Technical Sales Specialist suggested that such a situation could occur if the hose is stopped up or perhaps was up against insulation in the supply boot.  He went on to say; "You can simulate a pressure this high by putting your finger over an open tap on the DG-700 gauge.  It is harder to reproduce a pressure that high with a long length of hose attached, but you would see pressures that high if some debris is plugging the hose.  You also will see pressures that high if the hose is pinched, stepped on or if there is water in the hose."  

I believe that the end of the metal probe must have been up against the boot insulation, probably when I taped the hose  to secure it. The resulting restriction of air caused the errant reading.

Thanks to everyone who offered a suggestion.  

Something else to look out for.  If you use the metal probe to punch through the plastic tape you can actually punch a hole in the plastic tape which will cover the end of the probe.  I've had this happen to me and it caused some temporary confusion.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Dennis Heidner replied to J.C. Martel's discussion Disasters & sustainable energy
"Mark,  I am quite sure that if the Seattle grid were to go down - the Bullitt Center building…"
1 hour ago
Mark Richardson added a discussion to the group Renewable Energy
Thumbnail

Disasters & sustainable energy

Read my response to J.C. Martel's discussion:…See More
17 hours ago
Mark Richardson replied to J.C. Martel's discussion Disasters & sustainable energy
"Hi All, Interesting topic - myriad issues in play here, but I’ll try to touch on the ones I…"
17 hours ago
Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
yesterday
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
yesterday
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
yesterday
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
yesterday
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
yesterday
Tom Delconte's blog post was featured
yesterday
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
yesterday
Edward Foskey's blog post was featured
yesterday
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service